Default AFCI requirements

The new Texas SoP changes the required reporting regarding AFCI's. The document specifies reporting:

(17) the lack of arc-fault circuit interrupting devices serving family rooms, dining rooms, living
rooms, parlors, libraries, dens, bedrooms, sunrooms, recreations rooms, closets, hallways, or similar

rooms or areas;

Yet we are not required to operate these AFCI if the property is occupied, nor are we required to verify proper labeling.

My main question with this is regarding this placement of AFCIs. I do many new houses around here and have NEVER seen AFCIs located on circuits other than bedrooms and smokes. If I read this requirement correctly it is basically calling for AFCI on ALL outlet and switch circuits? I have never seen that. Which suggests that state and local building codes, even for brand new construction right now, do not require this and are not enforcing this.

So what is the point in having to put this as deficient on EVERY report from an inspector? What purpose will this serve other than confusing and scaring clients?




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #2  
Old 11/4/08, 11:09 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI requirements

Quote:
Originally Posted by kweiss View Post
The new Texas SoP changes the required reporting regarding AFCI's. The document specifies reporting:

(17) the lack of arc-fault circuit interrupting devices serving family rooms, dining rooms, living
rooms, parlors, libraries, dens, bedrooms, sunrooms, recreations rooms, closets, hallways, or similar

rooms or areas;

Yet we are not required to operate these AFCI if the property is occupied, nor are we required to verify proper labeling.

My main question with this is regarding this placement of AFCIs. I do many new houses around here and have NEVER seen AFCIs located on circuits other than bedrooms and smokes. If I read this requirement correctly it is basically calling for AFCI on ALL outlet and switch circuits? I have never seen that. Which suggests that state and local building codes, even for brand new construction right now, do not require this and are not enforcing this.

So what is the point in having to put this as deficient on EVERY report from an inspector? What purpose will this serve other than confusing and scaring clients?
I'm surprised that a smoke dectector would be placed on a circuit that could be tripped by a unit detecting small problems or having nusiance trips (if any).
Reply With Quote
  #3  
Old 11/4/08, 11:11 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: AFCI requirements

The 2008 NEC requires AFCI's on all of those circuits. Since there are no grandfaterhing provisions then we are required to identify those non-AFCI circuits as "Deficient" now. You are correct in that our state has not adopted that code as yet and may not for quite some time. This, along with numerous other issues, has been pointed out and discussed all this year regarding the new SOP.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #4  
Old 11/4/08, 11:22 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: AFCI requirements

Guess that will be one of the things that the SoP" for profit "training" course will explainn how to present? What a crock. Being required to muddle the report with something like that. I have always thought of myself as "helping" my clients to better understand the real issues with the house. Things like this do not help.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #5  
Old 11/4/08, 11:23 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: AFCI requirements

Quote:
Originally Posted by Brian A. MacNeish View Post
I'm surprised that a smoke dectector would be placed on a circuit that could be tripped by a unit detecting small problems or having nusiance trips (if any).
Since the smoke is considered an outlet of the room, they wanted it to be protected. However, 2008 NEC states that if the smoke detector is on it's own dedicated circuit and is piped in a metal raceway, there is no need for AFCI protection.

Jeff
Reply With Quote
  #6  
Old 11/4/08, 1:43 PM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 1,036
Default Re: AFCI requirements

Quote:
Originally Posted by kweiss View Post
Guess that will be one of the things that the SoP" for profit "training" course will explainn how to present? What a crock. Being required to muddle the report with something like that. I have always thought of myself as "helping" my clients to better understand the real issues with the house. Things like this do not help.
Kevin And All Other Texas Inspectors,

As Mike has said above, this is one of the many items discussed during the new SOP creation process. The SOP has many vague and poorly worded requirements and requires extensive clarifications. It is now up to all Texas Inspectors, at least those that are concerned about the welfare of the clients, to send in their "Request For Clarification" to the TREC legal counsel for any item that is unclear, vague or poorly written. Only your efforts can make a difference now!!



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593

Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Reply With Quote
  #7  
Old 11/4/08, 3:26 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AFCI requirements

Quote:
Originally Posted by jwicklander View Post
Since the smoke is considered an outlet of the room, they wanted it to be protected. However, 2008 NEC states that if the smoke detector is on it's own dedicated circuit and is piped in a metal raceway, there is no need for AFCI protection.

Jeff

Jeff,

Could you please supply that Code article? I do not remember that from the Code update I took.
Reply With Quote
  #8  
Old 11/4/08, 5:44 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: AFCI requirements

Jim,

Sure.. 210.12(B) exception #2. I don't have it readily available to cut and paste. If I do find it later online, I'll do it.

Jeff
Reply With Quote
  #9  
Old 11/4/08, 5:48 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: AFCI requirements

Any of you have a problem with this statement?

Safety enhancement upgrade: TREC requires me to report the absence of Arc Fault Circuit Interrupter (AFCI): These are now required, depending on local adoption of these new standards at all 120-volt, single phase, 15-20-ampere branch circuits supplying outlets installed in a dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, hallways, recreation rooms, closets, similar rooms or areas shall be protected by a listed arc fault interrupter combination-type, installed to provide protection of the entire branch circuit.
General AFCI info http://www.cpsc.gov/cpscpub/pubs/afcifac8.pdf2008
AFCI info and locations http://www.afcisafety.org/codes.html#NEC2008
Further information in regard to this would have to come from TREC admin@trec.state.tx.us



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #10  
Old 11/4/08, 6:00 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: AFCI requirements

Quote:
Originally Posted by badair View Post
Any of you have a problem with this statement?
Why would you indicate 'TREC requires' you to do that for AFCI's if you don't have that same narrative for GFCI's?

My AFCI narrative will likely read (but open to suggestions):
Quote:
One or more circuits are not protected by an Arc Fault Circuit Interrupter (AFCI). AFCIs are newly-developed electrical devices designed to protect against fires caused by arcing faults in the homes wiring. Arcing faults can be created by damaged, deteriorated, or worn electrical plugs, cords, and/or branch circuit conductors. AFCIs are required in new construction per current building standards which have been adopted in some jurisdictions across the country. Older homes with aging and deteriorating wiring systems can especially benefit from the added protection of AFCIs. I recommend the client consider having a qualified electrician evaluate and upgrade branch circuits to AFCI protection per current building standards.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog

Last edited by mboyett; 11/4/08 at 6:03 PM..
Reply With Quote
  #11  
Old 11/4/08, 6:05 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: AFCI requirements

I like it Barry, mind if I use it as a guide to make my own? I guess that will be the plan for some of the more murky requirements? Note it, pass it off to the TREC or a professional and move on - on EVERY inspection??? We can certainly do this and not

As to my original question, here is my confusion. I get that there are going to be murky, for lack of a better word, parts of any SoP for something like home inspection. In my gut, I tend to believe that a good minimum standard is better than no standard. And that nothing is perfect. Also understand that there are probably political and personal agendas at work behind the scene.

But what possible benefit is gained or purpose supported by requiring something like this? Effectively EVERY home we inspect will be found deficient in the panel because of this. How is it beneficial to the client? How is it beneficial to anyone? It isn't required by local or state codes. No one is going to "repair" it. If anything it just dilutes the report and makes inspectors look ridiculous. The more irrelevent things that are in the report, the less valid it is in my opinion. Last I knew they had not figured out how to handle the excessive heat problems of the AFCI breakers as crrently installed, what will they do with a panel full of them? Is this actual in practical use ANYWHERE in residential construction? What if someone actually has all the breakers replaced and something goes wrong fromt he heat - I have had clients that might do this, if it was in the report they want it done. Would we be liable? Are they trying to influence building codes by making us put this out there?

I know these things were brought up in the questioning period. Did they actually give any answers?




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #12  
Old 2/6/09, 2:33 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: AFCI requirements

Barry and Mike,

I liked both of your statements and have morphed them into this:

One or more circuits are not protected by an Arc Fault Circuit Interrupter (AFCI). TREC requires Inspectors to report the absence of Arc Fault Circuit Interrupter (AFCI): These are now required, depending on local adoption of these new standards, at all 120-volt, single phase, 15-20-ampere branch circuits supplying outlets installed in a dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, hallways, recreation rooms, closets, and similar rooms or areas.

AFCIs are newly-developed electrical devices designed to protect against fires caused by arcing faults in the homes wiring. Arcing faults can be created by damaged, deteriorated, or worn electrical plugs, cords, and/or branch circuit conductors. AFCIs are required in new construction per current building standards which have been adopted in some jurisdictions across the country. Older homes with aging and deteriorating wiring systems can especially benefit from the added protection of AFCIs. I recommend the client consider having a qualified licensed electrician evaluate and upgrade branch circuits to AFCI protection per current building standards.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #13  
Old 2/6/09, 4:49 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: AFCI requirements

Well, there ya go...I like it Mr. Wordsmith



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
Liability question jcahill Legislation, Licensing & Legal Issues for Inspectors 30 8/24/08 4:10 PM
AFCI future Requirements phughes Electrical Inspections 4 5/30/08 1:16 PM
AFCI Requirements jbowman4 Electrical Inspections 7 5/20/07 11:27 AM


All times are GMT -4. The time now is 5:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts