Default Re: Aluminum Ground - Allowed??

The 5-foot rule seems dubious now that plastic is allowed as underground water supply piping.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #17  
Old 11/7/06, 9:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Aluminum Ground - Allowed??

Not dubious........it only applies if the water pipe is Metal....and atleast 10' within the ground....if not present...not used.....



Paul W. Abernathy
Reply With Quote
  #18  
Old 11/7/06, 9:44 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Aluminum Ground - Allowed??

How can you tell how far into the metal pipe extends before it changes to plastic?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #19  
Old 11/7/06, 9:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Aluminum Ground - Allowed??

The plastic usually come all the way INTO the house and does not change out into the ground. So usually the location point is at the point of enterance of the water pipe systems.

Usually when plastic is being used it is again bought all the way into the dwelling....



Paul W. Abernathy
Reply With Quote
  #20  
Old 11/8/06, 11:50 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum Ground - Allowed??

Quote:
Originally Posted by kshepard
How can you tell how far into the metal pipe extends before it changes to plastic?
Once place where the NEC accepts reality as part of factor in determining what is 'OK' and what is not. If you use the water pipe as your grounding electrode (which is required if you can determine -sometimes as an educated guess since you can't see in the ground), then you still have to back it up with ground rod(s), ground plate, etc, etc...... So the water pipe seems to never be your sole grounding electrode.

Now back to what the HI can do. Contact the water department, find out if they use only metal supplies or switched over any time.

tom
Reply With Quote
  #21  
Old 11/8/06, 6:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Aluminum Ground - Allowed??

Quote:
Originally Posted by tdietrich1
Once place where the NEC accepts reality as part of factor in determining what is 'OK' and what is not. If you use the water pipe as your grounding electrode (which is required if you can determine -sometimes as an educated guess since you can't see in the ground), then you still have to back it up with ground rod(s), ground plate, etc, etc...... So the water pipe seems to never be your sole grounding electrode.

Now back to what the HI can do. Contact the water department, find out if they use only metal supplies or switched over any time.

tom
Educational Moment - In many older homes guys you will see the water pipe as the only GE....sad but true.......However, you should suggest to them a supplimental grounding electrode be added...now if they do it...thats their problem but in my opinion it should be suggested as a enhancement.



Paul W. Abernathy
Reply With Quote
  #22  
Old 11/8/06, 6:18 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum Ground - Allowed??

Quote:
Originally Posted by pabernathy
in my opinion it should be suggested as a enhancement.
Good advice!

I can personally say, keeping voltage transients to a min will preserve sensitive electronics in your house.

tom
Reply With Quote
  #23  
Old 11/8/06, 6:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Aluminum Ground - Allowed??

I always suggest a supplemental grounding electrode if the water pipes are the sole GE. It's too often that re-piping of the home and/or main disconnects the original GE.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #24  
Old 11/8/06, 6:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Aluminum Ground - Allowed??

Most certainly....and with the possible issue of connections being old and worn out, corroded and who knows....always a good suggesting to mention about the supplimental.....



Paul W. Abernathy
Reply With Quote
  #25  
Old 6/12/10, 9:49 AM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Aluminum Ground - Allowed??

Recently found this in a water heater closet so I am guessing this is not good as the WH is in a closet some 30 feet from the water entrance located in the attached garage.

Aside from the fact that the rod was loose and I could move it easily.
Attached Thumbnails
aluminum-ground-allowed-pict0022.jpg  



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #26  
Old 6/12/10, 11:32 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Aluminum Ground - Allowed??

This is a bonding connection, not a grounding connection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #27  
Old 6/12/10, 12:22 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Ground - Allowed??

The requirement to be within 5' of the entrance is a fairly recent change. In the past any accessible portion was acceptable for the grounding.


Not sure why T-stat or doorbell wire was used or the purpose.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM


All times are GMT -4. The time now is 2:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts