250.62 Grounding Electrode Conductor Material. The grounding electrode conductor shall be of copper, aluminum, or copper-clad aluminum. The material selected shall be resistant to any corrosive condition existing at the installation or shall be suitably protected against corrosion. The conductor shall be solid or stranded, insulated, covered, or bare. 250.64 Grounding Electrode Conductor Installation. Grounding electrode conductors shall be installed as speci- .ed in 250.64(A) through (F). (A) Aluminum or Copper-Clad Aluminum Conductors. Bare aluminum or copper-clad aluminum grounding conductors
shall not be used where in direct contact with masonry or the earth or where subject to corrosive conditions. Where used outside, aluminum or copper-clad aluminum grounding conductors shall not be terminated within 450 mm (18 in.) of the earth. Paul W. Abernathy |
|
#3
|
||||
|
||||
|
Please Note:
mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul - thanks for the fast response. Dumb question though...250.64 states that bare aluminum shouldn't be used if it's in direct contact with masonary or earth, is this ground still ok? It was mounted along a joist and grounded only to the plumbing. Nothing touching masonary or earth?
|
|
#4
|
||||
|
||||
|
Please Note:
mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul - also, I took your electrical class several months ago. Great class.
|
|
#5
|
||||
|
||||
|
As long as it is not in contact it's okay. This appears to be a bonding conductor rather than a grounding conductor.
Were you able to see where the piping was in contact with "earth?" IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Gotta love the grounds and neutrals that are twisted together!
|
|
#7
|
||||
|
||||
|
Quote:
imho, tom |
|
#8
|
|||
|
|||
|
OK...back....
Ok....now the question Jeff bought up is....is this the Bonding or is this the GEC.......quite funny now.... While 250.102 does have a " sniglet" about the equipment bonding conductors being copper or some other corrosive resistant material..... Generally Alum is acceptacle....BUT used very rare........ Paul W. Abernathy |
|
#9
|
|||
|
|||
|
Oh.......with that said and hearing as I go around the country doing these seminars...the understanding of BONDING is not very well known...except for in Sacramento, CA...where when I was explaining it they all had a EUREKA moment...lol......
IN this case based on what I see......I would not say it is the bonding conductor.....since in older homes it is probably rare they even knew how do bond correctly...so I would say it is the GEC to the Water Pipe.....but again I could be wrong...lol...but I doubt it... Oh.......who can I guess this...look at the picture of the panel....it looks like the small terminal buss under the large one has the larger solid aluminim running out of it.....BUT no other larger copper lines...???? SO.......the knew about the GEC before they truly undstand the meaning of bonding...so I can safely say I think it was the attempt at the GEC... Ok......done Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Please Note:
mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
This had to have been the grounding wire. I did not see any other grounds. No copper or other wires coming out of the box. I didn't see a bonding element either. I am recommending further evaluation because of double taps, and signs of arching.
Thanks everyone for their help. |
|
#11
|
||||
|
||||
|
Quote:
Also, if I remember correctly, in residential applications the GEC attachment should be within 5 feet of the point where the water pipe enters the home. The picture in the OP shows the piping system in, what appears to be, a crawl space, which would mean the only potential for effective grounding would be near the main water line. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Please Note:
mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff - I had also heard the 5 foot rule and in this case it is no where near that. The water enters the house in an adjacent room to where it's connect to the plumbing.
|
|
#13
|
||||
|
||||
|
Well if someone doesn't chime in soon, I guess I'll have to look up the reference. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 11/5/06 at 5:30 PM.. |
|
#14
|
|||
|
|||
|
lol.....if you mean me chime in Jeff....lol....the reference on the distance is NEC Article 250.52(A)(1)
250.52 Grounding Electrodes. (A) Electrodes Permitted for Grounding. (1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing effectively bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system. Exception: In industrial and commercial buildings or structures where conditions of maintenance and supervision ensure that only quali.ed persons service the installation, interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall be permitted as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system, provided that the entire length, other than short sections passing perpendicular through walls, .oors, or ceilings, of the interior metal water pipe that is being used for the conductor is exposed. Paul W. Abernathy |
|
#15
|
||||
|
||||
|
Please Note:
mwright1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank Paul and Jeff....as always...great advice.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Ground Wires Inside a Panel | mveitenhans | Electrical Inspections | 13 | 10/29/06 11:39 AM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical Inspections | 5 | 3/21/06 8:48 AM |