Can you please take a look at these pics and let me know what you think. Looks like an electrician installed it. Although, it looks like #6 AWG Alum on a 60 AMP breaker to a sub panel. Your thoughts are appreciated.
|
| Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Too small. It needs to be 3 AWG AL or 6 AWG CU. Or they can reduce the breaker to 40A.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Quote:
I like your wire size gauge. |
|
#4
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Electrician called me today and told me this is CODE.
Last edited by mnicholet; 11/12/09 at 12:59 PM.. |
|
#5
|
|||
|
|||
|
Please Note:
Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
It appears that it is 220V either feeding an electric oven, and AC unit, a subpanel or an electric dryer.
Around here electricians are notorious for downsizing 1 step on the guage for AC units. Wrong is wrong call it out and let the electrician put it in writing that it is correct. Shift liability to him/her. Also tell him/her to put anti-oxidant paste on it too Chuck |
|
#6
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
This AWG/breaker chart is a screenshot from InterNACHI mandatory online electrical course. It states 4 AWG required for 60 AMP Alum.
Obviously not CANADIAN friendly! This course should be updated as I used it for a reference along with this forum and it is WRONG! My Carson Dunlop text states 6AWG on ALUM is OK. Obviously, should have stayed with Carson Dunlop. Not a happy InterNACHI member!!! Maybe someone from InterNACHI can talk to this Electrician. Last edited by mnicholet; 11/12/09 at 2:59 PM.. |
|
#7
|
||||
|
||||
|
Quote:
Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 |
|
#8
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
InterNACHI course is NOT correct in BC. I have talked to three electricians today and they have crossed reference Canadian Electrical code and #6 AWG Alum is OK for 60 AMP Breakers. Carson Dunlop states the same.
Nick, phone a Canadian Electrician in BC and ask the question "6 AWG alum allowed on 60 AMPS?" and then have the courseware adjusted for Canadian members. |
|
#9
|
||||
|
||||
|
Carson Dunlop needs to go back to school. Definitely not right, I did industrial electricity for a several years. If you go to an electrical supply store, they will give you a free pocket chart or wheel that you can keep in your truck. My memory is not as good as it use to be so I got to refer to it every once in a while.
|
|
#10
|
||||
|
||||
|
Quote:
|
|
#11
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Nick, here is the number of the electrician that referenced BC Electric code: 1-250-751-1727
Here is their website: http://www.mazzeielectric.com/ |
|
#12
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Don't know don't care. Code is code. Fact of the matter is a call was made during a home inspection due to InterNACHI reference material that was challenged by reference to BC electric code by a qualified electrician.
|
|
#13
|
|||
|
|||
|
Quote:
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
| Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Mark, your electrician must have studied a Carson Dunlop manual as both are wrong.
Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 |
|
#15
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where is it wrong? in Colorado or BC?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| GE 200 amp 4/0 alum main | rwashington | Electrical Inspections | 11 | 6/25/09 10:23 PM |
| gal alum | rwashington | Exterior Inspections | 5 | 6/12/09 6:30 PM |
| Alum wiring | mthiltgen | Electrical Inspections | 2 | 4/16/09 8:53 PM |
| 3awg copper clad alum. enough for 200amp? | ccurrins | Electrical Inspections | 9 | 6/19/07 2:36 PM |
| Alum gutters | Rafael | Exterior Inspections | 3 | 3/3/06 6:18 AM |