Default All Breakers on left side of bus

I inspected a panel that had all the breakers on the left side of the bus bar, except for the a/c breaker. I have always seen the panel balanced with breakers on both side of the bus bar. Is this a problem? There are 19 breakers on the one side.

Thank you
Michael



Michael Cotten
Cornerstone Home Inspections Inc
www.cornerstonehomeinspect.net
cornerstone235@aol.com
Reply With Quote
  #2  
Old 1/29/07, 4:48 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: All Breakers on left side of bus

Michael,

Not really....ODD but not really a problem as the bar to these breakers is staggard ( or it SHOULD be ) anyway.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #3  
Old 1/29/07, 4:58 PM
mcotten mcotten is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Hoffman Estates, IL
Posts: 19
Default Re: All Breakers on left side of bus

Thank you I didn't think it was a problem. Home owners father in law was concerned. Thank you.



Michael Cotten
Cornerstone Home Inspections Inc
www.cornerstonehomeinspect.net
cornerstone235@aol.com
Reply With Quote
  #4  
Old 1/30/07, 8:52 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: All Breakers on left side of bus

It only would have been a prblem if they were on the same side and skipped every other breaker.
Reply With Quote
  #5  
Old 1/30/07, 8:56 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: All Breakers on left side of bus

Steven,

Why would this be a problem?

The service should be able to handle this installation, grant it odd but the Ungrounded Conductor will have no problem handling it and the "Grounded" conductor should be sized fine to handle it. Only because if skipped you are looking at like...10 breakers only...lol if on one side.

We are not talking about massive unbalanced issues like in 3 phase systems in this case.

In his case....would not be possible with todays 42 OCPD limitations . Now in 2008 the 42 OCPD limitations will be removed from what I understand and then could be possible issues. But it is the responsibility of the EC to calculate the loads before applying the service...now how many actually do that is always a issue.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 1/30/07, 9:01 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All Breakers on left side of bus

I would like to see this....
Attached Thumbnails
all-breakers-left-side-bus-worthlesswithoutpics.gif  
Reply With Quote
  #7  
Old 1/30/07, 9:12 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: All Breakers on left side of bus

lol.....Steven I did see a guy one time make a attempt to put EVERYTHING on one leg of the service. I mean he skipped every other one and did the same on each side and only had 20 breakers in the panel but they were all on one leg.

Because in order to do this they were single breakers and limited to 15 and 20 circuits it was not as much a problem...but COULD be I guess if someone did it for a reason and then made an effort to overload the circuits but again you REALLY have to work at it.

I asked him WHY he did that and he said to me in a straight face, " I thought that if you only had 120V loads they all had to be on the same phase"......My reply was..........NOPE...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 1/30/07, 9:17 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,934
Default Re: All Breakers on left side of bus

Quote:
Originally Posted by pabernathy
lol.....Steven I did see a guy one time make a attempt to put EVERYTHING on one leg of the service. I mean he skipped every other one and did the same on each side and only had 20 breakers in the panel but they were all on one leg.

Because in order to do this they were single breakers and limited to 15 and 20 circuits it was not as much a problem...but COULD be I guess if someone did it for a reason and then made an effort to overload the circuits but again you REALLY have to work at it.

I asked him WHY he did that and he said to me in a straight face, " I thought that if you only had 120V loads they all had to be on the same phase"......My reply was..........NOPE...
Saw a 3 phase 208 the person had skipped every third breaker .
Worked but wrote it up as needing immediate replacement .
What some people will try and do to save a dollar.
Roy Cooke
</IMG>



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #9  
Old 1/30/07, 9:53 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: All Breakers on left side of bus

Yeah...like I said before... on 3 phase you can have some serious issues when someone does that and it can play HAVOC on the transformer trying to deal with it.

Now compound that if the transformer is a "on-site" model and sized by the EC, now unbalance it and WHAMO......rapid transformer replacements will be needed.

Not so much the case in single phase because we are limited..RIGHT now anyway....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 1/30/07, 10:15 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: All Breakers on left side of bus

Quote:
Originally Posted by rcooke
Saw a 3 phase 208 the person had skipped every third breaker .
I've seen the 'skip' the high leg often in some commercial installations. Did you flag this because it was only a single phase install?

tom
Reply With Quote
  #11  
Old 1/30/07, 12:55 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All Breakers on left side of bus

You better see them "skip" the high leg every time if this is center tapped delta. Usually they install a single phase panel for the 120v
Reply With Quote
  #12  
Old 1/30/07, 12:56 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: All Breakers on left side of bus

lol....I can picture it now greg.....they use a 3 phase panel and SKIP breakers and put all the 120V ( intended anyway ) on the 208 High Leg and WHAMO....

Who gets that BILL....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 1/30/07, 2:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: All Breakers on left side of bus

We have a lot of "2 transformer" red leg in Naples. You have to be careful.
Reply With Quote
  #14  
Old 1/30/07, 2:25 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,934
Default Re: All Breakers on left side of bus

No up here we have in industry a lot of three phase 4 wire system star hook up 120 volt to neutral 208 between any two legs.
We also in industry use a lot of 347/600 volt systems .
The only place 440 volt is used is in the auto plants.

Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #15  
Old 2/1/07, 10:48 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: All Breakers on left side of bus

That would be an unbalanced panel. Good practice is to have each phase balanced.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Chapter Listings on the Left Hand side of this bb? jbowman Miscellaneous Discussion for Inspectors 14 1/30/06 5:15 PM
Comments on ground wires (left side) jweinberg Electrical Inspections 22 1/9/06 6:27 AM