I have a 100 amp sub panel with a 60 amp square D breaker, that leads to the detached garage with another 100 amp panel. That 60 Amp should be a 100 amp correct?
|
|
#2
|
||||
|
||||
|
It is not violate anything for a main breaker to be of less amperage than the max in the box. If it is used for lights, it will probably be okay.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Last edited by jbushart; 3/10/08 at 10:22 PM.. |
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Nope. The breaker protects the wire leading to that subpanel. The "100 amp" rating of the subpanel is the max rating that you can feed it at. In other words, it's "heavy duty-ness". This is the same as saying that you may only carry a sack of groceries in a 3/4 ton pickup truck. You don't need to carry 3/4 ton loads in it just because it's rated that heavy.
|
|
#4
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| Breaker Question | mhawley | Electrical Inspections | 5 | 1/14/08 3:25 PM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical Inspections | 4 | 9/7/07 2:05 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 9:04 AM |