Default AFCI in Bedroom Sitting Area

The master bedroom suite includes a large sitting area not seperated from the sleeping area by a door. Is Arc Fault protection required (house built in 2005) in the sitting area?
Reply With Quote
  #2  
Old 3/10/09, 8:51 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: AFCI in Bedroom Sitting Area

That would be part of the bedroom. You would have to check what your
jurisdiction follows codewise, and when it was implemented, if that interests you.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 3/10/09, 9:01 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: AFCI in Bedroom Sitting Area

If closets are considered part of the bedroom, this room would be also provided there is no other means of egress into the room.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/10/09, 10:15 AM
Calvin D. Cowles's Avatar
Calvin D. Cowles Calvin D. Cowles is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newnan, Ga
Posts: 46
Default Re: AFCI in Bedroom Sitting Area

Thanks guys. I thought it was required but couldn't find specific code language.
Reply With Quote
  #5  
Old 3/10/09, 1:35 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI in Bedroom Sitting Area

AFCI - From the 2002 NEC. (ALL outlets - bold is mine)
- 210.12 Arc-Fault Circuit-Interrupter Protection.
- - (B) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.

From the 1999 NEC. (ONLY "receptacle" outlets - bold is mine)
- 210-12. Arc-Fault Circuit-Interrupter Protection
- - (b) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere receptacle outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter(s). This requirement shall become effective January 1, 2002. Fittings; and Handhole Enclosures

Reply With Quote
  #6  
Old 3/13/09, 11:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI in Bedroom Sitting Area

Yes, it is required to be AFCI protected for the outlets ( 15 & 20A. 125V ) within that bedroom.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical Inspections 19 2/15/07 12:05 PM
Houses with AFCI Breakers.... Basic testers shut off AFCI breakers?!? jwatts1 Electrical Inspections 22 12/20/06 7:39 PM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM
Phoenix area Chapter Meeting - Jan 24th cvowell General Inspection Discussion 0 1/11/06 5:00 PM


All times are GMT -4. The time now is 5:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts