Default Academic Question

Could someone explain to me why the data plate on a central A/C condenser always specifies a maximum breaker size while the data plates on refrigerators and freezers don't. Thanks.
Reply With Quote
  #2  
Old 3/26/06, 11:32 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Academic Question

John,

Because of the Condenser on the central A/C is usually larger and is directly wired...so it simply shows the MAX size OCPD you can protect the unit......usually larger to allow for start up and so on.

Fridges and Freezers already factor this in and they already have the plugs attached...and usually smaller condensers...



Paul W. Abernathy
Reply With Quote
  #3  
Old 3/26/06, 1:00 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Academic Question

very nice, short and to the point




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #4  
Old 3/26/06, 3:56 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Academic Question

I agree entirely with Paul, I will just add because they are required to be marked the way they are.
Reply With Quote
  #5  
Old 3/26/06, 4:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Academic Question

It's good to hear from you again Bob. Take off your jacket and stay a while. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/26/06, 9:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Academic Question

If you try to absorb article 440 and the sizing of conductors vs O/C devices you will appreciate how great it is that they do the engineering for you.
Reply With Quote
  #7  
Old 3/27/06, 10:52 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Academic Question

Oh YES...........I will say for Electricians around the US...Thank you Engineers for already doing the math for us......One less thing to think about...



Paul W. Abernathy
Reply With Quote
  #8  
Old 3/27/06, 5:48 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Academic Question

Quote:
Originally Posted by Greg Fret well
If you try to absorb article 440 and the sizing of conductors vs O/C devices you will appreciate how great it is that they do the engineering for you.
I sure do appreciate it.
Reply With Quote
  #9  
Old 3/27/06, 5:48 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Academic Question

Quote:
Originally Posted by jpope
It's good to hear from you again Bob. Take off your jacket and stay a while. . .
Thanks Jeff.
Reply With Quote
  #10  
Old 3/29/06, 7:29 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Academic Question

Quote:
Originally Posted by pabernathy
John,

Because of the Condenser on the central A/C is usually larger and is directly wired...so it simply shows the MAX size OCPD you can protect the unit......usually larger to allow for start up and so on.

Fridges and Freezers already factor this in and they already have the plugs attached...and usually smaller condensers...
Thanks again Paul.
Reply With Quote
  #11  
Old 3/29/06, 9:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Academic Question

No problem my friend....thats what we are here for......Actually it is the main reason I came here...To help when needed..



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 9:57 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM


All times are GMT -4. The time now is 2:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts