Default AFCI breaker are HOT!

I was in a 3 year old house with Eaton AFCI breakers. The house was vacant an no load was being appled to the AFCI circuits. When the panel was off there was about a 30 degree difference on the temp of the breakers. I have never noticed this before and have no idea of the possible cause. Any info?

afci-breaker-hot-ir20080729_0038.jpg

Thanks in advance.
Reply With Quote
  #2  
Old 7/30/08, 5:53 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: AFCI breaker are HOT!

Russell,

AFCI's will be hotter than your average breaker, most of the time. Please be careful when utilizing infrared imaging to detect anomalies in Electrical panels because most of those hot spots are not an issue whatsoever.

http://www.massinfrared.com/?D=75

The only time I would call out an electrical hot spot on an electrical panel is if the temperature was anywhere over 100 degrees.
Reply With Quote
  #3  
Old 7/30/08, 6:12 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,575
Default Re: AFCI breaker are HOT!

They were about 130 degrees. The 94 was on the COLD part of the panel. But thanks for the reply.
Reply With Quote
  #4  
Old 7/30/08, 7:19 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: AFCI breaker are HOT!

I have found 15 amp GFCI's to run about eight to ten degrees hotter, as well.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 7/30/08, 11:47 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: AFCI breaker are HOT!

Quote:
Originally Posted by dvalley
Russell,

AFCI's will be hotter than your average breaker, most of the time. Please be careful when utilizing infrared imaging to detect anomalies in Electrical panels because most of those hot spots are not an issue whatsoever.

http://www.massinfrared.com/?D=75

The only time I would call out an electrical hot spot on an electrical panel is if the temperature was anywhere over 100 degrees.
Hey David
I had a question on electrical inspections with IR. I wondered if IR could (for instance) detect a loose connection, even if the house is vacant, with no load applied to the circuit?

It has been my thought that a poor connection would not reveal itself until loaded. Or is that incorrect?
Reply With Quote
  #6  
Old 7/30/08, 2:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: AFCI breaker are HOT!

Quote:
Originally Posted by hmiller
Hey David
I had a question on electrical inspections with IR. I wondered if IR could (for instance) detect a loose connection, even if the house is vacant, with no load applied to the circuit?

It has been my thought that a poor connection would not reveal itself until loaded. Or is that incorrect?

Ir can only detect temperature differential. If you had a live loose connection and it was not arcing or building up heat, then IR would not detect the loose connection as there must be a heat build-up in order for the IR camera to detect the fault.

Even in a vacant house, with no load. No load means no heat which means that the IR camera is useless in this particular situation.
Reply With Quote
  #7  
Old 7/31/08, 9:49 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI breaker are HOT!

not uncommon to see them 15-30 degrees hotter and the manufacturer ( eaton anyway ) has tested their AFCI's to function properly at I believe nearly 40-50 degrees hotter than normal....



Paul W. Abernathy
Reply With Quote
  #8  
Old 7/31/08, 11:17 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: AFCI breaker are HOT!

Paul, with the new AFCI code infect what would be the added cost to include these breakers in an average size home?

Say a 200 amp service on a 1200 sqr. foot ranch. Basic home.

Your help is appreciated.

Thanks, Pete
Reply With Quote
  #9  
Old 8/1/08, 9:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI breaker are HOT!

Well peter....hard to say because it depends on the house and the circuits the electrician chooses to run beyond the minimum required. But for craps and giggles...lets figure probably 18 MAX @ roughly $ 42.00 each = 756-900 bucks I would venture....

Now thats electrician numbers......figure mark up for resale to consumer at about $ 1,200 - $ 1,400 additional cost.....Honestly it is a small price for enhanced safety.

Just what does the car manufacturers charge for those fancy air bags...from what I hear it adds about $ 2,000 a BAG in your car....

The industry will absorb it.....because it is an "ACROSS THE BOARD" type of change....

Now...in your house example....40 CK panel.....on that small of a house probably less...like 12 or so...AFCI's....so just figure on about a $ 1,200.00 buck increase.....or about the cost of a better grade counter surface, or thicker shag carpet ( did I say shag....ewwww )....sad to say everyone equates cost to electrical and they have no idea people will WASTE $ 5,000 bucks on a counter top.....then put in a poor electrical system......guess it is a priority thing....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Smoke Detectors on AFCI breaker...finally:-) mgault Electrical Inspections 24 1/25/08 2:10 PM
AFCI Controversy rcooke Electrical Inspections 11 9/10/07 2:14 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical Inspections 19 2/15/07 12:05 PM


All times are GMT -4. The time now is 2:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts