Quote:
Size of Electrical Service: •120/240 Volt Main Service - Service Size: 180 Amp Main Disconnect: •Main Service Rating: Service limited by two 90 Amp service breakers installed in parallel. |
|
#62
|
||||
|
||||
|
Quote:
|
|
#63
|
||||
|
||||
|
Russell,
You say that it is a 90amp service because any single load on it that is greater than 90amps would overload the main panel. Right? That makes sense too. How about this: "180amp service with a limit of 90 amps for any single breaker" |
|
#64
|
||||
|
||||
|
I'm still not happy with the 180 amps, though. Adding two 90-amp breakers together to get 180 amps doesn't sit right with me.
Let's take a modern 42-breaker panel. Let's wire it with 3/0 for a maximum of 225 amps, just like this one, and give it a meter with a maximum of 200 amps, just like this one. Now, though, instead of two "main" breakers, let's give it 42 "main" breakers, all rated at 20 amps. Would you add up those 42 "main" breakers" to get 840 amp service? I wouldn't. On the other hand, I don't necessarily like calling it 20 amp service, although I think that's what it is. I don't think there is a checkbox solution, so I'm sticking with my 90 amps. However, I would modify my standard language to state something like "Meter service capacity is 200 amps while wiring service capacity is 225 amps. However, service capacity appeared to be limited to 90 amps due to the non-standard wiring of two 90-amp circuit breakers." Then I would add my standard less-than-100-amps caution regarding insurance. Last edited by rray; 3/9/06 at 8:58 AM.. |
|
#65
|
|||
|
|||
|
We know you are loaded with the BUCKS Ray Ray.......so I am sure you would upgrade fella...
Paul W. Abernathy |
|
#66
|
||||
|
||||
|
Please Note:
ddelaney is a non-member guest and is in no way affiliated with InterNACHI or its members.
Actually, the rating of any service is only the individual rating of the breaker (the actual #), not the wire size. The wire, when installed correctly, should be sized properly so that the overall load does not exceed 80%.
However, as home inspectors, we just need to know that the breaker rating is the service size. The thermal/mechanical overload limit in a 2 pole breaker is sized to trip when the total load exceeds the individual rating marked on the breaker. So, in theory, a 90 amp 2 pole breaker shouldn't be able to exceed a total of 90 amps. Hope this helps. |
|
#67
|
|||
|
|||
|
Please Note:
Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#68
|
||||
|
||||
|
Quote:
Quote:
Quote:
But in this case adding up the service panels breakers doesn't exceed the meter/feeders ... it actually limits the capacity, which is why my call is 180A capacity. Now if there was a single 180A main breaker in the panel with the 2-90A twin breakers to sub-panels (not service panels), what would be the service capacity ... obviously 180A as that limits the capacity ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#69
|
|||
|
|||
|
Incorrect...my agreeable point is (2) 90 Amp sub-panels based on the rating of the OCPD...I do not get into telling the client what the system COULD be if they wish to upgrade it or change it....My job is to tell them what they have RIGHT NOW.....and I see (2) 90 Amp panels with a combined service rating of 180 Amps.....
This is also not a normal set up....My report would have 180A Service with (2) 90A sub panels.....sure I could say you have 180A service....BUT based on this set up I am not going to list it as such....You are FREE to do what you wish.....from experience I am not going to list it that way....maybe it is just me. As far as I am concerned the client has the ability to have 90A from either location...yes, it is 180A capacity BUT I am more concerned with them overloading a 90 A panel....that is what I am saying. Paul W. Abernathy Last edited by pabernathy; 3/9/06 at 10:08 PM.. |
|
#70
|
||||
|
||||
|
Quote:
|
|
#71
|
|||
|
|||
|
I hear ya Ray Ray...but dont take my word for it..I don't know JACK.....
Paul W. Abernathy |
|
#72
|
||||
|
||||
|
Quote:
Quote:
Even then it would likely just be an issue with shifting some of the load/circuits from the older sub-panel (which does appear to be a little packed) over to the newer sub-panel. But that wouldn't affect the 180A service capacity. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#73
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Quote:
The bottom 4 breaker on the older subpanel are in the off position and two of those four don't even have condutors attached to them. Also, BOTH subpanels had deadfront labels that indicated 'spare' on at least a couple of breakers. And I KNOW we all believe that all deadfront markings are properly labeled... I don't feel there is a load to sub panel capacity issue on either subpanel NOW! I bet there was one before the second/newer subpanel was added though. |
|
#74
|
||||
|
||||
|
Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| HVAC Proper AMPS | lking | Inspecting HVAC Systems | 2 | 11/25/07 8:53 PM |
| Sub Panel Amps | mtimpani | Electrical Inspections | 7 | 10/1/06 9:47 AM |
| How many Amps??? | psmothers | Electrical Inspections | 7 | 8/9/06 2:01 PM |
| Another Service Entrance Amps Question | pdickerson | Electrical Inspections | 2 | 8/7/06 3:39 PM |
| Service Entrance Amps? | dtaylor | Electrical Inspections | 12 | 8/5/06 3:38 PM |