Default AFCI not a GFCI on jetted tub

ok????

or should it be a GFCI breaker?

No other protection installed, this breaker stopped the jets...
Attached Thumbnails
afci-not-gfci-jetted-tub-3-mar-09-085.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 3/3/09, 7:48 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: AFCI not a GFCI on jetted tub

Should have a GFCI somewhere, were you able to check under the tub or in the crawlspace for one? Sometimes they hide an outlet above the floor insulation in the crawl.

Also, don't think you can have both AF and GF on the same circuit.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 3/3/09, 7:50 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: AFCI not a GFCI on jetted tub

Quote:
Originally Posted by bking View Post
Should have a GFCI somewhere...
Agreed...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 3/3/09, 7:52 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: AFCI not a GFCI on jetted tub

Completely tiled in surround. No GFCI only type on any wall surface of the bathroom, fully elevated drywalled beneath the sub floors. And it functioned to disconnect the tub jets.

I'm thinking they should have used a GFCI (req'd) but used an AFCI breaker instead.
Attached Thumbnails
afci-not-gfci-jetted-tub-3-mar-09-094.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #5  
Old 3/3/09, 7:53 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: AFCI not a GFCI on jetted tub

Quote:
Originally Posted by lkage View Post
Agreed...
But doesn't, and I think they thought this was "protection too"



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 3/3/09, 8:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: AFCI not a GFCI on jetted tub

Quote:
Originally Posted by mgault View Post
Completely tiled in surround. No GFCI only type on any wall surface of the bathroom, fully elevated drywalled beneath the sub floors. And it functioned to disconnect the tub jets.

I'm thinking they should have used a GFCI (req'd) but used an AFCI breaker instead.
Those are plugged in and there should be an access panel.
Fault may lie with the decorator,not the Electrician.

Must admit I never saw a circuit with both though.
Reply With Quote
  #7  
Old 3/3/09, 10:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI not a GFCI on jetted tub

There's no reason you can't have both, but GFCI protection is required - regardless.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 3/3/09, 10:28 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: AFCI not a GFCI on jetted tub

Michael, did the bath have a separate toilet room? Electricians are known to place hydro-therapy tub GFCI's there if there is no easy under tub access, at least around here they do.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #9  
Old 3/3/09, 10:45 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: AFCI not a GFCI on jetted tub

Quote:
Originally Posted by mboyett View Post
Michael, did the bath have a separate toilet room? Electricians are known to place hydro-therapy tub GFCI's there if there is no easy under tub access, at least around here they do.
Same here, or sometimes in the master closet. And always behind a bathrobe or something else.
Reply With Quote
  #10  
Old 3/3/09, 11:14 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: AFCI not a GFCI on jetted tub

Sometimes you just can't confirm a GFCI. Then, I say this:

"We could not confirm that the hydro-spa is equipped with ground fault protection, which is an important safety feature that should be verified as being present or added. Ground fault circuit interrupter (GFCI) receptacles have been required for spa tubs since 1987."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 3/3/09, 11:33 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: AFCI not a GFCI on jetted tub

Just fill with water and throw in a toaster.
See if it trips.
Reply With Quote
  #12  
Old 3/7/09, 10:02 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI not a GFCI on jetted tub

Quote:
Originally Posted by relliott View Post
Just fill with water and throw in a toaster.
See if it trips.
OUCH....glad I did not say that...lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 5/1/09, 7:50 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: AFCI not a GFCI on jetted tub

Interesting thread. I just found a AFCI on a jacuzzi tup circuit today on my afternoon inspection. I could not locate a GFCI breaker anywhere.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared Thermographer®, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #14  
Old 5/1/09, 8:14 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: AFCI not a GFCI on jetted tub

I've seen them use AFCI's on exterior outlets. Old school electricians I guess..."if it's newer, it's better".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 5/1/09, 8:21 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: AFCI not a GFCI on jetted tub

I always find them in the master closet BUT in a couple instances with the large tile surround tubs, there is a single tile at the motor end that is held in place by strong magnets. The installer will supply a special suction handle to remove the tile with. You have to look real close at the space between the tiles. If there is no grout or you can see the seam, it is in back of the tile.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Afci & gfci rfitzwater Texas/TPREIA Inspectors 12 2/27/09 8:30 AM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
Stacking AFCI, GFCI breakers abolt Electrical Inspections 6 4/17/07 10:57 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 5:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts