Default AFCI dedicted circuits

Todays inspection was 2005 permitted construction SFR. Discovered that the master bedroom AFCI circuit included the master bath GFCI as well as lighting devices for both the bedroom and bath. Rightfully or wrongly it had been my understanding that the AFCI were for outlets only and could not be used to service other devices. Your insight will be appreciated



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/20/11, 4:26 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Everything is OK with the exception of the bathroom receptacle being on the same circuit as the bedroom. The bathroom receptacle(s) is/are required to be on a 20 amp circuit dedicated to only the bathroom(s) or a 20 amp circuit which supplies only the receptacle and equipment within that bathroom.
Reply With Quote
  #3  
Old 2/20/11, 5:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI dedicted circuits

Robert has answered the initial question regarding the bathroom outlets.
Quote:
Originally Posted by mtyson View Post
Rightfully or wrongly it had been my understanding that the AFCI were for outlets only and could not be used to service other devices. Your insight will be appreciated
"Outlets" and "receptacles" are not the same thing.

Generally, AFCI protection serves lighting outlets AND receptacle outlets. In other words - the entire branch circuit, which (in most cases) will be multiple "outlets."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/20/11, 6:13 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

All outlets are required to have AFCI protection. Outlet is a broad term that usually gets thought of as only receptacles but by definition it is not limited to receptacles. That definition would included receptacles, lights and hard wired smoke detectors, etc.
Reply With Quote
  #5  
Old 2/20/11, 11:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI dedicted circuits

Quote:
Originally Posted by Robert Meier View Post
All outlets are required to have AFCI protection. Outlet is a broad term that usually gets thought of as only receptacles but by definition it is not limited to receptacles. That definition would included receptacles, lights and hard wired smoke detectors, etc.
Yes, smoke detectors, CO detectors and other outlets included.

That brings up a question. I'd like to get your opinion Robert.

The blank-face, GFCI protection in the master bedroom closet, provided for the spa-tub (we discussed this breifly in another thread) - Do we consider this an "outlet" located in a "dwelling unit bedroom," which would also require AFCI protection?
Attached Thumbnails
afci-dedicted-circuits-ibcgetattachment.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/21/11, 8:25 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Quote:
Originally Posted by jpope View Post
Yes, smoke detectors, CO detectors and other outlets included.

That brings up a question. I'd like to get your opinion Robert.

The blank-face, GFCI protection in the master bedroom closet, provided for the spa-tub (we discussed this briefly in another thread) - Do we consider this an "outlet" located in a "dwelling unit bedroom," which would also require AFCI protection?
Good question. Here's the Article 100 NEC definition of an outlet:

Quote:
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
.
And the definition of utilization equipment:

Quote:
Utilization Equipment. Equipment that utilizes electric energy for electronic, electromechanical, chemical, heating, lighting, or similar purposes.
IMO that GFCI device will use electric energy so it is by definition utilization equipment. It is also at a point in the wiring system where it will take current to perform it's function.

But if you had a simple single pole switch switch it wouldn't meet the definition of an outlet.
Reply With Quote
  #7  
Old 2/21/11, 8:59 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: AFCI dedicted circuits

I don't see how it is utilization equipment because the device does not do any work
Quote:
utilizes electric energy for electronic, electromechanical, chemical, heating, lighting, or similar purposes
How ever the load it is monitoring is utilization equipment so the AFCI requirement would apply anyway.

Just my thoughts guys.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 2/21/11, 9:19 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

I would not consider a blank face GFI to be an outlet. I would consider this the same as a switch as no electric is being drawn out like it would for a receptacle or lighting outlet.
Reply With Quote
  #9  
Old 2/21/11, 9:34 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Quote:
Originally Posted by Jim Port View Post
I would not consider a blank face GFI to be an outlet. I would consider this the same as a switch as no electric is being drawn out like it would for a receptacle or lighting outlet.
But doesn't this device require the use of electricity to actually work? Surely the circuitry within the device uses a small amount of current to perform it's function.
Reply With Quote
  #10  
Old 2/21/11, 10:28 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Quote:
Originally Posted by Robert Meier View Post
But doesn't this device require the use of electricity to actually work? Surely the circuitry within the device uses a small amount of current to perform it's function.
Using that interpretation a GFI breaker would be an outlet. I do not think this is what is meant. I do not see this as meeting the definition of "outlet". You are not taking current to supply utilization equipment. The micro-ampere that is being used would not meet the intent IMO.
Reply With Quote
  #11  
Old 2/21/11, 10:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI dedicted circuits

This came up on a recent inspection. The AHJ had already made the determination that the blank-face DID require AFCI protection and the electrician was arguing that it did NOT.

My initial thought was that the electrician is correct as this is not "technically" an outlet.

In the end, the AHJ required AFCI protection for that circuit, but I'm still not sure I agree with his interpretation.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 2/21/11, 10:47 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Quote:
Originally Posted by Jim Port View Post
Using that interpretation a GFI breaker would be an outlet. I do not think this is what is meant. I do not see this as meeting the definition of "outlet". You are not taking current to supply utilization equipment. The micro-ampere that is being used would not meet the intent IMO.
You might be right, but you cannot deny that the GFCI device uses current (outlet definition) and therefore also fits the definition of utilization equipment. IMO having met both of those criterion the GFCI device would require AFCI protection if within a bedroom, but as with a lot of this stuff we're simply splitting hairs.

Jeffery asked the question as to my opinion on the topic, I understand that others may not see it my way which is OK too. I'm just forming my opinion after extrapolating information from the Article 100 definitions.

Now from a practical standpoint, if I have a wall that separates the bathroom from the bedroom and the device faces into the bathroom it would not require AFCI protection. Turn the box around and put it in the same wall in the bedroom and we're back to this discussion as to whether or not AFCI protection is required. Kind makes the entire argument kind of silly.
Reply With Quote
  #13  
Old 2/21/11, 1:13 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI dedicted circuits

Very similar to when bedroom closet lighting did not require AFCI as it was not in the bedroom, but the closet. Even tho the closet was in the bedroom. This was changed in the next cycle to include the closet lighting.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
GFCI on AFCI circuits mglowczynski Electrical Inspections 3 11/29/10 5:48 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 5:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts