Got a call to investigate an electrical fire in a house last week. It was 7:00 a.m., the residents were awake and noticed flames coming out of the walls.

If you look closely, you'll see the outlet says: "CU Wire Only"

It was a rental house. The residents moved out and I had the electricity and water to the home turned off until the owner makes the house electrically safe (in my capacity as the local AHJ).

alumimum-wiring-house-fire-122810-043.jpg alumimum-wiring-house-fire-122810-044.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/28/10 at 11:20 AM..
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/28/10, 1:24 PM
Jamie R. Wilks's Avatar
Jamie R. Wilks Jamie R. Wilks is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Southeast, Virginia
Posts: 133
Default Re: Alumimum wiring: house fire

Joe
As a Home Inspector and a Professional Fire Fighter, I have seen numerous homes with aluminum wiring problems (including fires). I have also seen some homes with aluminum wiring that do not seem to have any problems.
I always call out aluminum wiring and list the problems associated with it.
I was wondering, as the local AHJ, what do you consider making the home electrically safe? I have seen multiple ways to deal with aluminum wiring, but I only know of two ways that are approved or safe/correct (per most industry experts).



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
  #3  
Old 12/28/10, 1:46 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Alumimum wiring: house fire

Go read up on these;

http://www.alcopstore.com/



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #4  
Old 12/28/10, 3:13 PM
Jamie R. Wilks's Avatar
Jamie R. Wilks Jamie R. Wilks is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Southeast, Virginia
Posts: 133
Default Re: Alumimum wiring: house fire

Doug
I don't think the connectors show on the website you listed (http://www.alcopstore.com/ ) are one of the prefered methods of repair. These connectors still require a screw/torque and two different types of wire with different properties.
Actually the question I had, was what a local AHJ (Joe in this case) considers a proper/safe repair (making the house electrically safe).
I know some electrians consider the connector you posted a safe repair method, but I was wondering about various AHJ's.



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
  #5  
Old 12/28/10, 3:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by jwilks View Post
I was wondering, as the local AHJ, what do you consider making the home electrically safe?
Great question. I don't feel like I can require any particular type of repair. Just that the receptacles have to be listed for use with aluminum wiring. This is part of what I'm demanding:

"...After the repair, the electrician shall provide to me a written statement on his company letterhead stating that the house has been thoroughly inspected and made electrically safe. The inspection must include a visual inspection of the condition and correct type for each outlet, switch, and circuit breaker in the home and the letter must specifically state that all branch circuit breakers and branch circuit switches and outlets are safe for use with aluminum wiring. According to the International Residential Code, the repair must include the installation of hard-wired and interconnected smoke alarms and the installation of arc-fault circuit interrupters and ground-fault circuit breakers where required."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 12/28/10, 10:30 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Alumimum wiring: house fire

Cop Alum Crimps are/were popular, at one time I think they were the only endorsed by the CPSC. The tools used are not available at Home Depot



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #7  
Old 12/28/10, 11:07 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Alumimum wiring: house fire

Well Tim / If the tools aren't available at HomeDepot, how is the owner gonna make repairs?
Reply With Quote
  #8  
Old 12/29/10, 5:28 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by jfunderburk View Post
Great question. I don't feel like I can require any particular type of repair. Just that the receptacles have to be listed for use with aluminum wiring. This is part of what I'm demanding:

"...After the repair, the electrician shall provide to me a written statement on his company letterhead stating that the house has been thoroughly inspected and made electrically safe. The inspection must include a visual inspection of the condition and correct type for each outlet, switch, and circuit breaker in the home and the letter must specifically state that all branch circuit breakers and branch circuit switches and outlets are safe for use with aluminum wiring. According to the International Residential Code, the repair must include the installation of hard-wired and interconnected smoke alarms and the installation of arc-fault circuit interrupters and ground-fault circuit breakers where required."
Well as long as I don't have to inspect any Light Fixtures or Ceiling Fans............
Reply With Quote
  #9  
Old 12/29/10, 6:19 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by jfunderburk View Post
This is part of what I'm demanding:

"...After the repair, the electrician shall provide to me a written statement on his company letterhead stating that the house has been thoroughly inspected and made electrically safe. The inspection must include a visual inspection of the condition and correct type for each outlet, switch, and circuit breaker in the home and the letter must specifically state that all branch circuit breakers and branch circuit switches and outlets are safe for use with aluminum wiring. According to the International Residential Code, the repair must include the installation of hard-wired and interconnected smoke alarms and the installation of arc-fault circuit interrupters and ground-fault circuit breakers where required."
Could you actually find an electrical contractor who would do this and accept the liability? And does anyone really have the authority to require this?
Reply With Quote
  #10  
Old 12/30/10, 10:27 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by bkelly2 View Post
Well as long as I don't have to inspect any Light Fixtures or Ceiling Fans............
Yep. I changed the letter...forgot about that initially.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 12/30/10, 10:28 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by Robert Meier View Post
Could you actually find an electrical contractor who would do this and accept the liability? And does anyone really have the authority to require this?
The one electrician I know of who has bid on the job said he would only re-wire the home....no "fixes".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 12/30/10, 10:29 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by Robert Meier View Post
And does anyone really have the authority to require this?
The house was involved in a fire due to unsafe wiring practices. Repairs requiring a permit must occur. I have the authority to demand a full (documented) inspection of the home and repair as deemed necessary by the electrician. They have the right to appeal it (but the appeal costs $200).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/30/10 at 10:33 AM..
Reply With Quote
  #13  
Old 12/30/10, 4:03 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by jfunderburk View Post
Yep. I changed the letter...forgot about that initially.
Good call then Joe, it looks like you have it all covered.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/30/10, 7:09 PM
Bruce D. Pinel Bruce D. Pinel is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: North Kingstown, RI
Posts: 173
Default Re: Alumimum wiring: house fire

I did a 3 family that had the 3rd floor completely rebuilt due to electrical fire caused by aluminum wire. The realtor told my client that all the aluminum was removed from the house until I showed him it was still in 2 of the four panels. In fact, the new 3rd floor had a sub panel in it that was doubled tapped off of the sub-panel lugs in the cellar. He called the electrician that did the work who came over to challange me. I asked him if he wanted me to call the AHJ as a mediator. The sad part is the AHJ approved the installation after the fire. Must have been a "phone-in."
Attached Thumbnails
alumimum-wiring-house-fire-alum.jpg   alumimum-wiring-house-fire-double-tap.jpg  



S & B Services LLC
www.rihomeinspectionsbs.com
FHA/HUD Compliance Inspector S127

Reply With Quote
  #15  
Old 12/30/10, 8:17 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alumimum wiring: house fire

Quote:
Originally Posted by bpinel View Post
I did a 3 family that had the 3rd floor completely rebuilt due to electrical fire caused by aluminum wire. The realtor told my client that all the aluminum was removed from the house until I showed him it was still in 2 of the four panels. In fact, the new 3rd floor had a sub panel in it that was doubled tapped off of the sub-panel lugs in the cellar. He called the electrician that did the work who came over to challange me. I asked him if he wanted me to call the AHJ as a mediator. The sad part is the AHJ approved the installation after the fire. Must have been a "phone-in."
A building official/inspector would be overstepping his authority by demanding that aluminum wiring be removed. The double-tapping should have been caught, however.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector law suit rcooke Canadian Inspectors 0 2/18/10 11:48 AM
old wiring systems in homes? rlondon Electrical Inspections 4 5/20/09 6:07 PM
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM


All times are GMT -4. The time now is 5:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts