Default How about a 60 amp service?

Respectfully, I picked this from the archives and because the subject was covered in detail at the convention I believe like the second poster that there are not always problems associated with old panels:

Look here:

How many of you guys/gals will flag a panel, just because it's only 60A?

(Yes, 3-wire 60A ... and for a small house without any heavy heating or cooling load I wouldn't red flag that for an upgrade unless it was overloaded, but would list that as a "concern" due to expansion limitations) --
Robert O'Connor, PE
Eagle Engineering ®
Eagle Eye Inspections ®
NACHI Education Committee

I am absolutely amazed sometimes by how much thought goes into doing things wrong

Joe Farsetta
Advanced Professional Services Group, Inc.
User: jfarsetta
NACHI Member: Yes
Location: Pearl River, NY
Posts: 3743



Posted: Mon, Feb 16th, 12:37 AM Post subject: I see 60 amp service all the time in one particular condo complex. I let them know of my concerns, but if service and panel are in good shape, it's typically not a defect in my eyes.

Rob, Is it true that in NYC now, a 60 amp service is an automatic mandatory upgrade to 100 amps, as per AHJ and Con Ed? --
Reply With Quote
  #2  
Old 2/6/06, 1:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How about a 60 amp service?

If you have the 1500 sq/ft house in example D1(a) with a gas range and water heater you have no problem fitting nicely in a 60a service. (44.1a)
Where I was in Md that was a very common setup, sometimes even having a gas dryer, getting the calculated load in the 21a range. Central A/C is going to be the breaking point but you could probably still get away with it (complying with art 220 calc) if everything else was gas and you had an 18 seer unit or better.
I know the code requires 100a but that is relatively new compared to some of the houses I see you guys inspecting
Reply With Quote
  #3  
Old 2/6/06, 4:30 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: How about a 60 amp service?

Quote:
Originally Posted by jtedesco1
Rob, Is it true that in NYC now, a 60 amp service is an automatic mandatory upgrade to 100 amps, as per AHJ and Con Ed? --
My understanding is that any work on the service entrance conductors or panel would kick in the upgrade to 100A minimum, but that if just circuits are being added that it's not a mandatory upgrade, but a service capacity calc would have to be done to verify the 60A is still adequate.

JMO and 2-nickels ...

P.S. Looking at the electric meter base, in addition to the meter type, can give an indication of service capacity on the utility/feeder side. At least around my neck of the woods (your local mileage may vary) a round meter base generally indicates an older 60A service, a square meter base an older 100A service, and a rectangular meter base an older 200A service or for a newer installation at least a 100A service.

For example, seeing a round meter base and a 100A service panel is a red mind flag to look closer, and a probable panel upgrade without permits or upgrading the old 60A SE conductors.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 293 2/10/08 2:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
2-Wire Service - 2 Hots, No Neutral pdickerson Electrical Inspections 5 8/9/06 12:36 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 8:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 11:41 PM


All times are GMT -4. The time now is 7:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts