The home i inspected today had three AFCI's in the panel, I noticed when I tripped them that they were quite warm. I used my infrared thermo to see how warm they were, the top one read 108, the middle 112, and the bottom 106. Should they be this warm when the home is vacant?



Mark Simmons
JAM Home Inspections
Maricopa Az 85139
NACHI 03121906
Reply With Quote
Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America)
  #2  
Old 5/8/09, 10:56 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Afci ?????????

Some brands run warmer than others even with no load, usually the top one is the warmest if they are stacked vertically. If they test ok you can't really say those temps are unusual unless you have some data.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #3  
Old 5/8/09, 11:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Afci ?????????

They are fine.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 5/8/09, 11:09 PM
Mark A. Simmons Mark A. Simmons is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Maricopa AZ
Posts: 32
Default Re: Afci ?????????

Quote:
Originally Posted by bking View Post
Some brands run warmer than others even with no load, usually the top one is the warmest if they are stacked vertically. If they test ok you can't really say those temps are unusual unless you have some data.
Bruce, Thanks for the quick reply, they did work fine, it just surprised me at how warm they were.

Thanks again.



Mark Simmons
JAM Home Inspections
Maricopa Az 85139
NACHI 03121906
Reply With Quote
  #5  
Old 5/8/09, 11:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Afci ?????????

AFCI's can reach temps 15-20 degrees higher than a normal breaker. In Arizona since the ambient temps are higher you might get higher readings than lets say the ambient in new york for example. however, while the range may vary the results will be generally the same.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 5/12/09, 7:29 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Afci ?????????

Whenever a breaker (or other electrical device) contains active circuitry, some heat rejection should be expected. In this case, the electronics that are monitoring the voltage and current waveforms require power to operate. Since this power comes from the 120 v supply of the breaker itself, it has to be stepped down. That activity, as well as those of other circuit components, reject heat much like the heat generated by a desktop computer. So yes, they will operate hotter than a more passive breaker (or even a gfci) but are designed to operate safely under relatively high ambient conditions.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 5/12/09, 7:38 PM
Harry E. McClard's Avatar
Harry E. McClard Harry E. McClard is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Raymond, NH
Posts: 54
Default Re: Afci ?????????

Do you guys ever have trouble resetting them? I've had some that need what seems like a little "cool down time" after doing the test button...they always eventually reset but some just take a few tries.



Harry "Bud" McClard

Reply With Quote
  #8  
Old 5/13/09, 12:03 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Afci ?????????

Quote:
Originally Posted by hmcclard View Post
Do you guys ever have trouble resetting them? I've had some that need what seems like a little "cool down time" after doing the test button...they always eventually reset but some just take a few tries.
Never had a problem so far - but haven't seen a lot of them around here yet (or haven't inspected enough newer homes)



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #9  
Old 5/13/09, 12:40 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Afci ?????????

Quote:
Originally Posted by hmcclard View Post
Do you guys ever have trouble resetting them? I've had some that need what seems like a little "cool down time" after doing the test button...they always eventually reset but some just take a few tries.
One brand, forget right now, has a rocker type test switch that gets stuck to one side, you might not notice it and after pushing on the lever a few times trying to reset, it will pop back in place and presto it works again!



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Controversy rcooke Electrical 11 9/10/07 3:14 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical 19 2/15/07 1:05 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 1:40 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts