Default Aluminum Ground - Allowed??

Is single strand aluminum allowed to be used as a ground? I'd never seen this before?

aluminum-ground-allowed-pic-227.jpg

aluminum-ground-allowed-pic-230.jpg
Reply With Quote
  #2  
Old 11/5/06, 11:37 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Aluminum Ground - Allowed??


250.62 Grounding Electrode Conductor Material.
The grounding electrode conductor shall be of copper, aluminum,
or copper-clad aluminum. The material selected shall be resistant
to any corrosive condition existing at the installation or
shall be suitably protected against corrosion. The conductor
shall be solid or stranded, insulated, covered, or bare.

250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as speci-
.ed in 250.64(A) through (F).
(A) Aluminum or Copper-Clad Aluminum Conductors.
Bare aluminum or copper-clad aluminum grounding conductors
shall not be used where in direct contact with masonry
or the earth or where subject to corrosive conditions.
Where used outside, aluminum or copper-clad aluminum
grounding conductors shall not be terminated within 450 mm
(18 in.) of the earth.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 11/5/06, 11:41 AM
Michael J. Wright's Avatar
Michael J. Wright Michael J. Wright is offline
InterNACHI Member
 
Join Date: Feb 2005
Posts: 64
Default Re: Aluminum Ground - Allowed??

Paul - thanks for the fast response. Dumb question though...250.64 states that bare aluminum shouldn't be used if it's in direct contact with masonary or earth, is this ground still ok? It was mounted along a joist and grounded only to the plumbing. Nothing touching masonary or earth?
Reply With Quote
  #4  
Old 11/5/06, 11:41 AM
Michael J. Wright's Avatar
Michael J. Wright Michael J. Wright is offline
InterNACHI Member
 
Join Date: Feb 2005
Posts: 64
Default Re: Aluminum Ground - Allowed??

Paul - also, I took your electrical class several months ago. Great class.
Reply With Quote
  #5  
Old 11/5/06, 12:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: Aluminum Ground - Allowed??

As long as it is not in contact it's okay. This appears to be a bonding conductor rather than a grounding conductor.

Were you able to see where the piping was in contact with "earth?"



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 11/5/06, 12:09 PM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Ground - Allowed??

Gotta love the grounds and neutrals that are twisted together!
Reply With Quote
  #7  
Old 11/5/06, 1:15 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum Ground - Allowed??

Quote:
Originally Posted by Tab M. Wilcox
Gotta love the grounds and neutrals that are twisted together!
Yeah saw that too, especially how they are barely under the screws, or even multiple wires under a screw. Defer to a qualified electrician. But then this is beyond the scope of the OP.

imho,

tom
Reply With Quote
  #8  
Old 11/5/06, 4:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Aluminum Ground - Allowed??

OK...back....

Ok....now the question Jeff bought up is....is this the Bonding or is this the GEC.......quite funny now....

While 250.102 does have a " sniglet" about the equipment bonding conductors being copper or some other corrosive resistant material.....

Generally Alum is acceptacle....BUT used very rare........



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 11/5/06, 4:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Aluminum Ground - Allowed??

Oh.......with that said and hearing as I go around the country doing these seminars...the understanding of BONDING is not very well known...except for in Sacramento, CA...where when I was explaining it they all had a EUREKA moment...lol......

IN this case based on what I see......I would not say it is the bonding conductor.....since in older homes it is probably rare they even knew how do bond correctly...so I would say it is the GEC to the Water Pipe.....but again I could be wrong...lol...but I doubt it...

Oh.......who can I guess this...look at the picture of the panel....it looks like the small terminal buss under the large one has the larger solid aluminim running out of it.....BUT no other larger copper lines...???? SO.......the knew about the GEC before they truly undstand the meaning of bonding...so I can safely say I think it was the attempt at the GEC...

Ok......done



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 11/5/06, 4:57 PM
Michael J. Wright's Avatar
Michael J. Wright Michael J. Wright is offline
InterNACHI Member
 
Join Date: Feb 2005
Posts: 64
Default Re: Aluminum Ground - Allowed??

This had to have been the grounding wire. I did not see any other grounds. No copper or other wires coming out of the box. I didn't see a bonding element either. I am recommending further evaluation because of double taps, and signs of arching.

Thanks everyone for their help.
Reply With Quote
  #11  
Old 11/5/06, 5:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: Aluminum Ground - Allowed??

Quote:
Originally Posted by pabernathy
IN this case based on what I see......I would not say it is the bonding conductor.....since in older homes it is probably rare they even knew how do bond correctly...so I would say it is the GEC to the Water Pipe.....but again I could be wrong...lol...but I doubt it...
I doubt you're wrong, but the question remains in my mind (based on what's visible in the picture). Is that water pipe "effectively grounded?"

Also, if I remember correctly, in residential applications the GEC attachment should be within 5 feet of the point where the water pipe enters the home.

The picture in the OP shows the piping system in, what appears to be, a crawl space, which would mean the only potential for effective grounding would be near the main water line.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #12  
Old 11/5/06, 5:41 PM
Michael J. Wright's Avatar
Michael J. Wright Michael J. Wright is offline
InterNACHI Member
 
Join Date: Feb 2005
Posts: 64
Default Re: Aluminum Ground - Allowed??

Jeff - I had also heard the 5 foot rule and in this case it is no where near that. The water enters the house in an adjacent room to where it's connect to the plumbing.
Reply With Quote
  #13  
Old 11/5/06, 5:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: Aluminum Ground - Allowed??

Well if someone doesn't chime in soon, I guess I'll have to look up the reference. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 11/5/06 at 6:30 PM..
Reply With Quote
  #14  
Old 11/5/06, 6:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Aluminum Ground - Allowed??

lol.....if you mean me chime in Jeff....lol....the reference on the distance is NEC Article 250.52(A)(1)



250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe.
A metal underground
water pipe in direct contact with the earth for 3.0 m
(10 ft) or more (including any metal well casing effectively
bonded to the pipe) and electrically continuous (or made
electrically continuous by bonding around insulating joints
or insulating pipe) to the points of connection of the
grounding electrode conductor and the bonding conductors.
Interior metal water piping located more than 1.52 m (5 ft)
from the point of entrance to the building shall not be used
as a part of the grounding electrode system or as a conductor
to interconnect electrodes that are part of the grounding
electrode system.




Exception: In industrial and commercial buildings or

structures where conditions of maintenance and supervision
ensure that only quali.ed persons service the installation,
interior metal water piping located more than 1.52 m
(5 ft) from the point of entrance to the building shall be
permitted as a part of the grounding electrode system or as
a conductor to interconnect electrodes that are part of the
grounding electrode system, provided that the entire length,
other than short sections passing perpendicular through
walls, .oors, or ceilings, of the interior metal water pipe
that is being used for the conductor is exposed.




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 11/5/06, 8:45 PM
Michael J. Wright's Avatar
Michael J. Wright Michael J. Wright is offline
InterNACHI Member
 
Join Date: Feb 2005
Posts: 64
Default Re: Aluminum Ground - Allowed??

Thank Paul and Jeff....as always...great advice.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Ground Wires Inside a Panel mveitenhans Electrical 13 10/29/06 12:39 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 8:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts