Default Aluminum/Copper connector

Anyone seen these new copper/aluminum connectors out there? Know anything about them? I have a friend who is doing some re-modeling in his home and he wants to make sure his connections are safe. He is asking me about them, but I've not seen them before.

http://www.alcopstore.com/



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #2  
Old 2/28/08, 12:02 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

There have been several discussions here about these. It is probably as good a solution as there is if you have the room in the box for them. They are as good as the heavily hyped Copalum
Reply With Quote
  #3  
Old 2/28/08, 1:36 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by Greg Fretwell
There have been several discussions here about these. It is probably as good a solution as there is if you have the room in the box for them. They are as good as the heavily hyped Copalum
I did a thread search, but didn't see any references. Got any links?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 2/28/08, 4:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Aluminum/Copper connector

I agree with Greg. These are a good alternative to the Copalum crimps, and don't require any special training or "certifications."

The only down-sides (if you will) is that these aren't an "irreversible" connection and they require that the installer provide proper torque, which requires the proper tool. Homeowners or other unqualified personnel may be inclined to disregard the torque requirements rather than purchase a torque-driver.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/28/08, 5:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

I got a baggie of these for free from a salesman, but I keep forgetting that I have them. I'll have to give them a whirl one day. They are bigger than they look on an internet picture, so they'll fill the box up pretty quick. As with any aluminium termination, the use of a torque screwdriver is an absolute must. Furthermore, if an electrical contractor is installing these, his torque screwdriver had best have recent verifiable calibration as a simple CYA move. The calibration date of the torque screwdriver should be recorded on the invoice and any other paperwork associated with the aluminium job.
Reply With Quote
  #6  
Old 2/28/08, 5:37 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum/Copper connector

There is an alternative approved torquing method. Which doesn't require a torque wrench.

Just follow the directions.

tom

P.S. The only way to make solid branch wire 100% safe is to remove it, so there is a risk associated with everything. Including crossing a street or eating, or even sleeping.
Reply With Quote
  #7  
Old 2/28/08, 5:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by tdietrich1
There is an alternative approved torquing method. Which doesn't require a torque wrench.

Just follow the directions.
Huh? The directions clearly specify a torque value for each gauge size. You really have no choice but to use a torque screwdriver, unless you happen to have a calibrated wrist.

http://www.kinginnovation.com/pdfs/5...-AlumiConn.pdf
Reply With Quote
  #8  
Old 2/28/08, 10:59 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by Marc D. Shunk
unless you happen to have a calibrated wrist.
Don't have a calibrated wrist, but I do have the ability to read the whole page. Check out section labeled "Manufacturer Approved Alternative Torque Method" Now it's only for solid wire, but that's the only aluminum wire I'm VERY concerned about.

tom
Reply With Quote
  #9  
Old 2/29/08, 8:09 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Aluminum/Copper connector

Quote:
3A) Manufacturer-Approved Alternate Torque Method for Use on Solid Wire Only
Using a screwdriver, tighten set screw until it comes into contact with the solid conductor. Note location of screwdriver slot and continue tightening the set screw as indicated below. Note: This method is not associated with the UL listing.
What does that last sentence mean? Does it mean the device looses UL approval if that method is used?
Reply With Quote
  #10  
Old 2/29/08, 11:29 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Aluminum/Copper connector

The listing is given based on use of the proper tool. That sentence pretty much says it all - it's not a listed connector unless it has been properly torqued.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/29/08, 5:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by jpope
The listing is given based on use of the proper tool. That sentence pretty much says it all - it's not a listed connector unless it has been properly torqued.
You got it. Plus, the NEC, 110.3(B) requires electricians to install equipment in accordance with its listing and labeling. In a nutshell, it is to be installed exactly the way the UL evaluated it, or the product is basicly being misused. The manufacturer can approve a given method, but unless the UL evaluated that alternate method, it's a non-UL compliant use of the product.

You could use a radiator hose clamp to hook a ground wire to a pipe and it might do a fine job, but the UL never evaluated radiator hose clamps for grounding use. This is just a parallel example.
Reply With Quote
  #12  
Old 3/1/08, 12:35 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

Question: Are CO/ALR devices avaiable, or are they hard too find?
Reply With Quote
  #13  
Old 3/1/08, 1:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by jtedesco1
Question: Are CO/ALR devices available, or are they hard too find?
They seem to be more available in areas where aluminium branch circuit wiring was commonly installed in the day, and less available where aluminium wiring was not ever commonly installed. The ready availability concerns me some, since the mis-application of a co/alr device or fitting can create more of a hazard than leaving the device alone in the first place.
Reply With Quote
  #14  
Old 3/1/08, 1:30 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by jtedesco1
Question: Are CO/ALR devices avaiable, or are they hard too find?

Lowes
Reply With Quote
  #15  
Old 3/1/08, 2:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum/Copper connector

Quote:
Originally Posted by tdietrich1
Lowes
That's about the only place I can find them in my area as well. I very rarely need a co/alr switch or receptacle, since there is little aluminium wiring in our area. Not much point in the regular electrical suppliers stocking them. Anything can be ordered off the 'net for delivery in a couple days, so it's really no big deal.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas appliance connector mboyett Inspecting HVAC Systems 14 12/27/07 7:51 AM
Gas flex connector to furnace jcahill Inspecting HVAC Systems 25 7/24/07 6:22 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Help Identifying connector Steven Brewster Electrical Inspections 5 4/10/06 11:00 PM


All times are GMT -4. The time now is 5:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts