Old 11/5/06, 11:29 AM
mwright1's Avatar
mwright1 mwright1 is offline
Please Note: mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Aluminum Ground - Allowed??
Is single strand aluminum allowed to be used as a ground? I'd never seen this before?
Old 11/5/06, 11:37 AM
Paul W. Abernathy's Avatar
Default Re: Aluminum Ground - Allowed??
250.62 Grounding Electrode Conductor Material.
The grounding electrode conductor shall be of copper, aluminum,
or copper-clad aluminum. The material selected shall be resistant
to any corrosive condition existing at the installation or
shall be suitably protected against corrosion. The conductor
shall be solid or stranded, insulated, covered, or bare.
250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as speci-
.ed in 250.64(A) through (F).
(A) Aluminum or Copper-Clad Aluminum Conductors.
Bare aluminum or copper-clad aluminum grounding conductors
shall not be used where in direct contact with masonry
or the earth or where subject to corrosive conditions.
Where used outside, aluminum or copper-clad aluminum
grounding conductors shall not be terminated within 450 mm
(18 in.) of the earth.
Paul W. Abernathy,CMI,CPI,CME
Old 11/5/06, 11:41 AM
mwright1's Avatar
Paul - thanks for the fast response. Dumb question though...250.64 states that bare aluminum shouldn't be used if it's in direct contact with masonary or earth, is this ground still ok? It was mounted along a joist and grounded only to the plumbing. Nothing touching masonary or earth?
mwright1's Avatar
Paul - also, I took your electrical class several months ago. Great class.
Old 11/5/06, 12:07 PM
Jeffrey R. Pope's Avatar
As long as it is not in contact it's okay. This appears to be a bonding conductor rather than a grounding conductor.
Were you able to see where the piping was in contact with "earth?"
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 11/5/06, 12:09 PM
Tab M. Wilcox Tab M. Wilcox is offline
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Gotta love the grounds and neutrals that are twisted together!
Old 11/5/06, 1:15 PM
tdietrich1's Avatar
Yeah saw that too, especially how they are barely under the screws, or even multiple wires under a screw. Defer to a qualified electrician. But then this is beyond the scope of the OP.
imho,
tom
Old 11/5/06, 4:08 PM
OK...back....
Ok....now the question Jeff bought up is....is this the Bonding or is this the GEC.......quite funny now....
While 250.102 does have a " sniglet" about the equipment bonding conductors being copper or some other corrosive resistant material.....
Generally Alum is acceptacle....BUT used very rare........
Old 11/5/06, 4:14 PM
Oh.......with that said and hearing as I go around the country doing these seminars...the understanding of BONDING is not very well known...except for in Sacramento, CA...where when I was explaining it they all had a EUREKA moment...lol......
IN this case based on what I see......I would not say it is the bonding conductor.....since in older homes it is probably rare they even knew how do bond correctly...so I would say it is the GEC to the Water Pipe.....but again I could be wrong...lol...but I doubt it...
Oh.......who can I guess this...look at the picture of the panel....it looks like the small terminal buss under the large one has the larger solid aluminim running out of it.....BUT no other larger copper lines...???? SO.......the knew about the GEC before they truly undstand the meaning of bonding...so I can safely say I think it was the attempt at the GEC...
Ok......done
Old 11/5/06, 4:57 PM
mwright1's Avatar
This had to have been the grounding wire. I did not see any other grounds. No copper or other wires coming out of the box. I didn't see a bonding element either. I am recommending further evaluation because of double taps, and signs of arching.
Thanks everyone for their help.
Old 11/5/06, 5:30 PM
I doubt you're wrong, but the question remains in my mind (based on what's visible in the picture). Is that water pipe "effectively grounded?"
Also, if I remember correctly, in residential applications the GEC attachment should be within 5 feet of the point where the water pipe enters the home.
The picture in the OP shows the piping system in, what appears to be, a crawl space, which would mean the only potential for effective grounding would be near the main water line.
Jeff Pope
Santa Clarita CA
(661) 212-0738
Old 11/5/06, 5:41 PM
mwright1's Avatar
Jeff - I had also heard the 5 foot rule and in this case it is no where near that. The water enters the house in an adjacent room to where it's connect to the plumbing.
Old 11/5/06, 5:48 PM
Well if someone doesn't chime in soon, I guess I'll have to look up the reference. . .
Jeff Pope
Santa Clarita CA
(661) 212-0738
Old 11/5/06, 6:16 PM
lol.....if you mean me chime in Jeff....lol....the reference on the distance is NEC Article 250.52(A)(1)
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe.
A metal underground
water pipe in direct contact with the earth for 3.0 m
(10 ft) or more (including any metal well casing effectively
bonded to the pipe) and electrically continuous (or made
electrically continuous by bonding around insulating joints
or insulating pipe) to the points of connection of the
grounding electrode conductor and the bonding conductors.
Interior metal water piping located more than 1.52 m (5 ft)
from the point of entrance to the building shall not be used
as a part of the grounding electrode system or as a conductor
to interconnect electrodes that are part of the grounding
electrode system.
Exception: In industrial and commercial buildings or
structures where conditions of maintenance and supervision
ensure that only quali.ed persons service the installation,
interior metal water piping located more than 1.52 m
(5 ft) from the point of entrance to the building shall be
permitted as a part of the grounding electrode system or as
a conductor to interconnect electrodes that are part of the
grounding electrode system, provided that the entire length,
other than short sections passing perpendicular through
walls, .oors, or ceilings, of the interior metal water pipe
that is being used for the conductor is exposed.
Old 11/5/06, 8:45 PM
mwright1's Avatar
Thank Paul and Jeff....as always...great advice.
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM