I received this email Today.

How do you report conditions related to Aluminum wiring when encountered.

From: XXXXXXXXXXXXXXXXXXXXXXXXX
Sent: Tuesday, October 02, 2007 11:16 AM
To: joseph.hagarty@housemaster.com
Subject: Aluminum wiring

Joe,

I just went through a small claims law suit. I used the NACHI forums for some research. I came across a forum with you and some others speaking back and forth about Copalum crimping and aluminum wiring. I am not a member so I could not post. I was the seller of a home in Phoenix. The buyer read the inspectors summary report making the general “fire hazard” statements about aluminum wiring and recommended seeking counsel of an electrician and with proper methods “such as Copalum crimp”. The buyer stupidly copied and pasted from the summary report of the inspection to make his repair request. The electrician and I interpreted it as repair outlets or switches properly that are not working. All of outlets and switches did work by the way. The buyer was thinking the entire house every switch, outlet and connection needed to be Copalum crimped. The buyer ends up trying to sue me to have everything Copalum crimped in the house. The judge sided in our favor within minutes saying that “we agreed to repair not to update the house”.

Copalum crimping is an extremely expensive method. Each Copalum nut is $2.70 (in Phoenix), must be performed by a certified electrician who has gone through a certified Copalum crimp school. Copalum crimp is not a common method nor is it the only method approved by the NEC. I like the fact that you refer electrical stuff to an electrician. Too many inspectors are or inadvertently advising a little too much and those buyers who lack any common sense think take every word to heart. Too many people are looking at the smear campaign all over the internet concerning aluminum wiring. I wonder what company is behind all of that????? No home inspector should ever mention only one method of repair. They should either mention all of them or none of them. Please post this for me. Anyone is welcome to ask about my situation via email. I emailed this to you since your email was the only one I found of the posters.

Thanks,

XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #2  
Old 10/2/07, 2:10 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum Wiring

Once again Joe,

Good stuff.

tom
Reply With Quote
  #3  
Old 10/2/07, 3:13 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

I think the concerns around aluminum wiring are very real. I have yet to see an aluminum wired house without some sort of past/present arcing condition (burned wires, melted wirenuts, buzzing switches)----I don't think there is any "smear" campaign against aluminum wiring. Copalum connections are the only CPSC approved connection regardless of what the NEC says----I would like to see a reference of the NEC saying anything one way or the other about it.
Reply With Quote
  #4  
Old 10/2/07, 3:29 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Quote:
Originally Posted by cbuell
I think the concerns around aluminum wiring are very real. I have yet to see an aluminum wired house without some sort of past/present arcing condition (burned wires, melted wirenuts, buzzing switches)----I don't think there is any "smear" campaign against aluminum wiring. Copalum connections are the only CPSC approved connection regardless of what the NEC says----I would like to see a reference of the NEC saying anything one way or the other about it.
And I am on the other side of the fence .
I had aluminum in my last home and never had a concern.
I have inspected many homes with Aluminum wire and also have never had a concern .
Now Insurance companies are a different thing .
I was looking to but a nice home in Brighton and it had Aluminum no insurance company in this area would give a insurance .
Now I do a lot of inspections in Port Hope 25 miles away and 90% of the home in one area are all wired with aluminum and they never have a problem getting insurance.
Ontario Hydro has never condemned Aluminum wire in Canada.

.... Cookie
Reply With Quote
  #5  
Old 10/2/07, 3:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Aluminum Wiring

Quote:
Originally Posted by cbuell
Copalum connections are the only CPSC approved connection regardless of what the NEC says
That's correct. The only "permanent" correction (short of rewiring the home) as advised by the CPSC. That's why we will suggest cop-alum crimps.

The NEC does not address "corrective measures" for problematic or deficient systems. However, as the poster stated, there are other alternatives. None of which are advised by the CPSC. If your electrician suggests a less expensive correction, he is certainly well within his rights to do so, as he is assuming the liability for the repairs.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 10/2/07, 3:38 PM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Aluminum Wiring

http://www.inspect-ny.com/aluminum/aluminum.htm

http://www.cpsc.gov/CPSCPUB/PREREL/prhtml03/03120.html

http://www.cpsc.gov/CPSCPUB/PREREL/prhtml74/74040.html



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 10/2/07, 5:38 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: Aluminum Wiring

I too am from the side of the fence that solid conductor aluminum wiring is a potential hazard. About half of the homes in a sub-division I live in late in the 80's had aluminum wiring. Several house fires occurred during the five years I lived there, and all were due to the aluminum wiring.

I call out it's presence in the home, and defer to an electrician for a thorough evaluation of the electric system.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #8  
Old 10/2/07, 6:35 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum Wiring

imho,

I'm a fan of these: http://www.alumiconn.com/ Never than the cpsc posts here, and NEC compliant.

tom
Reply With Quote
  #9  
Old 10/2/07, 6:55 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

To square with teh NEC, you could go out this very day and wire an entire home with aluminium wiring if you wanted to. That would be dumb of you, but it's still permissible.

I handle aluminium wired homes with more of a hybrid repair method. Replace as much as can be replaced with copper, without doing damage to the wall and ceiling finishes. What's left, either CopAlum or change the devices to AL/CU rated one's and put them on an annual PM program to check the aluminium terminations each year.
Reply With Quote
  #10  
Old 10/2/07, 7:01 PM
mbarnett mbarnett is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Lancaster, CA
Posts: 19
Default Re: Aluminum Wiring

Guys... come on,
If a solid aluminum conductor is found during an inspection simply refer it out to a licensed electrician for evaluation instead of providing a "specialist solution". We all know (or should if we actually read NACHI's Electircal Course) that the presence of a solid aluminum conductor is an issue. Let the electrician determine what fix they are going to use not us. Remember "non-invasive....non-technical" is the key.



Michael Barnett C.H.I. #NACHI07081803, HIF#9725A
Barnett's Certified Home Inspections BL#10009708
(661) 816-4123
www.barnetts-inspections.com
mbarnett@ca.nachi.org
www.nachi.org
Reply With Quote
  #11  
Old 10/2/07, 7:17 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

I have been told the Aluminum wire used in Canada was a different type then was used In USA that could be the reason very little problems with it here .
Same as FP panels no big concern Different panels then in USA.
...... Cookie
Reply With Quote
  #12  
Old 10/2/07, 11:29 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Aluminum Wiring

Quote:
The system includes SINGLE STRAND ALUMINUM WIRE that has long been suspect. Aluminum wire does not conduct current as efficiently as copper wire and, inasmuch as it oxidizes, it can become an insulator instead of a conductor. Also it has a tendency to expand and contract more, and thereby become loose at any one of the multiple connections, at switches and outlets, and elsewhere, and create a fire-hazard. Therefore, you should seek the counsel of a electrician who is familiar with this issue, and with the recommended procedures for correcting the known deficiencies, such as Copalum crimping.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail

Last edited by bkelly2; 6/12/09 at 7:47 PM..
Reply With Quote
  #13  
Old 10/2/07, 11:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Bear in mind CPSC is a political organization, U/L is a nationally recognized testing lab. U/L does list a couple other ways to deal with aluminum, not insignificantly the CO/ALr device. As much as CPSC and Inspect-NY hate them the Ideal 65 wirenut is also listed. The NEC only refers to nationally recognized testing labs, CPSC is NOT on that list.
You can pump up the Copalum device and the electricians will love you for it but don't be confused about the code compliance issues and don't be shocked if a lawyer notices too.
Reply With Quote
  #14  
Old 10/3/07, 12:00 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Aluminum Wiring

Quote:
Originally Posted by Greg Fretwell
....You can pump up the Copalum device and the electricians will love you for it but don't be confused about the code compliance issues and don't be shocked if a lawyer notices too.
Quote:
Originally Posted by Greg Fretwell
...the Ideal 65 wirenut is also listed.
What is the Ideal 65? Have a link?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #15  
Old 10/3/07, 12:03 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Aluminum Wiring

Quote:
Originally Posted by Greg Fretwell
Bear in mind CPSC is a political organization, U/L is a nationally recognized testing lab. U/L does list a couple other ways to deal with aluminum, not insignificantly the CO/ALr device. As much as CPSC and Inspect-NY hate them the Ideal 65 wirenut is also listed. The NEC only refers to nationally recognized testing labs, CPSC is NOT on that list.
You can pump up the Copalum device and the electricians will love you for it but don't be confused about the code compliance issues and don't be shocked if a lawyer notices too.

Therefore, you should seek the counsel of a electrician who is familiar with this issue
, and with the recommended procedures for correcting the known deficiencies, such as Copalum crimping



http://www.inspect-ny.com/aluminum/ideal65.htm


Most Electricians here (and Realtors) say things like, "well there have been no problems yet". But they will not write the, no problems yet BS down, I womder why?


http://www.mnpropertyinspection.com/...inumWiring.pdf



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail

Last edited by bkelly2; 10/3/07 at 12:15 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring acox Electrical 4 8/27/07 12:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Reporting Aluminum Wiring Richard Seay Electrical 3 2/28/07 5:27 PM
Aluminum Wiring homeowner001 Electrical 36 7/7/06 2:08 AM
Aluminum wiring rray Electrical 11 6/17/06 12:41 PM


All times are GMT -4. The time now is 3:17 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts