Default Adequate clearance?

Inspected a new construction today and there was a slop sink installed in a garage just to the left of twin 200 AMP service panels. Approximate distance from the edge of the slop sink to the closest edge of the electrical panel was about 26".

The builder took out the sink and capped the supply and waste stubs just prior to the final village inspection, then afterwards re-installed the sink. According to IRC 3305.2 the clearance should be 30" wide. Technically this does not mean 30" from the sides of the panels. Still the installation and location of the sink bothers the hell out of me.

Does this meet code? Since I'm not a code enforcement official and just a lowly home inspector how would you all report on this?
Attached Thumbnails
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/26/10, 2:15 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adequate clearance?

Yes, it meets code. My opinion is there is nothing to report.

www.MauiHomeInspections.com
Reply With Quote
  #3  
Old 5/26/10, 4:45 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adequate clearance?

There is no problem with the sink adjacent to a panelboard. The 30" working space requirement is for in front of the panel not 30" from the edge of the panel. Since there are two panels side by side the required space would only need be directly in front of the two panels measured from the outer edges of the panels. Also the panelboard does not need to be centered within the 30" space. The sink could be right against the left edge of the panelboard if you could still maintain the 30" spacing to the right of the sink. Here's a graphic from the NECH:

Reply With Quote
  #4  
Old 5/26/10, 7:09 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Adequate clearance?

The 30" working space is not required to be centered.
Attached Thumbnails
adequate-clearance-working-space-nec-110.26.jpg  



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 5/26/10, 8:23 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adequate clearance?

At the risk of repeating what everyone else has already said, as long as the cabinet with the laptop on it is not installed, the NEC clearences and work space requirements look like they have been met. No issue.
Reply With Quote
  #6  
Old 5/29/10, 1:28 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Adequate clearance?

When two panels are installed side-by-side, what is the total clearance required - 30" for the group? Something else?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 5/29/10, 2:17 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Adequate clearance?

Quote:
Originally Posted by fnewman View Post
When two panels are installed side-by-side, what is the total clearance required - 30" for the group? Something else?
The clearance required is 30" or the width of the two panels, whichever is greater.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Clearance Testing tfarmer Ancillary Inspection Services & Additional Topics 15 2/26/08 5:41 PM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 9:55 PM
Service panel clearance wwarner Electrical Inspections 13 8/12/06 12:07 PM
Siding to Ground Clearance tneumann Exterior Inspections 14 2/8/06 11:48 PM


All times are GMT -4. The time now is 5:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts