Default What the...?

I've never seen something like this and I'm hoping someone can either confirm or deny that this is a major problem. The photo shows all the neutral circuit wires connected where the feed neutral wire should be (not to mention all the ground wires connected to the lug next door), and the neutral feed is nowhere to be found.

Any help would be greatly appreciated, thanks.
Attached Thumbnails
a-gunther4-018.jpg  
Reply With Quote
  #2  
Old 6/6/07, 12:04 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: What the...?

The sparkies here will confirm this is a major problem and needs to be further inspected and repaired as needed by a qualified electrical contractor.
Reply With Quote
  #3  
Old 6/6/07, 1:03 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

I see enough stuff wrong in that one little picture that you can safely defer that whole thing to an electrician. Looks like some serious DIY to the rescue work there.
Reply With Quote
  #4  
Old 6/6/07, 1:53 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

Don't just stop there. Why is this dangerous? I can guess three things.

1) if the ground wire to the panel is cut, everything become live?
2) The neutral and ground are essentially shared on the same wire. So the current flowing on neutral wire would easily cause a large voltage difference (up to many volts) on different outlets grounds. The ground potential on any outlet will then depend on the load current, neutral wire resistance and the mains phase it is connected to.
3) The neutral is effectively shorted to ground implying nasty ground loop problems.

Am I right? Any more?
Reply With Quote
  #5  
Old 6/6/07, 2:37 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

Where is the neutral from the service? That is the most serious issue I see. The list certainly does go on.
Reply With Quote
  #6  
Old 6/6/07, 2:58 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

Isn't the neutral for the service entering through the middle left, looping right and then secured to the metal thingy?
Reply With Quote
  #7  
Old 6/6/07, 4:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

The fat bare wire looks like a 4ga ground electrode conductor. That implies a 200a service and I would expect to see a 2/0 copper or 4/0 aluminum white insulated conductor on that bus.
Reply With Quote
  #8  
Old 6/6/07, 4:53 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

I would like to inspect my panel i.e. look at it, not touch.

Is it safe to unscrew the cover with the main breaker on, or should I switch this off, so I only have the two main supply wire entering as live?

Or should I just leave it be?
Reply With Quote
  #9  
Old 6/7/07, 4:33 PM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 36
Default Re: What the...?

Quote:
Originally Posted by Greg Fretwell
Where is the neutral from the service? That is the most serious issue I see. The list certainly does go on.
There isn't one. It's turned into a ground wire before it enters the mass head, exactly like the picture I posted in another thread this morning (entitled Service Entrance Question ). This is a bad scenario right? Why is it even setup this way?
Reply With Quote
  #10  
Old 6/7/07, 11:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What the...?

If that is true, where is the grounding electrode conductor? That grounded conductor also looks smaller that the ungrounded conductors.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts