Quote:
Originally Posted by Jim Port View Post
I think that change might be rescinded in the 2014 code. If it were it would not add any substantiation to why it changed in the first place.
They seem to go back and forth on some issues ... like the previous changes related to service wire ampacities ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #32  
Old 8/26/11, 10:23 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 90 amp breaker

Quote:
Originally Posted by roconnor View Post
They seem to go back and forth on some issues ... like the previous changes related to service wire ampacities ...
Yes like the most recent code cycle (2011) where they changed the ampacities of #14 and #12 conductors to match the Canadian electrical code. Since when do we care about the Canadian electrical code? Sorry all of our Canuck friends.
Reply With Quote
  #33  
Old 8/26/11, 10:26 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 90 amp breaker

Quote:
Originally Posted by Robert Meier View Post
Yes like the most recent code cycle (2011) where they changed the ampacities of #14 and #12 conductors to match the Canadian electrical code. Since when do we care about the Canadian electrical code? Sorry all of our Canuck friends.
I understand it is a good code so why not use the best there is... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #34  
Old 8/26/11, 10:50 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 90 amp breaker

Quote:
Originally Posted by rcooke View Post
I understand it is a good code so why not use the best there is... Roy
Easy there. If ya rile up enough people here we might just have to invade "Canadian Bacon" style ... http://www.invadecanada.us/



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #35  
Old 8/26/11, 11:00 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 90 amp breaker

Quote:
Originally Posted by roconnor View Post
Easy there. If ya rile up enough people here we might just have to invade "Canadian Bacon" style ... http://www.invadecanada.us/
Our Best friends where here from Florida for ten days .
They love shopping in Canada She loads up with spices and special tea from our Bulk food store .
She spent about $800;00 on things she can not get in USA .
She gets it for many others .
This should last till December when we will take her down some things she needs .
We have been doing this for over 30 years .
Gosh it would be great if she still lived in NJ .
Strange how that bacon is so popular here and not there.
Thanks for the memories.. .. Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #36  
Old 8/27/11, 8:34 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: 90 amp breaker

Have you ever watched Rick Mercer Report?
This will give you an idea why we have a problem.
In some areas US is way ahead of us and in others it is behind.
I agree with the most stringent applications.
Nice to see color in you money now. LOL



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #37  
Old 8/28/11, 11:48 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 90 amp breaker

Quote:
Originally Posted by rcooke View Post
Strange how that bacon is so popular here and not there.
Yea, that is strange ... ... But all kidding aside my favorite place to visit was Montreal ...

Quote:
Originally Posted by Robert Meier View Post
... like the most recent code cycle (2011) where they changed the ampacities of #14 and #12 conductors to match the Canadian electrical code.
Was that the reason they gave?



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #38  
Old 8/28/11, 12:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 90 amp breaker

Quote:
Originally Posted by roconnor View Post
Yea, that is strange ... ... But all kidding aside my favorite place to visit was Montreal ...


Was that the reason they gave?

It seems that the original ampacity table 310.16 was originally derived from the CEC. So they lowered the ampacities of a few condcutors to be in harmony with the CEC. IMO this is a worthless change because the substantiation has no real safety value. The old ampacities were fine the way that they were. Here's part of the ROP:

Quote:
Substantiation: Acceptance of this proposal will harmonize the ampacity
values between NEC Table 310.16 and CEC Tables 2 and 4 with technically
substantiated values.
The ampacities for both copper and aluminum conductors with a conductor
temperature rating of 75ºC are identical between the NEC and CEC.
The ampacities for conductors with temperature ratings of 60ºC and 90ºC
were calculated from the 75ºC values using the equation shown on the pages
provided as supporting material that also contain supporting tables. The
equation is defined in the following standards:
IEEE Std 835-1994, IEEE Standard Power Cable Ampacity Tables,
Section 3.4.2 Adjustment for change in maximum conductor temperature or
temperature due to dielectric loss.
AIEE-IPCEA Power Cable Ampacities, 1962 (AIEE Pub. No. S-135-1 /
IPCEA Pub. No. P-46-426) Volume 1 – Copper Conductors, Adjustment for
Change in Parameters, page III.
60ºC copper conductor temperature – There are only two differences (5 amps)
in ampacities between the NEC and the CEC and the CEC matches the rounded
calculated values on these two conductor sizes. There are three values where
the NEC and CEC agree but all three differ from the rounded calculated values
by 5 amps. A proposal is also being submitted to correct the CEC on the five
minor deviations.
90ºC copper conductor temperature – There are only two differences (5 amps)
in ampacities between the NEC and the rounded calculated ampacities. The
CEC is lower on all values and a proposal is being submitted to correct the
CEC to agree with the rounded calculated values and the revised NEC. The
CEC agrees with the values in the 1978 NEC.
60ºC aluminum conductor temperature – There are three differences (5 amps)
in ampacities between the rounded calculated ampacities, and the NEC and the
CEC have the same values for these three sizes (8 & 4/0 AWG and 700 kcmil).
On 12 AWG, the NEC is 5 amps higher (20 vs 15 amps) than the rounded
Reply With Quote
  #39  
Old 8/28/11, 12:42 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 90 amp breaker

Sounds like the values are a little different from rounding off equations, and changes to both the NEC and CEC are being made so they are consistent. May not be such a bad thing.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Re-Inspection apolillo Electrical Inspections 7 11/14/09 7:01 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM