Default 80 AMP on 6 AWG

Here is an 80 AMP breaker on 6 AWG conductor feeding a furnace/heat pump condenser. The Furnace/heat pump condenser has a 60 AMP breaker. Therefore the load should not pull more than 60 AMPS? Right??
Attached Thumbnails
80-amp-6-american-wire-guage-pict0101-small-.jpg.JPG
Views:	187
Size:	72.0 KB
ID:	34870   80-amp-6-american-wire-guage-pict0136-small-.jpg.JPG
Views:	129
Size:	66.8 KB
ID:	34871  
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/11/10, 3:14 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: 80 AMP on 6 AWG

I don't see any problems here Mark.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 2/12/10, 9:47 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 80 AMP on 6 AWG

This is where the dataplate on the equipment need to be consulted for the proper Minimum Circuit Ampacity and the Maximum Overcurrent Size.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 5:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts