Default Re: All 20 amp breakers

Quote:
Originally Posted by tclayton View Post
Hello David A. Andersen, I am not picking on you just asking if you have any IR pictures depicting the elevated IR signature of the wiring concealed with in the wall. I understand if there is a load applied to the circuit you may see a elevated temp due to the equipment drawing additional current because of the reduced voltage. The comments you posted just may not have given all of the info I needed to understand it. Thanks I am just trying to learn.
Be careful when you say that a reduced voltage will increase current. That is not true when dealing with resistive loads. If you reduce the voltage to a heater by half you will reduce the current by half as well.
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 5/2/11, 7:28 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: All 20 amp breakers

Quote:
Originally Posted by Robert Meier View Post
Be careful when you say that a reduced voltage will increase current. That is not true when dealing with resistive loads. If you reduce the voltage to a heater by half you will reduce the current by half as well.
I am many years out of school but I think if you half the voltage you quarter the load ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #18  
Old 5/2/11, 7:53 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All 20 amp breakers

Quote:
Originally Posted by rcooke View Post
I am many years out of school but I think if you half the voltage you quarter the load ... Roy

That depends on how you define your use of the word load. It terms of current, the voltage and current are directly proportional so they would increase or decrease at the same proportion, decrease the voltage by half and the current decreases by half too. But it terms of output in watts you are correct, decrease the voltage by half and the wattage drops to 1/4.
Reply With Quote
  #19  
Old 5/2/11, 8:01 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All 20 amp breakers

Quote:
Originally Posted by rcooke View Post
I think you need to talk to your apprentice and get him to explain it to you .
Are you saying that my post was incorrect? Then maybe it's true that you've been out of school for too long. For the record I said:

-Resistive load
-Reduce voltage by 1/2
-Current is reduced by 1/2
-Wattage (output) is reduced to 1/4
Reply With Quote
  #20  
Old 5/2/11, 9:14 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: All 20 amp breakers

Quote:
Originally Posted by Robert Meier View Post
Are you saying that my post was incorrect? Then maybe it's true that you've been out of school for too long. For the record I said:

-Resistive load
-Reduce voltage by 1/2
-Current is reduced by 1/2
-Wattage (output) is reduced to 1/4
Sorry Robert My mind is tired , Thanks for bearing with me ... Roy

Trying to Follow our Federal election and this Forum is not a smart thing to do .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #21  
Old 5/2/11, 9:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All 20 amp breakers

Quote:
Originally Posted by rcooke View Post
Sorry Robert My mind is tired , Thanks for bearing with me ... Roy

No problem. Your one-liner was pretty funny.
Reply With Quote
  #22  
Old 5/3/11, 4:04 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: All 20 amp breakers

Robert I apologize for my statement, I was actually thinking incorrectly while typing, thinking along the lines of the difference 120v vs 240v sorry. But I was just curious mostly about his pictures, thanks fro your response.
Reply With Quote
  #23  
Old 5/3/11, 4:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All 20 amp breakers

Quote:
Originally Posted by tclayton View Post
Robert I apologize for my statement, I was actually thinking incorrectly while typing, thinking along the lines of the difference 120v vs 240v sorry. But I was just curious mostly about his pictures, thanks fro your response.
No need to apologize. We're all here to share ideas and maybe even learn a thing or two.
Reply With Quote
  #24  
Old 5/3/11, 5:16 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: All 20 amp breakers

Quote:
Originally Posted by tclayton View Post
Hello David A. Andersen, I am not picking on you just asking if you have any IR pictures depicting the elevated IR signature of the wiring concealed with in the wall. I understand if there is a load applied to the circuit you may see a elevated temp due to the equipment drawing additional current because of the reduced voltage. The comments you posted just may not have given all of the info I needed to understand it. Thanks I am just trying to learn.

I'm not sure I understand what it is you're looking for or asking.
I have most of my IR scans on another computer/server. I don't really take pictures of hot wires inside the wall, though I do have some somewhere. I usually try for a more direct temperature measurement by removing an electrical component on the circuit as the direct temperature of the conductors are more important than sheet rock wall temperature.
 



The circuit that this outlet was on had a voltage drop. This was the hottest outlet on the circuit and was the source of resistance on the circuit.

The voltage drop occurs downstream of this outlet, not upstream.
We see this temperature rise with the thermal camera due to conduction of heat energy down the electrical wire. It is not necessarily because there is an increase in current through the conductor.

If you have a very high resistance load on the circuit which is at close to full capacity, you may see upstream conductors warmer than downstream because the current passing through the upstream conductor is equal to the load on the circuit plus the high resistance loss occurring on the circuit.

It is unlikely you will see this with most thermal cameras.
You can see that the upper wires on this plug are warmer than the lower wires, but this is more likely due to convection within the electrical box.
 



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #25  
Old 5/3/11, 5:32 PM
Allen L. Catterton's Avatar
Allen L. Catterton Allen L. Catterton is offline
InterNACHI Member
 
Join Date: May 2004
Location: Cantonment, FL
Posts: 198
Default Re: All 20 amp breakers

So good to see Marc Shunk posting here again. I have always enjoyed his informative and specific statements regarding electrical issues.



Allen L. Catterton, CMI
Catterton Home Inspections
http://www.cattertonhomeinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Siemens recalls circuit breakers due to fire hazard. gromicko Electrical Inspections 3 9/24/10 7:36 AM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM


All times are GMT -4. The time now is 5:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts