Default 70 amp service

Okay here we go. 70 amp service into a main panel near electric service meter. The 70 amp service feeds a 100 amp sub-panel in the home. That just happens to be FPE with Stablok breakers. Which i see alot in this section of town. Electrical contractor comes and tells client that 70 amp service is fine. Now there is a forced air gas furnace and gas water heater but a 70 amp service is under sized correct? Also how does this ground look in the pic i attached? Do u like the double tap?
Attached Thumbnails
70-amp-service-img_7020.jpg   70-amp-service-img_7019.jpg   70-amp-service-img_7038.jpg  
Reply With Quote
  #2  
Old 11/5/08, 2:26 PM
Justin D. Schlueter Justin D. Schlueter is offline
New User
 
Join Date: Jul 2008
Location: Minnesota
Posts: 11
Please Note: Justin D. Schlueter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 70 amp service

Are the service wires attached to the 70 amp breaker or are they connected to the main lugs at the top in the first picture?
Reply With Quote
  #3  
Old 11/5/08, 2:28 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 70 amp service

Quote:
Originally Posted by Justin D. Schlueter View Post
Are the service wires attached to the 70 amp breaker or are they connected to the main lugs at the top in the first picture?
Ah, good call Justin.
Reply With Quote
  #4  
Old 11/5/08, 3:04 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 70 amp service

Hi Harry,

I don't see anything wrong with that set up, the service is no doubt 100amp or greater with the 70 amp just feeding the interior panel, was this a mobile/manufactured home by any chance, as thats the way most of them are wired with the disconnects for both the interior panel and the AC beside the meter

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 11/5/08, 5:18 PM
Harry McBride's Avatar
Harry McBride Harry McBride is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 199
Default Re: 70 amp service

No this is a 1970 concrete block home. So a 70 amp service is sufficient for a 4 bedroom - 1 1/2 bath home. What am i missing here? Did i mention that the sub-panel is a Federal Pacific panel with Stablok breakers? Yes it is a 100 amp service with a 70 amp breaker to the sub-panel.
Reply With Quote
  #6  
Old 11/5/08, 5:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 70 amp service

Harry,
Depends.........if the dwelling is mostly gas appliances and heat then quite possibly the 100A is fine. Now you do have some issues with the 200.7 dealing with the white wire needing re-identified, 110.3(B) and 110.14 in regards to the breakers and double taps and so on as those breakers are not designed for this.

Now the connection in the second ( middle ) picture does not look good but I can't see it well.......so if you are thinking 100A panel is small.......you have to actually look at whats in the house....if you have an Electric Range, Electric Heat and so on then you may have something but if mostly gas then probably not an issue.



Paul W. Abernathy
Reply With Quote
  #7  
Old 11/5/08, 7:24 PM
Harry McBride's Avatar
Harry McBride Harry McBride is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 199
Default Re: 70 amp service

Okay gas furnace and gas water heater. Electric range and electric dryer. Compressor unit is off the main panel not the sub. I appreciate it Paul.
Reply With Quote
  #8  
Old 11/6/08, 12:23 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 70 amp service

I will just write up have a electrician come out and check the system very carefully and the main panel i can see a screw looks like overheated on the alum conductor above it.

now for subfeed box that breaker you see two wires going in the single pole breaker that is not listed for two conductors in single termation.

Merci,Marc
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 7:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 10:41 PM


All times are GMT -4. The time now is 5:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts