Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by mnicholet View Post
Nick, phone a Canadian Electrician in BC and ask the question "6 AWG alum allowed on 60 AMPS?"
I suggest you look at your national code, rather than relying on the electricians. There's a reason we have inspectors checking the work of tradesmen.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #17  
Old 11/12/09, 4:50 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,613
Default Re: Alum 60 AMP on #6 AWG

Mark asks:
Quote:
Where is it wrong? in Colorado or BC?
My calculator produces the same result all over the world.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #18  
Old 11/12/09, 5:08 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Alum 60 AMP on #6 AWG

Mark....did you happen to see the type of AL wire, i.e. THHN, THWN, USE, etc?



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #19  
Old 11/12/09, 8:28 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Here is the 2009 Canadian Electrical code. As you can see for type R90, RW90, T90 Nylon the ampacity is 55** AMPS

** states 55 is equal to 60 AMPS

Therefore ALUM Conductors (not more than 3 in a raceway) can be 60 AMPS when the appropriate type is used.
Attached Thumbnails
alum-60-amp-6-american-wire-guage-11-12-2009-5-20-30-pm.jpg   alum-60-amp-6-american-wire-guage-11-12-2009-5-26-08-pm.jpg  
Reply With Quote
  #20  
Old 11/12/09, 8:59 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Alum 60 AMP on #6 AWG

Mark...that's exactly why I asked about that in the prior post. Even the US standards say as much (unless I'm reading it wrong):

alum-60-amp-6-american-wire-guage-capture.jpg
Reply With Quote
  #21  
Old 11/12/09, 9:24 PM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by mboyett View Post
Mark...that's exactly why I asked about that in the prior post. Even the US standards say as much (unless I'm reading it wrong):

Attachment 33245
Thanks, for your help. None the less there is some variables invloved regarding this particular issue. It appears, as per Canadian and US electricial code that the AMP rating for a 6 AWG Aluminum conductor can be between 40 and 75 AMPS depending on the type.

I believe, I made the right call as identifying conductor type was not readily accessible without shutting off breakers. Further investigation by a qualified electrician should be conducted and was. Unfortunately, the electrician was very unprofessional with his communication and service. I am going to recommend to my clients that they have this electrician provide them in writing that the conductor type is appropriate.

Now, if we get back to the InterNACHI courseware how do we state that 40 AMP breaker on a 6 AWG is appropriate? As in fact it is correct if it is type TW but incorrect if it is type R90. Maybe this should be noted in the courseware to help prevent this issue from arising again. As table 4 of the Canadian electrical code states variables in the columns.

Furthermore, the Carson Dunlop text I refered to earlier (6AWG for 60AMPS) was for service drop and service entrance (free air), my mistake. Carson Dunlop states on pg 45 of module 3 in the Electricial courseware that ALUM wire size should be 6 AWG for 40 AMPS (same as InterNACHI).

I sincerely appreciate and respect everyones help on this thread. Thanks Nick and all fellow InterNACHI inspectors. The electrician I talked to today was very ignorant and I plan on filing an official complaint with his company.

Last edited by mnicholet; 11/12/09 at 9:37 PM..
Reply With Quote
  #22  
Old 11/29/09, 7:01 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Alum 60 AMP on #6 AWG

An AC unit can be on an undersized wire as long as the the wire is big enough to support minimuim ampacity on the AC unit's data plate. As far as I know that only applies to AC units. I read that in "Electrcal Inspections Of Excisting Dwellings", great book



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #23  
Old 11/29/09, 8:34 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by Chuck Lambert View Post
It appears that it is 220V either feeding an electric oven, and AC unit, a subpanel or an electric dryer.

Around here electricians are notorious for downsizing 1 step on the guage for AC units. Wrong is wrong call it out and let the electrician put it in writing that it is correct. Shift liability to him/her.

Also tell him/her to put anti-oxidant paste on it too

Chuck
There is no requirement for the use of the anti-oxidant paste. Good practice but not required.

Secondly the rules for sizing the wiring goes by a different sizing criteria. The nameplate will have the needed info on it. The wire is sized based on the minimum circuit ampacity. The breaker is sized based on the maximum overcurrent size.

Please review Article 440 so you do not needlessly cost the customer money because you wrote up something that is proper.
Reply With Quote
  #24  
Old 11/30/09, 10:57 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Alum 60 AMP on #6 AWG

I agree with Jim. However, I do need to add that in some cases you get a disconnect that will indeed call for Anti-Oxident in the listings posted on the product. In that case the Anti-Oxident would be required as part of the listing requirement.

However as Jim Said in a previous post, Anti-Oxident is not a requirement by the NEC in itself but rather a guideline for use when specific conditions warrant the application and use of an Anti-Oxident per the condition or listing of equipment.

I am not aware of any panelboard that requires Anti-Oxident paste but as jim said and I agree it is good practice and I always did it in my installations.



Paul W. Abernathy
Reply With Quote
  #25  
Old 11/30/09, 10:58 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Alum 60 AMP on #6 AWG

P.S. In case anyone is wondering....I am on Vacation Today !!!! 11/30/2009



Paul W. Abernathy
Reply With Quote
  #26  
Old 11/30/09, 1:31 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by pabernathy View Post
P.S. In case anyone is wondering....I am on Vacation Today !!!! 11/30/2009
Enjoy your vacation!!
Reply With Quote
  #27  
Old 11/30/09, 1:43 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Alum 60 AMP on #6 AWG

Quote:
Originally Posted by mnicholet View Post
Thanks, for your help. None the less there is some variables invloved regarding this particular issue. It appears, as per Canadian and US electricial code that the AMP rating for a 6 AWG Aluminum conductor can be between 40 and 75 AMPS depending on the type.


Now, if we get back to the InterNACHI courseware how do we state that 40 AMP breaker on a 6 AWG is appropriate? As in fact it is correct if it is type TW but incorrect if it is type R90. Maybe this should be noted in the courseware to help prevent this issue from arising again. As table 4 of the Canadian electrical code states variables in the columns.
Mark, you need to correct a typo in the above quote......

A 40 amp breaker is always allowed with any of the 6 gauge wire temperature ratings.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GE 200 amp 4/0 alum main rwashington Electrical Inspections 11 6/25/09 10:23 PM
gal alum rwashington Exterior Inspections 5 6/12/09 6:30 PM
Alum wiring mthiltgen Electrical Inspections 2 4/16/09 8:53 PM
3awg copper clad alum. enough for 200amp? ccurrins Electrical Inspections 9 6/19/07 2:36 PM
Alum gutters Rafael Exterior Inspections 3 3/3/06 6:18 AM


All times are GMT -4. The time now is 2:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts