Cool AFCI question

I recently inspected a new home, homeowner complained that every time she plugged in a clothes iron (1200 watt) into an upstairs bedroom the AFCI would trip, shutting off the power to bedroom and the downstairs Office/Den.
Usually I find only the bedrooms only are protected by AFCI's. Is multiple use allowed by the NEC or is this just bad wiring practice, the builder did use the worst and I'm sure the cheapest Electric/Plumbing/HVAC all purpose contractor they could find.The builder is Stewart/Kret.

All opinions appreciated. Thanks, John
Reply With Quote
  #2  
Old 8/19/06, 12:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AFCI question

Early generations of the AFCI breakers have problems with a shared neutral or multiwire circuit. This condition causes nuisance tripping, which sounds to be what you have described.

The generally accepted remedy has been to wire (or re-wire) one circuit to one breaker (not necessarily one room).

I'm not sure if this issue has been addressed by the AFCI manufacturers in newer productions.

Also, if the power to the appliance is "on" when the plug is inserted, the AFCI will do its job and trip when an arc is detected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/19/06, 12:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI question

AFCIs simply don't work on a multiwire. They incorporate GF protection at the 30ma level.
Reply With Quote
  #4  
Old 8/19/06, 5:26 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI question

Two-pole AFCI breakers DO work on multi-wire circuits.
Reply With Quote
  #5  
Old 8/20/06, 5:58 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI question

John,

To answer your question.....AFCI's can protect any 15A or 20A Branch Circuit the electrician chooses...As this question came up in the seminar I did this weekend as well......AFCI is not bound by the bedroom...while the bedroom has to be AFCI protected.....it does not disallow other areas of the dwelling to also be on that same AFCI circuit.

The NEC does not " Specifically" tell you how many receptacles have to be on a circuit....but gives you the calculation guidelines to do it correctly.

So....can you have a bedroom on a AFCI and also pick up the receptacle in the hall lets say.....or even another bedroom.....Sure....nothing wrong with that...

Also as Greg has stated.....when the 2008 NEC is adopted...look for AFCI's on all 120V 15A and 20A Branch Circuits......

Hope this helps....



Paul W. Abernathy
Reply With Quote
  #6  
Old 8/21/06, 5:03 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI question

It may be that the AFCI part of the breaker is not the cause of the trip, but rather that the circuit is being overloaded. She is adding 10 amps to the circuit by plugging in the iron.
Paul,
I hate that I wasn't able to get to your seminar, I heard that it was very informative. Maybe next time.
Reply With Quote
  #7  
Old 8/22/06, 2:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AFCI question

Steve,

Wish you could have attended, Hopefully I will be able to bring it back to SC at some point as it is always being "TWEEKED"

Very hard to keep it from going too far yet keeping it to the items the HI should be aware of. Some may find it too basic while others will find it very extensive....in the end........it seemed to be a balanced day...lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
AFCI Controversy rcooke Electrical Inspections 11 9/10/07 2:14 PM
Hypothetical AFCI question... mgault Electrical Inspections 11 7/12/07 6:08 PM
AFCI question kweiss Electrical Inspections 19 11/4/06 5:03 PM
AFCI question cbuell Electrical Inspections 23 8/9/06 11:31 AM


All times are GMT -4. The time now is 5:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts