Question Adding an extra disconnect

Hi all,

I have learned a lot from this board, thank you all very much for sharing your knowledge.

I am upgrading my garage by adding a subpanel. I am running 6/3 Romex (the wire will never go in ground or outside the structure so Romex should be fine) from the main panel on a 50 AMP 2-pole breaker. I believe 6/3 Romex is rated up to 55 Amps, and while I *think* you can round-up to the next available breaker (60 amp), I don't think I will need it. I am only planning to run lights, a 240-volt air compressor, a bunch of 120-volt tools. That's about it. No major appliances that would ever go over 40-amp even. I am using a 125-amp rated panel with NO main-breaker in the panel.

I would like to add a disconnect to the garage itself so I can shut the power off to the garage easily without having to walk over to the main house panel and shut off the 50-amp breaker. I was planning on buying this:

http://www.homedepot.com/webapp/wcs/...00&R=100676700

Here is my question:

The switch has 3 poles. One for each hot, and one for the neutral. Since I am running Romex with 3 wires plus the bare ground, what do I do with the ground (bare copper)? Do I add a grounding bus bar into the switch panel? If so, do I bond the grounding bus bar to the panel? Then when I continue from the disconnect switch to the sub-panel itself do I just run the ground off that grounding bus bar to the sub-panel?

Thank you all in advance for the help and suggestions.
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/1/12, 9:52 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adding an extra disconnect

This board is more for home inspection type questions, not a DIY how-to board.

It would be easier to use a panel with a main breaker built in.
Reply With Quote
  #3  
Old 1/1/12, 10:14 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adding an extra disconnect

I agree with Jim this isn't the place for DIY advice and also, go with the MAIN CB in the panel. Other than that you might consider getting some help from an electrical professional.
Reply With Quote
  #4  
Old 1/1/12, 5:16 PM
Chad Nicholas Chad Nicholas is offline
New User
 
Join Date: Jan 2012
Posts: 2
Please Note: Chad Nicholas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adding an extra disconnect

I understand, I was more asking what is up to code rather than how-to. I should have explained that. I can get the electricity to work, I'm not worried about that, I just want to be sure to pass inspection when it comes.
Reply With Quote
  #5  
Old 1/2/12, 8:45 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Adding an extra disconnect

What Jim and Robert stated above. Trust them. They know their stuff.

Also, most Home Inspectors are not Code inspectors. Although we are knowledgeable about code, and use it as a reference, we typically don't care what code is. We want it right, and safe.

Now, if I was inspecting a (older) home/garage, and I noticed there was a new panel/subpanel installed, some of my first thoughts would be... "was a permit obtained for the work, and did the AHJ perform their inspections"? These questions are clues (early warning signs) as to what I may or may not find during my inspection. If I am unable to determine, I always recommend my client request copies of permits from the seller.

So, did you pull a permit for your upgrade? Most all municipalitys require them for panel/subpanel work.

Does your municipality allow the homeowner to perform panel/subpanel upgrades? I am finding that more often lately, they do not. A licensed electrician is required.

Good luck.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
50 amp disconnect for 1600sf condo kmccullough Electrical Inspections 5 4/10/07 8:49 PM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 12:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 12:32 PM


All times are GMT -4. The time now is 5:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts