When using aluminum wire a 30A breaker requires wire size #8, a 20A #10 (NACHI Online Ed.). Am I correct in believing a 25A would also require #8?
Anybody have any documentation regarding what a 25A requires? An electrician quotes the NEC (200 In the photo you will see breakers manufactured by Bryant. On my report I recommended an electrician evaluate further the Bryant breakers and he said they are OK. |
| Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America) |
AFIK: #10AWG aluminum is OK for 25amps
Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
Double Post.....go back and read what I typed on the other message.
It is important to understand what you are asking. If you want to know the "ampacity" of a given conductor you would look at the 90 degree column. However, since we are limited to the ratings of the terminals if known or the allowances of 110.14[C][1]. So this can be a loaded question depending on the answer being seeked. based on the 2008 NEC the Ampacity of a 8 AWG AL is 45 Amps. But of course terminals are usually limited to 60 or 75 degree's so you have adjust it based on that information. So in reality lets say your terminals are 75 degree and the terminals of the piece of equipment is 75 degrees....the adjusted ampacity is then 40A based on 75 degrees. In your question you pose a 25A ampacity need...based on lets say a piece of equipment. With that said we have to assume 75 degree terminals so the size conductor being needed would be 10 AWG AL....since under the 75 degree column it is good for 30 Amps....Right........Right...... Then of course you need to check 240.4[D] which in the 2008 NEC reminds us that the overcurrent protection for the 10 AWG AL can't exceed 25A OCPD unless of course you bring in the allowances of 240.4[E] or [G] like for a motor in which you could use the ampacity of 310.16. Hope this was a little helpful....Gotta Run ! Paul W. Abernathy Last edited by pabernathy; 8/31/09 at 11:02 PM.. |