Can you please take a look at these pics and let me know what you think. Looks like an electrician installed it. Although, it looks like #6 AWG Alum on a 60 AMP breaker to a sub panel. Your thoughts are appreciated.
Attached Thumbnails
alum-60-amp-6-american-wire-guage-pict0170-medium-.jpg.JPG
Views:	294
Size:	100.6 KB
ID:	33171   alum-60-amp-6-american-wire-guage-pict0172-medium-.jpg.JPG
Views:	307
Size:	97.4 KB
ID:	33172  
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 11/9/09, 11:26 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Alum 60 AMP on #6 AWG

Too small. It needs to be 3 AWG AL or 6 AWG CU. Or they can reduce the breaker to 40A.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/9/09, 5:27 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by mnicholet View Post
Can you please take a look at these pics and let me know what you think. Looks like an electrician installed it. Although, it looks like #6 AWG Alum on a 60 AMP breaker to a sub panel. Your thoughts are appreciated.

I like your wire size gauge.
Reply With Quote
  #4  
Old 11/12/09, 12:08 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Electrician called me today and told me this is CODE.

Last edited by mnicholet; 11/12/09 at 12:59 PM..
Reply With Quote
  #5  
Old 11/12/09, 1:37 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

It appears that it is 220V either feeding an electric oven, and AC unit, a subpanel or an electric dryer.

Around here electricians are notorious for downsizing 1 step on the guage for AC units. Wrong is wrong call it out and let the electrician put it in writing that it is correct. Shift liability to him/her.

Also tell him/her to put anti-oxidant paste on it too

Chuck
Reply With Quote
  #6  
Old 11/12/09, 2:03 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

This AWG/breaker chart is a screenshot from InterNACHI mandatory online electrical course. It states 4 AWG required for 60 AMP Alum.

Obviously not CANADIAN friendly!

This course should be updated as I used it for a reference along with this forum and it is WRONG!

My Carson Dunlop text states 6AWG on ALUM is OK. Obviously, should have stayed with Carson Dunlop.

Not a happy InterNACHI member!!! Maybe someone from InterNACHI can talk to this Electrician.
Attached Thumbnails
alum-60-amp-6-american-wire-guage-codechart.jpg  

Last edited by mnicholet; 11/12/09 at 2:59 PM..
Reply With Quote
  #7  
Old 11/12/09, 3:45 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: Alum 60 AMP on #6 AWG

Quote:
This AWG/breaker chart is a screenshot from InterNACHI mandatory online electrical course. It states 4 AWG required for 60 AMP Alum.

Obviously not CANADIAN friendly!

This course should be updated as I used it for a reference along with this forum and it is WRONG!

My Carson Dunlop text states 6AWG on ALUM is OK. Obviously, should have stayed with Carson Dunlop.

Not a happy InterNACHI member!!! Maybe someone from InterNACHI can talk to this Electrician.
Stop reading Carson Dunlop books. They are full of errors. InterNACHI's course is correct.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #8  
Old 11/12/09, 3:55 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

InterNACHI course is NOT correct in BC. I have talked to three electricians today and they have crossed reference Canadian Electrical code and #6 AWG Alum is OK for 60 AMP Breakers. Carson Dunlop states the same.

Nick, phone a Canadian Electrician in BC and ask the question "6 AWG alum allowed on 60 AMPS?"

and then have the courseware adjusted for Canadian members.
Reply With Quote
  #9  
Old 11/12/09, 3:57 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Alum 60 AMP on #6 AWG

Carson Dunlop needs to go back to school. Definitely not right, I did industrial electricity for a several years. If you go to an electrical supply store, they will give you a free pocket chart or wheel that you can keep in your truck. My memory is not as good as it use to be so I got to refer to it every once in a while.
Reply With Quote
  #10  
Old 11/12/09, 4:00 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by mnicholet View Post
InterNACHI course is NOT correct in BC. I have talked to three electricians today and they have crossed reference Canadian Electrical code and #6 AWG Alum is OK for 60 AMPS. Carson Dunlop states the same.

Nick, phone a Canadian Electrician in BC and ask the question "6 AWG alum allowed on 60 AMPS?"

and then have the courseware adjusted for Canadian members.
I wonder why Canadian electricity is different than American electricity?
Reply With Quote
  #11  
Old 11/12/09, 4:02 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Nick, here is the number of the electrician that referenced BC Electric code: 1-250-751-1727

Here is their website:
http://www.mazzeielectric.com/
Reply With Quote
  #12  
Old 11/12/09, 4:05 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by jbraun View Post
I wonder why Canadian electricity is different than American electricity?
Don't know don't care. Code is code. Fact of the matter is a call was made during a home inspection due to InterNACHI reference material that was challenged by reference to BC electric code by a qualified electrician.
Reply With Quote
  #13  
Old 11/12/09, 4:05 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by jbraun View Post
I wonder why Canadian electricity is different than American electricity?
Canada has longer waiting lines.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #14  
Old 11/12/09, 4:13 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: Alum 60 AMP on #6 AWG

Mark, your electrician must have studied a Carson Dunlop manual as both are wrong.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #15  
Old 11/12/09, 4:15 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by gromicko View Post
Mark, your electrician must have studied a Carson Dunlop manual as both are wrong.
Where is it wrong? in Colorado or BC?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GE 200 amp 4/0 alum main rwashington Electrical Inspections 11 6/25/09 10:23 PM
gal alum rwashington Exterior Inspections 5 6/12/09 6:30 PM
Alum wiring mthiltgen Electrical Inspections 2 4/16/09 8:53 PM
3awg copper clad alum. enough for 200amp? ccurrins Electrical Inspections 9 6/19/07 2:36 PM
Alum gutters Rafael Exterior Inspections 3 3/3/06 6:18 AM


All times are GMT -4. The time now is 2:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts