#1
|
|||
|
|||
|
Could someone explain to me why the data plate on a central A/C condenser always specifies a maximum breaker size while the data plates on refrigerators and freezers don't. Thanks.
|
|
#2
|
||||
|
||||
|
John,
Because of the Condenser on the central A/C is usually larger and is directly wired...so it simply shows the MAX size OCPD you can protect the unit......usually larger to allow for start up and so on. Fridges and Freezers already factor this in and they already have the plugs attached...and usually smaller condensers... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#3
|
||||
|
||||
|
very nice, short and to the point
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
|
#4
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree entirely with Paul, I will just add because they are required to be marked the way they are.
|
|
#5
|
||||
|
||||
|
It's good to hear from you again Bob. Take off your jacket and stay a while. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If you try to absorb article 440 and the sizing of conductors vs O/C devices you will appreciate how great it is that they do the engineering for you.
|
|
#7
|
||||
|
||||
|
Oh YES...........I will say for Electricians around the US...Thank you Engineers for already doing the math for us......One less thing to think about...
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
|||
|
|||
|
Quote:
|
|
#11
|
||||
|
||||
|
No problem my friend....thats what we are here for......Actually it is the main reason I came here...To help when needed..
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| WA Structural Pest Inspector Law | hmiller | Legislation, Licensing & Legal Issues | 18 | 4/1/07 3:10 AM |
| Plumbing vent Routing Question | kweiss | Plumbing | 7 | 11/1/06 10:57 PM |
| Rule of Thumb A/C sizing question from Practice Exam | gliebig | HVAC | 9 | 5/25/06 2:38 AM |