Default AFCI in Damp Locations

From what I've read, it seems that arc-faults are a structure protection device and ground-faults are a personal protection device. But why does the arc-fault requirement not include damp locations? I realize that those locations should be protected by GFCI's, but that's just personal protection, right?

If a bathroom is connected with GFCI receptacles and not a GFCI breaker, why wouldn't the cables running through the walls need protection by an AFCI breaker?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Find an InterNACHI certified Iowa Home Inspector (and anywhere else in North America)
  #2  
Old 11/24/09, 11:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI in Damp Locations

There's no prohibition to installing AFCI's on additional circuits, there's just nothing currently requiring them.

AFCI's are relatively new technology and were originally required at bedroom receptacle outlets. It has been expanded to include all bedroom outlets, and may (one day) be required at all branch circuits of the residence.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/24/09, 11:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI in Damp Locations

Currently their are few places remaining in a dwelling that is not going to require AFCI technology. The few places still not requiring AFCI is kitchens, bathrooms, garages and so on....but I am sure it is coming.

You are 100% correct in that AFCI protection should also be in those locations as well and the kitchen one was an oversite as they probably wanted just the SABC circuits only but instead it exempted the entire requirement within the kitchen.

Statistics are what started it in the bedroom back in the 1999 code, effective in 2002 and it has grown from their.....and look for it to continue to grow.



Paul W. Abernathy
Reply With Quote
  #4  
Old 11/25/09, 12:10 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: AFCI in Damp Locations

Some areas opt out of portions of the code as they are allowed to do if they file the right papers with the state. We have one county that does not allow bedroom smoke detectors on AFCI's.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 11/25/09, 12:15 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI in Damp Locations

And you know bruce....that county probably has a building official that simply does not understand how the AFCI works. At one point OHIO was against the AFCI to in the end remove the OPT OUT and accept it.

Only time will tell but in most cases ( and I do work for a local goverment...lol ) the going against the grain is usually marked up to ignorance but i see it everyday in our own governmental roadblocks.



Paul W. Abernathy
Reply With Quote
  #6  
Old 11/25/09, 7:45 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: AFCI in Damp Locations

Thanks guys. That's what I figured but wanted to make sure I wasn't missing something.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #7  
Old 11/25/09, 8:19 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: AFCI in Damp Locations

Paul, what are they going to do about the excessive heat generated by AFCI's if all branch circuits require protection? Required ventilation of the panels? New AFCI design?

As it is, having 6 or 7 AFCI's in a panel heats the wall in the adjacent room where it can be felt with your hand.

Has anyone determined the watt consumption of these devices?

I may just do that, if that info is not available.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 11/25/09, 9:37 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: AFCI in Damp Locations

Quote:
Originally Posted by jpope View Post
There's no prohibition to installing AFCI's on additional circuits, there's just nothing currently requiring them.

AFCI's are relatively new technology and were originally required at bedroom receptacle outlets. It has been expanded to include all bedroom outlets, and may (one day) be required at all branch circuits of the residence.
I think you meant to say "expanded to include all living areas"?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 11/26/09, 10:27 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI in Damp Locations

Quote:
Originally Posted by dandersen View Post
Paul, what are they going to do about the excessive heat generated by AFCI's if all branch circuits require protection? Required ventilation of the panels? New AFCI design?

As it is, having 6 or 7 AFCI's in a panel heats the wall in the adjacent room where it can be felt with your hand.

Has anyone determined the watt consumption of these devices?

I may just do that, if that info is not available.
David,

I actually read a report that was in the Eaton office when I was in PA doing a seminar. They have actually done the tests on the "crowding" of AFCI devices and have determined that the rise in temperature will not effect the operation of the product. They also determined that since the temperature levels of the optimum operation levels would never rise enough to cause any concerns. The research is on going but to date their is no evidence that the rise in heat will lead to an excessive level like you would have from an ARC condition....the heat is stable and within the UL testing levels and this test was done with a fully loaded enclosure and panelboard at full load capacity and it did fine.

Don't as me for a copy of it because I dont have it , however I can promise you it was and is always being looked at by the manufacturers and during UL Listings.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Light Switch Near Shower vsantos Electrical Inspections 204 3/19/12 9:58 AM
Nice One For You - Lesson 1 pabernathy Electrical Inspections 18 12/16/06 10:03 AM


All times are GMT -4. The time now is 5:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts