Here is an 80 AMP breaker on 6 AWG conductor feeding a furnace/heat pump condenser. The Furnace/heat pump condenser has a 60 AMP breaker. Therefore the load should not pull more than 60 AMPS? Right??
|
| Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I don't see any problems here Mark.
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is where the dataplate on the equipment need to be consulted for the proper Minimum Circuit Ampacity and the Maximum Overcurrent Size.
|
![]() |