Default AFCI at bedrooms on new construction?

I understand that AFCI are required at bedroom recepticles for new construction, but are they required for overhead lights and ceiling fans in bedrooms? If I'm correct, the 2002 NEC only requires AFCI at bedroom recepticles on new construction.

Thanks,

Kip McCullough

KRM Home Inspections, LLC
Atlanta, GA
Reply With Quote
  #2  
Old 2/9/06, 5:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI at bedrooms on new construction?

All 125 volt, 15 and 20 amp, single phase outlets.

An "outlet" is any point of power supply (basically) which includes smoke detectors, lights, receptacles, etc., etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 2/9/06, 5:30 PM
Jon Jones Jon Jones is offline
New User
 
Join Date: May 2005
Location: Maine
Posts: 2
Please Note: Jon Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI at bedrooms on new construction?

In most areas of ME, smoke detectors are exempt from the AFCI requirement.
Reply With Quote
  #4  
Old 2/9/06, 5:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI at bedrooms on new construction?

That would have to be a local AHJ thing Jon, because based on the NEC as a whole it requires them to be on the AFCI circuit. Many fight the idea that if the AFCI circuit goes off the smoke circuit will also.....Yet I would argue that the advantage of this is the notice you would get from the AFCI system via the smokes....since as we know the smokes are required to be of battery back up nature......anyway....not a all together bad thing when on an AFCI circuit......

Usually we feed a bedroom...smaller one of the closest nature...let it feed the smoke circuit and then loop it so they all are covered by AFCI....very important to note that AFCI can leave the bedroom and pick up other items....and you can have more than (1) AFCI within a bedroom....just wanted to throw that in for ya.



Paul W. Abernathy
Reply With Quote
  #5  
Old 2/9/06, 11:00 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: AFCI at bedrooms on new construction?

I caution folks from calling out missing AFCIs on new construction. You need to ask the AHJ if they require it, because not all do. AFCIs are not required on new construction in NY State... period.
Reply With Quote
  #6  
Old 2/9/06, 11:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI at bedrooms on new construction?

Quote:
Originally Posted by jfarsetta
I caution folks from calling out missing AFCIs on new construction. You need to ask the AHJ if they require it, because not all do. AFCIs are not required on new construction in NY State... period.
Is this because they haven't adopted a newer version of the IRC or NEC, or do they have their own State Code (like CA does)?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 2/9/06, 11:57 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI at bedrooms on new construction?

Joe,
Below is info I lifted off of the "New York State Division of Code Enforcement and Administration". Is your info something new?

Are arc-fault circuit-interrupters required in residential buildings regulated by the BCNYS?
YES. Chapter 27 of the BCNYS references the 1999 version of the NEC which in section 210-12, requires arc-fault
circuit-interrupter protection for all branch circuits that supply 125-volt, single-phase, 15- and 20- ampere receptacle
outlets installed in dwelling unit bedrooms (effective January 1, 2002).
Reply With Quote
  #8  
Old 2/10/06, 3:57 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: AFCI at bedrooms on new construction?

Here's a good graphic from About Homes:

Click here
Reply With Quote
  #9  
Old 2/10/06, 4:02 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: AFCI at bedrooms on new construction?

Russel,

Is that a link from your IRS?



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #10  
Old 2/10/06, 5:03 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: AFCI at bedrooms on new construction?

Yes.

We've only recently been noting absence (or presence) of AFCI breakers, so I had to come up with something to explain why my Clients should have AFCI breakers installed, and something to explain what they do if they were installed.

Ultimately all of my IRS reference materials will be at About Homes, but the PowerPoint presentation (think marketing) won't be there, just the information.

About Homes and the materials there are free to NACHI members through March 31, 2006, so check often (I create and/or upload information daily) and make sure you join us as a home inspector at our discounted NACHI rate prior to March 31, 2006.
Reply With Quote
  #11  
Old 2/10/06, 8:03 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI at bedrooms on new construction?

I agree....I think your question is very important Jeff.....because even back to 1999 the AFCI was mandated for 2002 as I believe Charles posted as well. The local AHJ certainly has the ability to modify the NEC but I am not in NY so I dont know but from all the places I deal with AFCI's are now required....yes I can see some saying the smoke is not on the circuit but from an electricians standpoint it is moot...their is no way in getting around the wording of the NEC on the issue of AFCI's in bedrooms....the smoke is 120V and should be on AFCI....period.



Paul W. Abernathy
Reply With Quote
  #12  
Old 2/10/06, 10:58 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: AFCI at bedrooms on new construction?

Quote:
Originally Posted by Kip McCullough
I understand that AFCI are required at bedroom recepticles for new construction, but are they required for overhead lights and ceiling fans in bedrooms? If I'm correct, the 2002 NEC only requires AFCI at bedroom recepticles on new construction.
The 1999 NEC only requires AFCI protection for bedroom receptacles, and the 2002 NEC requires AFCI protection for all bedroom outlets (receptacles, lights, etc.)

However, the 2000 IRC as a "stand-alone" code does not require any AFCI protection for bedrooms (see IRC E3802). That was added to the IRC in 2002 (E3802.11)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 2/10/06, 11:02 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: AFCI at bedrooms on new construction?

And just for clarification, note that most, if not all, of the jurisdictions here are still using the UBC from ca. 1996, which, I believe, didn't even know that AFCI's existed. Yet I as a home inspector here regularly recommend the upgrade.
Reply With Quote
  #14  
Old 2/10/06, 11:02 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI at bedrooms on new construction?

Just to be clear......I as an electrician wire to the NEC and it is refered from the UBC here in VA....and probably in most cases. In other words they are going to refer to the standards of the NEC if adopted in the state.....and the NEC is clear on the AFCI requirements I believe....

Now if the local AHJ chooses to waive certain portions of things it is within their Art 90 power to do so.

RR....Does the UBC not refer you to the NEC on electrical installations and requirements...and if so what NEC edition has been adopted in your state?



Paul W. Abernathy
Reply With Quote
  #15  
Old 2/10/06, 11:02 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: AFCI at bedrooms on new construction?

Quote:
Originally Posted by cbuell
Joe, Below is info I lifted off of the "New York State Division of Code Enforcement and Administration". Is your info something new?

Are arc-fault circuit-interrupters required in residential buildings regulated by the BCNYS?
YES. Chapter 27 of the BCNYS references the 1999 version of the NEC which in section 210-12, requires arc-fault circuit-interrupter protection for all branch circuits that supply 125-volt, single-phase, 15- and 20- ampere receptacle outlets installed in dwelling unit bedrooms (effective January 1, 2002).
The question really is does the Residential Code of New York State (RCNYS) require AFCI protection in 1/2 family homes and townhouses. I think the answer is "No" since the RCNYS/IRC is a "stand-alone" code that does not require you to go to the NEC unless specifically stated. Homes are not regulated by the BCNYS, they are regulated by the RCNYS.

The current RCNYS is based on the 2000 IRC, which does not require any AFCI protection (see E3802) ... unless you also apply the 1999 NEC, which some AHJ's may do (I think incorrectly, since E3802 does not kick you out to the NEC).



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 2/10/06 at 12:11 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM


All times are GMT -4. The time now is 5:25 AM.