Default AFCI Breaker/GFCI Rec

Can an AFCI breaker take the place of a GFCI Rec. in a wet location?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 4/20/09 at 12:47 AM..
Reply With Quote
  #2  
Old 12/2/07, 11:58 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI Breaker/GFCI Rec

Christopher
AFCI devices have a Class "B" type of GFP protection. This is generally set at 20-40 miliamps.
Where a GFCi device is a Class "A" type device, which is set at between 4 and 6 Miliamps. This is the type required for most GFCI applications.
Reply With Quote
  #3  
Old 12/3/07, 12:50 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: AFCI Breaker/GFCI Rec

Quote:
Quote:
Originally Posted by Pierre Belarge
Christopher
AFCI devices have a Class "B" type of GFP protection. This is generally set at 20-40 miliamps.
Where a GFCi device is a Class "A" type device, which is set at between 4 and 6 Miliamps. This is the type required for most GFCI applications.
Thanks, do you see a GFI breaker in this panel On the ledger it states two bathrooms (which have normal rec.) are covered by GFI breakers. All I see are the AFCI. Also All 20 amp breakers.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 12/3/07, 12:55 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: AFCI Breaker/GFCI Rec

The breaker with the red test button is the GFCI.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #5  
Old 12/3/07, 2:04 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: AFCI Breaker/GFCI Rec

Quote:
Quote:
Originally Posted by sstanczyk
The breaker with the red test button is the GFCI.
That is the only one I found too. It states that breakers 16 and 18, on the right are protecting the bathrooms with GFI protection. It was built in 2003, I thought maybe i was missing something.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 12/3/07, 2:14 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: AFCI Breaker/GFCI Rec

Found my answer..
http://www.eaton.com/EatonCom/Market...iteId=EatonCom.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
AFCI Controversy rcooke Electrical Inspections 11 9/10/07 2:14 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical Inspections 19 2/15/07 12:05 PM


All times are GMT -4. The time now is 5:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts