Default AFCI in Bedrooms and four point?

Do we unscrew and open all bedroom switches to check this or is checking just one enough?

Thanks
Reply With Quote
  #2  
Old 7/17/08, 9:59 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: AFCI in Bedrooms and four point?

Quote:
Originally Posted by jtormo
Do we unscrew and open all bedroom switches to check this or is checking just one enough?

Thanks
Jason,

I hate to say it but it appears that you know enough to be dangerous!!

you test the bedroom AFCI's by pressing the test button on the breaker.

We have a very comprehensive online electrical course that as a member you are REQUIRED to take, please do so real fast.

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 7/17/08, 10:17 PM
jtormo jtormo is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Fort Lauderdale, FL
Posts: 14
Default Re: AFCI in Bedrooms and four point?

Thanks, I'll take it right now so I can be sure of what I am doing when I begin to do these inspections.

Thanks
Reply With Quote
  #4  
Old 7/17/08, 11:27 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: AFCI in Bedrooms and four point?

Jason,

I see your a working member. I went through all the requirements in just a week. You can to and this is the first step you need to do is work towards full membership. I read read and I read somemore. Everyday I am reading something new.

http://www.inspect-ny.com/

http://www.housedetective.com -- Read all his columns

http://home.howstuffworks.com/house.htm

http://www.heymark.info

These above are a great starting point. Study them. One thing is clear Jason if your lacking education your going to miss something. Ensure once you do start inspecting you have a experienced home inspector look over your report to help you better understand. You won't be a pro over night. This business is a learn as you go system. However the more you read now the better you'll be. I studied under a CMI for awhile before I ever did my first paid inspection. I highly advise you do that. Also make sure you use something that looks professional for a report. Don't do something up in word and turn it in unless you know what your doing like RR and others. If you ever need help let anyone of us know. Jason you have joined the best organization on this planet.

-- Another thing volunteer for Habitat for Humanity. Get out there and build houses if you never have. That will teach you a ton. Ask a electrician and a HVAC tech to let you join them on a inspection if one will.

-- Get ICC certified. It's a huge help. IRC -- International Residential Code



Bill
PS. Im tired. I have alot more resources. If you ever need anything just ask.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes

Last edited by bboerner; 7/17/08 at 11:35 PM..
Reply With Quote
  #5  
Old 7/18/08, 8:27 PM
jtormo jtormo is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Fort Lauderdale, FL
Posts: 14
Default Re: AFCI in Bedrooms and four point?

Thank You! I realise how stupid my question was.

I was motivated to post the question because of an article I read.

http://www.mikeholt.com/mojonewsarch...s~20050728.php

This article refers to an AFCI tester on the market. Seems like there is controversy on the subject of AFCI use.

So yeah I mentioned looking at wires etc because I thought that would determine another option.

Anyhow I appreciate all the advice and I realise that one can not be affraid to ask questions no matter how stupid they may appear.

I am learning something new everyday and I am glad I am sourrounded by so many professionals.

Thanks for all the tips.

Jason
Reply With Quote
  #6  
Old 7/18/08, 8:49 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: AFCI in Bedrooms and four point?

Quote:
Originally Posted by jtormo
Thank You! I realise how stupid my question was.

This article refers to an AFCI tester on the market. Seems like there is controversy on the subject of AFCI use.
Hi Jason, the only stupid questions are the ones that are not asked, sorry if my prior response was a little "pithy"

Yes there is a problem with testers, my own hi-end SureTest needs a firmware upgrade as they do not properly test the breakers. I have done it manually using the test and reset buttons for quite some time as I have never trusted that the SureTest was working properly.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 7/18/08, 8:51 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: AFCI in Bedrooms and four point?

Quote:
Originally Posted by jtormo
Thank You! I realise how stupid my question was.

I was motivated to post the question because of an article I read.

http://www.mikeholt.com/mojonewsarch...s~20050728.php

This article refers to an AFCI tester on the market. Seems like there is controversy on the subject of AFCI use.

So yeah I mentioned looking at wires etc because I thought that would determine another option.

Anyhow I appreciate all the advice and I realise that one can not be affraid to ask questions no matter how stupid they may appear.

I am learning something new everyday and I am glad I am sourrounded by so many professionals.

Thanks for all the tips.

Jason
Jason remember this no question is ever stupid in this business. We just want you to become educated so you can turn the favor around and help someone new down the road. ALWAYS ask question no matter how little. With that said though I'm not sure how much experience you have in home construction. If none get to reading and do not do a home inspection until you know what your doing. I have not near the experience as alot of these guys here. However if I don't know something I research and I dig. Remember two things. Google and Wikipedia know pretty much everything if you don't know. I can't stress this enough. START CREATING A LIBRARY. I story everything I see or come across from these guys as long. Keep in mind one day you and I will be just as good or better than some old timers here. Why? For starters I'm about 10 yrs younger than most and I have a HUGE desire to suck up as much as I can. Think were I'll be in 10 yrs from now as a home inspector. I've been doing this for a bit now but I can't claim years and years like alot here can. So keep posting and keep asking. That's how your going to learn. By the way Gerry is like the NACHI electrical guru and he's very helpful.

Bill



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #8  
Old 7/18/08, 10:15 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: AFCI in Bedrooms and four point?

I'm with Gerry on this even though I've tried most and own a few testers

The opinion of the industry and breaker manufacture convinced me

BTW Jason, Mike's article is from the days when AFCI was being hotly debated, not so much the case today, 2008 NEC AFCI info



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #9  
Old 7/18/08, 11:32 PM
jtormo jtormo is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Fort Lauderdale, FL
Posts: 14
Thumbs up Re: AFCI in Bedrooms and four point?

No offense taken!

I am hear to learn and getting beat up is no problem.

I managed and developed several Modular Home projects in the Florida Keys.

Well that was a while ago and it just won't work in this market anymore.

So yes, I have construction experience.

Have you ever seen a house flying through the air?

Well that's what it looks like when you swing one section then another onto an elevated 12 foot high foundation.

Once again, Thanks to all of you. One day I will be glad to help others just as you are doing for me.

Peace.

Jason
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts