Default adding a ground wire

on an older two wire system can a single bare copper ground wire be added and run to the crawlspace and hooked to a looped ground wire connected to the ground bar in the panel ?
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/26/10, 9:38 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: adding a ground wire

Sounds wrong. Running a ground wire is one thing... but bare copper?

For what purpose?
Reply With Quote
  #3  
Old 7/26/10, 10:16 PM
Ron E. Perkerewicz Ron E. Perkerewicz is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Bremerton, WA
Posts: 89
Default Re: adding a ground wire

he wants to update the old two wire with grounded outlets and not totaly rewire the whole house or open all the walls.
Reply With Quote
  #4  
Old 7/26/10, 11:01 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: adding a ground wire

Isthis for all receptacles or just ones in the crawlspace?
Reply With Quote
  #5  
Old 7/26/10, 11:27 PM
Ron E. Perkerewicz Ron E. Perkerewicz is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Bremerton, WA
Posts: 89
Default Re: adding a ground wire

all the rec on the main floor, bring the wire down and tie to one ground wire in the crawl and run it to the panel
Reply With Quote
  #6  
Old 7/27/10, 12:13 AM
gfransway gfransway is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Tucson, AZ
Posts: 43
Default Re: adding a ground wire

Sounds like if done and all connections are secure, it would be an effective ground. If I were to find this during an inspection, I would report it as "amateurish wiring added that should be further evaluated by a licensed specialist."
Reply With Quote
  #7  
Old 7/27/10, 4:53 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: adding a ground wire

Quote:
Originally Posted by gfransway View Post
Sounds like if done and all connections are secure, it would be an effective ground. If I were to find this during an inspection, I would report it as "amateurish wiring added that should be further evaluated by a licensed specialist."
You might want to read Article 250.130(C) before wasting your clients money.

(C) Nongrounding Receptacle Replacement or Branch
Circuit Extensions.
The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar

within the service equipment enclosure
Reply With Quote
  #8  
Old 7/27/10, 4:56 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: adding a ground wire

Here's what the 2008 NEC says:

Quote:
250.134 Equipment Fastened in Place or Connected by Permanent Wiring Methods (Fixed) — Grounding.
Unless grounded by connection to the grounded circuit conductor as permitted by 250.32, 250.140, and 250.142, non–current-carrying metal parts of equipment, raceways, and other enclosures, if grounded, shall be connected to an equipment grounding conductor by one of the methods specified in 250.134(A) or (B).
(A) Equipment Grounding Conductor Types. By connecting to any of the equipment grounding conductors permitted by 250.118.
(B) With Circuit Conductors. By connecting to an equipment grounding conductor contained within the same raceway, cable, or otherwise run with the circuit conductors.
Exception No. 1: As provided in 250.130(C), the equipment grounding conductor shall be permitted to be run separately from the circuit conductors.
Exception No. 2: For dc circuits, the equipment grounding conductor shall be permitted to be run separately from the circuit conductors.
Quote:
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar within the service equipment enclosure
FPN: See 406.3(D) for the use of a ground-fault circuit-interrupting type of receptacle.
Reply With Quote
  #9  
Old 7/27/10, 9:27 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: adding a ground wire

Why not just drive a ground rod and run a proper wire to the panel?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #10  
Old 7/27/10, 4:22 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: adding a ground wire

Quote:
Originally Posted by fnewman View Post
Why not just drive a ground rod and run a proper wire to the panel?
What would the ground rod actually do?
Reply With Quote
  #11  
Old 7/27/10, 9:06 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: adding a ground wire

Hmmm - guess I didn't understand the question exactly...



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #12  
Old 7/28/10, 9:18 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: adding a ground wire

Quote:
Originally Posted by fnewman View Post
Why not just drive a ground rod and run a proper wire to the panel?
Frank, ground rods are to ground the system against high voltage events like lightning strikes or surges. They have nothing to do with an equipment grounding conductor that runs to the third prong on a receptacle.
Reply With Quote
  #13  
Old 7/29/10, 9:03 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: adding a ground wire

As I said, I misunderstood the original question, so my comment was not applicable.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/31/10, 10:56 AM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default Re: adding a ground wire

would changing to GFCI outlets be an acceptable solution. Its my understanding they don't provide a ground but do provide personal protection and would allow for modern appliancec to be used, but not grounded
Reply With Quote
  #15  
Old 7/31/10, 11:19 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: adding a ground wire

Quote:
Originally Posted by sdonnelly View Post
would changing to GFCI outlets be an acceptable solution. Its my understanding they don't provide a ground but do provide personal protection and would allow for modern appliance to be used, but not grounded
Yes, that would be an acceptable solution as outlined by the NEC. As you've stated it would provide personal protection, but a GFCI device cannot be used as a substitute for grounding.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 5:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts