Default 60 amp service, very warm.....

Recent home inspection had a 60amp service. Slight scorch mark on dead front panel above drawer pull out fuse. It felt warm to the touch, infared temp had it at 108 degrees, the rest of drawer fuses were 73 degrees. Is this within acceptable temperatures?
Reply With Quote
  #2  
Old 7/21/07, 6:42 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by gwilcox
Recent home inspection had a 60amp service. Slight scorch mark on dead front panel above drawer pull out fuse. It felt warm to the touch, infared temp had it at 108 degrees, the rest of drawer fuses were 73 degrees. Is this within acceptable temperatures?
Absolutely not....Your average breaker or fuse cartridge should be at room temperature.

If your getting 108 degrees, recommend an Electrician to evaluate that particular fuse cartridge.

Did you open the cover to see what may be causing this heat build-up?
Reply With Quote
  #3  
Old 7/21/07, 7:04 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: 60 amp service, very warm.....

More info:

http://www.nachi.org/forum/showthread.php?t=4390&highlight=breaker+temperatur e

http://www.nachi.org/forum/showthread.php?t=7760&highlight=breaker+temperatur e



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 7/21/07, 7:20 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: 60 amp service, very warm.....

Thanks David, Larry. I did pull the dead front, but nothing stood out. I didn't pull the drawer, because of shutting off portions of the house. Bakalite looked worn and the pull and the face of the drawer looked well used! No# 4 copper service cable looked recent and the lugs were bright. Judging from the screwdriver slots on the lug screws he/she had some trouble getting them tight.
Reply With Quote
  #5  
Old 7/21/07, 7:32 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by dvalley
Absolutely not....Your average breaker or fuse cartridge should be at room temperature.
This is simply not so.

Here is a quote from one of the threads linked above. It is written by one of the foremost experts in the electrical field IMO:
Quote:
Originally Posted by Pierre Belarge
If you take a look at 310.16, the 75C column, you will see the F temps as well. If a conductor/breaker is loaded to the maximum current permitted, the conductor/breaker may reach this temperature (possibly 167F). So the conductor/breaker can actually be hot to the touch, well above the ambient temperature surrounding them.

Some breakers as they get older will buzz due to the pitting of the contacts, which also may increase the breaker temp. Depending on the load applied to the breaker in the picture posted, I would say the buzzing is from pitted or loose contacts, and the temp is not creating this problem. There are many variables, but this is my guess.
Reply With Quote
  #6  
Old 7/21/07, 7:48 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by Speedy Petey
This is simply not so.

Here is a quote from one of the threads linked above. It is written by one of the foremost experts in the electrical field IMO:

So you're stating that "Hot" breakers and fuse cartridges do not need an Electricians' evaluation?
Reply With Quote
  #7  
Old 7/21/07, 9:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by dvalley
So you're stating that "Hot" breakers and fuse cartridges do not need an Electricians' evaluation?
I absolutely did NOT say that. Look at the line I quoted. I am saying that breakers above "room temperature" are not necessarily a problem.
I guess it is up to you guys to determine how hot is too hot.

Warmer than room temp is not an immediate red flag IMO. Literally hot to the touch is.
Reply With Quote
  #8  
Old 7/22/07, 6:23 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 60 amp service, very warm.....

Speedy,

Well, when I stated ...
Quote:
"Your average breaker or fuse cartridge should be at room temperature. If your getting 108 degrees, recommend an Electrician to evaluate that particular fuse cartridge."
You stated
Quote:
"This is simply not so".
That (to me) translates that I'm wrong in what I stated...IMO.
Reply With Quote
  #9  
Old 7/22/07, 6:44 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

David, PLEASE go back and re-read post #5. You are looking at it with your man vision. You are seeing only what you want to see.

I ONLY quoted the line about the breaker being at room temp. And please note the post was not edited.
Reply With Quote
  #10  
Old 7/22/07, 6:51 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by Speedy Petey
David, PLEASE go back and re-read post #5. You are looking at it with your man vision. You are seeing only what you want to see.

I ONLY quoted the line about the breaker being at room temp. And please note the post was not edited.
But you posted "This is simply not so," referring to my opinion.

Am I right?
Reply With Quote
  #11  
Old 7/22/07, 10:00 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by Speedy Petey
You are looking at it with your man vision.
David, there has got to be a way to market this special ability!

Possible example for your website:

Our Inspectors use "Man Vision**" during the course of the inspection. This special ability insures our observations are superior to those who use just plain vision.

**
Man vision tablets are available at your local NACHI mall outlet store. For added boost try our "Testosterone Vision" tablets. Not associated with "Women Vision" and "Estrogen Vision" which has been known to cause side effects such as outbursts of uncontrolled emotions, chronic crying and wild shopping sprees.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #12  
Old 7/22/07, 11:06 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by dvalley
But you posted "This is simply not so," referring to my opinion.

Am I right?
Yes, I said your opinion that breakers should be at room temperature is flawed. I'm not sure how I could have been clearer.
Reply With Quote
  #13  
Old 7/22/07, 11:07 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by jonofrey
David, there has got to be a way to market this special ability!
I'm not sure about you guys, but my man vision gets me in trouble all the time.
Reply With Quote
  #14  
Old 7/22/07, 11:32 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60 amp service, very warm.....

Here in AZ, most main panels are attached to the outside of the home. When its 110 degrees outside, all the breakers show elevated temps because they've been in the heat. I will scan each breaker and look for a deviation from the average to see if any of them are overheating becuase here, they are usually all hot to the touch.
Reply With Quote
  #15  
Old 7/22/07, 4:37 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 60 amp service, very warm.....

Quote:
Originally Posted by Scott Schultz
Here in AZ, most main panels are attached to the outside of the home. When its 110 degrees outside, all the breakers show elevated temps because they've been in the heat. I will scan each breaker and look for a deviation from the average to see if any of them are overheating becuase here, they are usually all hot to the touch.
So, in your situation your room temperature would be the outside temperature. Right?
The sun is normally very hot and does actually heat up everything it reflects off of. So that would obviously make the breakers a tad warmer.

Oopps...I forgot, it's not a room.....Attachment 13342 I guess it must be an actual room to qualify for room temperature.

Last edited by dvalley; 10/7/07 at 4:40 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 7:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 10:41 PM


All times are GMT -4. The time now is 5:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts