Home #1: #2 copper conductor to main panel w/125 Amp main breaker.
#2 is allowed for 100 Amp max. breaker (60C rated assumed).
Is #2 ok for 125 Amp 75C rated breaker?

Home #2: #2 aluminum conductor to main panel w/100 Amp main breaker.
#2 is allowed for 90 Amp max. breaker (60C rated assumed).
Is #2 ok for 100 Amp 75C rated breaker?

I don't recall breaker ratings being discussed in the NACHI electrical course and am assuming the wire to breaker sizes mentioned in the course are for 60C rated breakers.

Any input greatly appreciated.
Reply With Quote
  #2  
Old 10/16/07, 11:24 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60c / 75c

Most breakers are 75C rated but if this is the main feeder or service conductor for a dwelling you can use 310.15(B)(6) to size the breaker.
#2cu is OK for 125a and #2al is ok on a 100.
Reply With Quote
  #3  
Old 10/17/07, 12:04 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 60c / 75c

As Greg stated, for the purpose of sizing residential service conductors temp ratings do not come into play. Wire types do, but all "typical" wire types are listed in 310.15(B)(6).
Reply With Quote
  #4  
Old 10/17/07, 10:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 60c / 75c

I also agree.......chances are the terminals you are dealing with ( because they are service terminations ) are 75 degree rated. Just use the table 310.15 (B)(6) for your sizing and you will be fine.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 6:03 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts