For all of the electrical guru's out there. I do believe this is a 60 amp service right? I al would like to know if a double tap is acceptable on this pannel. It is a pushmatic, rated at a 100 amps. The double tap is on a 60 amp breaker, going to the range and the dryer outlet.
Attached Thumbnails
60-amp-right-img_0612.jpg   60-amp-right-img_0625.jpg   60-amp-right-img_0660.jpg   60-amp-right-img_0657.jpg  



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #2  
Old 5/26/07, 3:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 AMP....Right?

Quote:
Originally Posted by rcramer
I do believe this is a 60 amp service right?
Not enough information has been given yet to make that determination. From what I can see visually, the likelihood that it is either a 60 or 100 amp service is about equal. The pipe from the tap can to the meter base seems a bit big for 60 and about right for 100, but it's really hard to say at this point. What was the rating on the main breaker? What gauge were the service entrance conductors.


Quote:
Originally Posted by rcramer
I al [sic] would like to know if a double tap is acceptable on this pannel [sic]. ...The double tap is on a 60 amp breaker, going to the range and the dryer outlet.
No way, for several reasons.

Last edited by Marc D. Shunk; 5/26/07 at 3:45 PM..
Reply With Quote
  #3  
Old 5/26/07, 3:55 PM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: 60 AMP....Right?

The main Breaker was 100 amp and the service entrance conductors were a 4. Here is a pic of the overhead, it was high up on the pole to tell exactily what gusge the OH conductors are.
Attached Thumbnails
60-amp-right-img_0611.jpg  



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #4  
Old 5/26/07, 4:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 60 AMP....Right?

I agree with Marc.....you stated you believe it is a 60A panel but the main OCPD was rated at 100A, so you stated the wire is a #4 AWG...so is that CU or AL...because based on 310.15(b)(6) # 4 CU would be fine for a 100A panel....so if it walks like a duck, quacks like a duck....it's a duck. FYI....did the panel have a rating label in it by chance for an additional confirmation?

On the double tap issue.....other than the breaker not being rated for such...the largest concern is they have different size conductors that are terminating under the same termination.....when different size conductors terminate like this there is no possible way the smaller conductor will have a proper connection which can lead to a loose connection and issues when load is present on the conductor.....among other things.

PS. The size of the overhead from the pole to the connection point means nothing really as they have allowances for free-air and so on, and again the POCO beats to their own drum...always look at the point past the drip loop and into the mast head to aid in wire sizes and make sure it matches the size in the enclosure....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 5/26/07, 4:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 AMP....Right?

I'm guessing (or rather, hoping) that the 4 gauge observed was copper. The PushMatic panels of that vintage were not rated for AL conductors in the lugs. In fact, most of the very early one's had solid copper lugs.
Reply With Quote
  #6  
Old 5/26/07, 4:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 60 AMP....Right?

Thats a great point Marc......many will find that it was not until the 60's and 70's that AL terminations and busses started to become the flavor.....most older equipment was CU only rated.......great points...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 5/26/07, 4:32 PM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: 60 AMP....Right?

Yes it was copper. Thanks guys. I just thought all round meter bases were rated at 60 amps.....learn someting new every day, I apperciate the fast response. ANy other concerns with the pushmatic pannel?



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #8  
Old 5/26/07, 4:39 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 60 AMP....Right?

Watch my video...http://www.theelectricalguru.com/video.html on sizing a service......the meter can itself is always the poorest choice to use in doing an analysis.....remember while most round are 30-60 A....it is not uncommon to find them 100A as well.....but very hard to determine that so use it is as guideline to confirm the things you CAN determine and if if not needed throw it out in the final conclussion.

As for Pushies......well they are old and I don't like any OCPD over 25-30 years old but thats me.....they are costly to replace and many have reported the breakers stick with age probably due to heat and expansion and dust but for the most part the OCPD feature seems solid.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 5/26/07, 4:40 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 AMP....Right?

Quote:
Originally Posted by rcramer
. ANy other concerns with the pushmatic pannel?
Nothing specific to the brand, other than the fact that it is obsolete and the breakers are expensive. Your example is an older one in the range. I'd guess mid 60's, perhaps. They were a fantastic breaker in their day, but some people have a hard time pushing them 'on' and 'off'. It does take some force, which some older people can't muster.
Reply With Quote
  #10  
Old 5/26/07, 4:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 AMP....Right?

Quote:
Originally Posted by pabernathy
Watch my video...http://www.theelectricalguru.com/video.html on sizing a service......the meter can itself is always the poorest choice to use in doing an analysis.....remember while most round are 30-60 A....it is not uncommon to find them 100A as well.....but very hard to determine that so use it is as guideline to confirm the things you CAN determine and if if not needed throw it out in the final conclussion.
Right. If, for instance, you encountered a round meter can, about the only thing you can say for sure at that point is that it isn't a 200 amp (or bigger) service. You can still buy a round 100 amp meter can to this very day. It is not on the approved list of meter cans for most power companies, due to it's tight wiring space and the fact that it requires a meter retaining ring.

http://www.meter-devices.com/graphics/100_amp.pdf

Last edited by Marc D. Shunk; 5/26/07 at 4:45 PM..
Reply With Quote
  #11  
Old 5/26/07, 4:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 60 AMP....Right?

Here is the meter marc is refering too ( hope you dont mind marc I blew it up for them to see )
Attached Thumbnails
60-amp-right-roundmeter.jpg  



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 5/26/07, 8:58 PM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: 60 AMP....Right?

Thanks Marc & Paul,

You guys are great electrical guru's....I apperciate the help.



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #13  
Old 5/26/07, 9:08 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,361
Default Re: 60 AMP....Right?

That looks like a new meter can in the first photo.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts