Default Aluminum wire fire

Just got this Email from a fellow inspector posted here with his permission
See updated PDF

Hey Guys,

Conducted an inspection yesterday on a 1960’s house in Dallas. Bank owned. Aluminum wiring. The whole nine yards. Anyway, thought I was going to have to call the fire department. During my sampling of outlets to check wire connections, had an outlet and wires arc and start a small fire in the box. See pictures attached. Anyway, what I’ve read about “pig tailing” as unreliable was demonstrated yesterday. Obviously turned power off to property and alerted selling agent immediately. Also,

I’ve also attached a document with some updated information about aluminum wiring I thought you might be interested in. That’s it, stay safe!

Regards,


Brian Bassett, TREC #6581
Wall-2-Wall Home Inspections
817.721.4778 (cell)
brianbassett@tx.rr.com
www.wall2wallhomeinspections.com



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:21 PM..
Reply With Quote
  #2  
Old 1/23/08, 5:33 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: Aluminum wire fire

Thanks Barry
Reply With Quote
  #3  
Old 1/23/08, 8:06 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Aluminum wire fire

Quote:
Originally Posted by badair
Just got this Email from a fellow inspector posted here with his permission
See updated PDF

Hey Guys,

Conducted an inspection yesterday on a 1960’s house in Dallas. Bank owned. Aluminum wiring. The whole nine yards. Anyway, thought I was going to have to call the fire department. During my sampling of outlets to check wire connections, had an outlet and wires arc and start a small fire in the box. See pictures attached. Anyway, what I’ve read about “pig tailing” as unreliable was demonstrated yesterday. Obviously turned power off to property and alerted selling agent immediately. Also,

I’ve also attached a document with some updated information about aluminum wiring I thought you might be interested in. That’s it, stay safe!

Regards,


Brian Bassett, TREC #6581
Wall-2-Wall Home Inspections
817.721.4778 (cell)
brianbassett@tx.rr.com
www.wall2wallhomeinspections.com
Sounds like he saved a house from burning down.

Is it typical for TREC inspectors to "sample outlets to check wire connections"?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 1/23/08, 8:20 PM
Brian Bassett Brian Bassett is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Arlington, TX
Posts: 8
Default Re: Aluminum wire fire

Hi Larry,

Yes TREC SOP states "Inspect (if branch circuit aluminum wiring is discovered in the main or subpanels) a random sampling of accessible receptacles and switches and report as in need of repair the absence of appropriate connections, such as copper/aluminum approved devices, pig-tailed connections or crimp connections".

The buyer was very happy to have this information before purchasing this property.
Reply With Quote
  #5  
Old 1/23/08, 8:32 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Aluminum wire fire

Quote:
Originally Posted by bbassett
Hi Larry,

Yes TREC SOP states "Inspect (if branch circuit aluminum wiring is discovered in the main or subpanels) a random sampling of accessible receptacles and switches and report as in need of repair the absence of appropriate connections, such as copper/aluminum approved devices, pig-tailed connections or crimp connections".

The buyer was very happy to have this information before purchasing this property.
I bet they were happy.

Thanks for the info.

Nice job!



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 1/23/08, 11:47 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum wire fire

That looks more like a short than a loose connection. Did a wirenut pop off or a wire break and short to the box?
Reply With Quote
  #7  
Old 1/24/08, 12:21 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum wire fire

I see in that second picture that you found my 10-in-1. Thanks for keeping it safe for me.
Reply With Quote
  #8  
Old 1/24/08, 6:08 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Aluminum wire fire

Quote:
Originally Posted by lkage
Sounds like he saved a house from burning down.

Is it typical for TREC inspectors to "sample outlets to check wire connections"?
Larry,

Here is a link to the rules Texans work under...

TREC Rules

thanx JP

also AlumiConn will send samples and flyers



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 1/24/08 at 6:13 AM..
Reply With Quote
  #9  
Old 1/24/08, 8:55 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum wire fire

I've run into this in the past. Ideal makes Al purple wire nuts. Some people see the cost and then next to them, are regular purple wire nuts. Another glance, they find no-oxide compound the shelf below, and the the light bulb goes on. Why pay $10 for four Ideal Al Purple Wire Nuts, when for $4 you can make a whole bunch of home-made ones!

tom
Reply With Quote
  #10  
Old 1/24/08, 10:22 AM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Aluminum wire fire

Barry & Brian -

Good info!

Permission to use photos please!


-- bz



Brian Zimbelman
Circle Z Inspection Services
http://www.circlezinspections.com
575-535-4481 (wk)
575-313-1281 (cell)
Reply With Quote
  #11  
Old 1/24/08, 12:10 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Aluminum wire fire

Barry; I'm mot sure from your post if the pigtailing was or was not done with approved connectiors. If approved were they "COPALUM" or "ALUMICONN"?
Reply With Quote
  #12  
Old 1/25/08, 8:43 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Aluminum wire fire

Quote:
Originally Posted by kgerhauser
Barry; I'm mot sure from your post if the pigtailing was or was not done with approved connectiors. If approved were they "COPALUM" or "ALUMICONN"?
The "Ideal" purple wire (which appears to be what is pictured) nut is UL approved and, accordingly, is NEC approved --- but the Consumer Product Safety Commission and others have recommended strongly against their use. CPSC favors the Copalum clip in its place.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #13  
Old 1/25/08, 9:13 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Aluminum wire fire

Quote:
Originally Posted by kgerhauser
Barry; I'm mot sure from your post if the pigtailing was or was not done with approved connectors. If approved were they "COPALUM" or "ALUMICONN"?
Karl,
This wasn't my inspection and the photo is too fuzzy to be certain, but as I James stated and from what I can see these appear to be the Ideal 65 "Twister"

here's the AlumiConn in action, obviously due to their size/configuration excessive bending stress and box overfill is/may be an issue



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:21 PM..
Reply With Quote
  #14  
Old 1/25/08, 12:06 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Aluminum wire fire

Thank, I couldn't tell anything, but black and melty, from the photo. I have not seen the ideal twister in this area, I was hoping this wasn't "COPALUM" that I have seen.
Reply With Quote
  #15  
Old 1/26/08, 11:34 AM
Brian Bassett Brian Bassett is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Arlington, TX
Posts: 8
Default Re: Aluminum wire fire

Yes,
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM