Default 600 amp single phase service

Under const. 10k sf under roof, pool, boat dock, outdoor kitchen

Note the small meter conduit, uses 20 amp meter with current sampling.
The meter has a tag that says multiply reading by 40.

The large panel had an anti-tamper tag present so no pictures of inside.

Yes, this is called "single phase" which is commonly referred to by industrial types as "2 phase".
Attached Thumbnails
600-amp-single-phase-service-sept10-040-small-.jpg.jpg
Views:	225
Size:	31.1 KB
ID:	14438   600-amp-single-phase-service-sept10-041-small-.jpg.jpg
Views:	249
Size:	30.4 KB
ID:	14439  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 9/12/07, 3:21 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 600 amp single phase service

Quote:
Originally Posted by bking
Yes, this is called "single phase" which is commonly referred to by industrial types as "2 phase".
This is not a "2 phase" set up and anyone calling it that is incorrect.
Reply With Quote
  #3  
Old 9/12/07, 3:44 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 600 amp single phase service

The meter is fed from "Current Transformers" (CTs) which encircle each of the main conductors and, in this case, deliver 1/40th of the actual current to the meter. Such arrangements are very common for large residential / commerical / and industrial applications.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #4  
Old 9/12/07, 7:21 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 600 amp single phase service

Quote:
Originally Posted by Mike Whitt
This is not a "2 phase" set up and anyone calling it that is incorrect.
I whole heartedly agree.
Single phase is single phase.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to tell single from 3 phase krentz Electrical Inspections 20 7/30/07 5:07 PM
Free single family electrical service calculator. gromicko Electrical Inspections 2 3/28/07 9:39 PM
Free single family electrical service calculator for NACHI members. gromicko Special Discounts for InterNACHI Inspectors 1 3/26/07 6:53 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 8:12 PM


All times are GMT -4. The time now is 2:18 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts