  #1  
Old 7/22/09, 4:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default AL Wiring

Just in case you need a reminder. . .
Attached Thumbnails
al-wiring-20090722_14_01.jpg   al-wiring-20090722_26_01.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 7/22/09, 4:21 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: AL Wiring

Quote:
Originally Posted by jpope View Post
Just in case you need a reminder. . .
Good one. Is this the same home with the bomb.. I mean water heater?



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #3  
Old 7/22/09, 4:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: AL Wiring

Quote:
Originally Posted by rnewland View Post
Good one. Is this the same home with the bomb.. I mean water heater?
Same place



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 7/23/09, 12:03 AM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AL Wiring

Did you have opportunity to find out if the receptacle was rated CO/ALR?
Reply With Quote
  #5  
Old 7/25/09, 10:45 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AL Wiring

This is a classic case of terminal concerns with AL Wiring. The wiring within the wall itself is probably fine when installed properly. However, the terminations in itself is where lies the hazard and potential for the most concern.

When I see a home with AL Wiring it increases my desire to thermal all receptacles and terminations within the enclosure. While I dont really grown too much regarding the AL Wiring if sized properly in single strand days of old. The terminations offer me the greater level of concern.



Paul W. Abernathy
Reply With Quote
  #6  
Old 7/25/09, 6:52 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: AL Wiring

Quote:
Originally Posted by pabernathy View Post
This is a classic case of terminal concerns with AL Wiring. The wiring within the wall itself is probably fine when installed properly. However, the terminations in itself is where lies the hazard and potential for the most concern.

When I see a home with AL Wiring it increases my desire to thermal all receptacles and terminations within the enclosure. While I dont really grown too much regarding the AL Wiring if sized properly in single strand days of old. The terminations offer me the greater level of concern.
So what do you recommend when AL wiring is present?

Attached pic is from a kitchen counter top receptacle recently replaced by what owner said a licensed electrician.
Attached Thumbnails
al-wiring-img_0137.jpg  



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #7  
Old 7/25/09, 6:56 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AL Wiring

Marcel,

I can't see the CO/ALR marking on the strap and I don't remember any Decora style that were reated for use with AL.
Reply With Quote
  #8  
Old 7/25/09, 7:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: AL Wiring

I thought that was a burn mark on Marcel's picture but with enlargement it looks like a finger shadow.

The sad part is that it probably will be a burn soon with Jim's info.

I recommend a qualified electrician examine the complete system, and make needed corrections for safety, with AL wiring.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 7/25/09, 9:22 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: AL Wiring

Quote:
Originally Posted by lkage View Post
I recommend a qualified electrician examine the complete system, and make needed corrections for safety, with AL wiring.
Larry,

That is also what I recommend when I see AL wiring.

But what is the electrician going to do? Pigtail every AL single strand receptacles and switches with a copper wire and proper marette / connector...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 7/25/09, 9:26 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: AL Wiring

Attached is a pic that I took while Realtor was saying that all outlets in the home were pigtailed with the approved connectors...
Attached Thumbnails
al-wiring-img_0080.jpg  



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #11  
Old 7/26/09, 11:34 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: AL Wiring

Quote:
Originally Posted by mgratton View Post
Larry,

That is also what I recommend when I see AL wiring.

But what is the electrician going to do? Pigtail every AL single strand receptacles and switches with a copper wire and proper marette / connector...
Yes, Marcel, I don't know all of what is available for the connections but pigtailing may be necessary.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #12  
Old 7/26/09, 11:51 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AL Wiring

Quote:
Originally Posted by mgratton View Post
So what do you recommend when AL wiring is present?

Attached pic is from a kitchen counter top receptacle recently replaced by what owner said a licensed electrician.
Do you notice that most classic pictures of issues when involving AL Wiring has pictures of devices and not the wiring itself. My recommendation for anyone with a home with AL Wiring is to not FEAR them into submission. I would recommend a licenesed electrical contractor come and check all terminations they can, if possibly check as many devices as possible and simply give a good expert evaluation of the electrical components that are associated with the termination of the AL Wiring.
If they are very concerned about their AL Wiring then suggest they think about installing AFCI's or GFCI's and so on to raise their level of protection but I would not say "you need to rewire the entire house, that AL Wiring is a ticking timebomb"....it is the connections that are main source of suspect in AL Wired homes.



Paul W. Abernathy
Reply With Quote
  #13  
Old 7/26/09, 11:54 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AL Wiring

Quote:
Originally Posted by mgratton View Post
Attached is a pic that I took while Realtor was saying that all outlets in the home were pigtailed with the approved connectors...

lol...did you all ever read my little soap box thingie on "why I believe Real Estate Agents are Corupt" back a few years ago. Boy I took some FLACK over that post. However, I still believe the same now as I did back then.

Many ( possibly not all ) will say anything they can to sell a home, make a commission and move on to the next home. Once they taste blood they wont go back...oh wait, wrong analogy I think.

http://www.nachi.org/forum/f13/why-f...upt-imo-12866/



Paul W. Abernathy
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #14  
Old 7/26/09, 11:56 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: AL Wiring

Quote:
Originally Posted by pabernathy View Post
I would recommend a licenesed electrical contractor...

If they are very concerned about their AL Wiring then suggest they think about installing AFCI's or GFCI's and so on to raise their level of protection...
Great suggestion...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM