  #1  
Old 2/9/12, 7:43 AM
Jason Frat Jason Frat is offline
New User
 
Join Date: Feb 2012
Posts: 2
Please Note: Jason Frat is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Adding to kitchen circuit

I currently have 4 15amp duplex kitchen receptacles running through a gfci. These are on 12-2 wire on a 20 amp breaker.

Two additional outlets were recently added above the kitchen cabinets that are on a switch.

I noticed that the receptacles that were added recently were tapped into the last receptacle in the above mentioned loop and they are being ran with 14-3 wire, 15amp duplex receptacles (these receptacles are on a switch, which is getting its power from that last outlet mentioned before). Is this ok or does that need to be 12-3 wire?

Thanks, I want to make this right.

Jason
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/9/12, 1:33 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Adding to kitchen circuit

Quote:
Originally Posted by Jason Frat View Post
I currently have 4 15amp duplex kitchen receptacles running through a gfci. These are on 12-2 wire on a 20 amp breaker.

Two additional outlets were recently added above the kitchen cabinets that are on a switch.

I noticed that the receptacles that were added recently were tapped into the last receptacle in the above mentioned loop and they are being ran with 14-3 wire, 15amp duplex receptacles (these receptacles are on a switch, which is getting its power from that last outlet mentioned before). Is this ok or does that need to be 12-3 wire?

Thanks, I want to make this right.

Jason

Are they convenience receptacles or are they on a small appliance branch circuit? Either way, what you have described is not OK.

You should hire an electrician to do the work. I am not telling you that because I used to be an electrician. I am telling you to get an electrician because I do electrical fire investigations. Most of the fires I have investigated have been caused by wiring that complied with the National Electrical Code and other building codes. There is a reason that most jurisdictions require 16,000 hours practical experience to get an electrical contractor's license (8,000 hours for a journeyman).



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #3  
Old 2/9/12, 2:39 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Adding to kitchen circuit

I agree that if you have a concern bring out a licensed guy to check the work. It sounds like they wanted lights or something above the cabinet. The plugs allow the option of changing out the lighting which is something I see often. The closest outlet is often used to get power for the installation of a new light. To answer your question, there is a need for 12/3 in this installation as described.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #4  
Old 2/9/12, 3:09 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Adding to kitchen circuit

You can't use 14 AWG wire on a 20 amp circuit. It's a fire hazard.

Also, there are restrictions on what can be on the two required dedicated circuits serving the kitchen counters. You should contact an electrician. The wire size is definitely wrong.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 2/9/12, 4:18 PM
Jason Frat Jason Frat is offline
New User
 
Join Date: Feb 2012
Posts: 2
Please Note: Jason Frat is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adding to kitchen circuit

Thank you for the responses, I will have someone come out and correct the issue.

I appreciate it!
Reply With Quote
  #6  
Old 2/9/12, 4:34 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Adding to kitchen circuit

Sorry but I can't answer DIY type of questions on this site



Mike Whitt
Contractor/Instructor
Reply With Quote
  #7  
Old 2/10/12, 10:43 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Adding to kitchen circuit

Quote:
Originally Posted by jwhitt View Post
Sorry but I can't answer DIY type of questions on this site
What do-it-yourselfers don't seem to understand is that a little knowledge is dangerous. Like you, Mike, I come here to help home inspectors. It may come across as arrogant or unhelpful to those who come here looking for DIY instructions but we are, in reality, doing them a big favor by telling them to hire a properly trained professional.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 5:22 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts