Default aluminum wiring

Observed aluminum wiring in a sub panel of a 16 year old house today. This is the first time I have seen solid strand in a newer house like this and I recommended review of connections and application of anti oxidant paste to terminals by a qualified electrician familiar with aluminum wiring. Looking for advice before I send report out.

John
Attached Thumbnails
aluminum-wiring-hip-046.jpg  
Reply With Quote
  #2  
Old 4/8/08, 7:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: aluminum wiring

Quote:
Originally Posted by jjones2
Observed aluminum wiring in a sub panel of a 16 year old house today. This is the first time I have seen solid strand in a newer house like this and I recommended review of connections and application of anti oxidant paste to terminals by a qualified electrician familiar with aluminum wiring. Looking for advice before I send report out.

John
John,

Aluminum branch wiring is a red flag. It needs to be deferred to a licensed Electrician.

http://www.masscertifiedhomeinspections.com/?D=97

UPGRADING ALUMINUM WIRING
Reply With Quote
  #3  
Old 4/8/08, 8:09 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

Quote:
Originally Posted by dvalley
Aluminum branch wiring is a red flag. It needs to be deferred to a licensed Electrician.
This depends on the size and application of the conductor.

True, #12 & #10 solid used for general use branch circuits is bad, but larger conductors are fine and still used today in many applications.
Reply With Quote
  #4  
Old 4/8/08, 10:50 AM
John G. Jones's Avatar
John G. Jones John G. Jones is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Muskegon, Mi
Posts: 88
Send a message via MSN to jjones2
Default Re: aluminum wiring

Quote:
Originally Posted by dvalley
John,

Aluminum branch wiring is a red flag. It needs to be deferred to a licensed Electrician.

http://www.masscertifiedhomeinspections.com/?D=97

UPGRADING ALUMINUM WIRING
Thanks David,

as you see from my post that is what I wrote up, but since I hadnt seen solid strand 10 awg in newer construction I wanted to make sure I am not aware of some type of alumicopptinium if you know what I mean. The sheathing stated some type of metal mixture that I have never seen before but dont recall what is was since I called it out for further review anyways.

John
Reply With Quote
  #5  
Old 4/8/08, 12:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

I see copper right below that. How much was aluminum? I am not even sure where you would get 10ga al 16 years ago and it should be the new alloy if it was bought new then. The insulation looks like TW so that might just be one circuit put in with antique wire
Reply With Quote
  #6  
Old 4/8/08, 3:08 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: aluminum wiring

If this is newer construction, that must be tinned copper.
Reply With Quote
  #7  
Old 4/8/08, 3:24 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

Quote:
Originally Posted by jjones2
I recommended review of connections and application of anti oxidant paste to terminals by a qualified electrician familiar with aluminum wiring. Looking for advice before I send report out.

John
Why would you recommend the use of this junk?
Reply With Quote
  #8  
Old 4/8/08, 4:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

David, I think tinned copper is an older technology than aluminum.
In 1993 it would be hard to find either one of these in a supply house and niether would be in a home store.
It sure looks like pre 1986 aluminum to me (TW insulation). That is why I asked how many circuits are wired with it. This coukld be a homeowner addition using something he had saved along with his leisure suit and platform shoes.
Reply With Quote
  #9  
Old 4/8/08, 4:33 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: aluminum wiring

Quote:
Originally Posted by Greg Fretwell
David, I think tinned copper is an older technology than aluminum.
In 1993 it would be hard to find either one of these in a supply house and niether would be in a home store.
It sure looks like pre 1986 aluminum to me (TW insulation). That is why I asked how many circuits are wired with it. This coukld be a homeowner addition using something he had saved along with his leisure suit and platform shoes.
That's what I thought, it does indeed look like aluminum wire to me. But the build date screwed me up.

It looks like my aluminum wiring here....

Reply With Quote
  #10  
Old 4/8/08, 10:57 PM
John G. Jones's Avatar
John G. Jones John G. Jones is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Muskegon, Mi
Posts: 88
Send a message via MSN to jjones2
Default Re: aluminum wiring

Quote:
Originally Posted by Mike Whitt
Why would you recommend the use of this junk?
Because that is what I was taught. Isnt it supposed to prevent contact with air which promotes oxidation, hence the ANTI oxidant paste. Do you have a reason to not recommend it? I am always open to learn , that is why I asked for opinions.

John
Reply With Quote
  #11  
Old 4/8/08, 11:11 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

That sure looks like the old NM with the TW insulation to me which makes it pre-1986. Either that house is 20 years older than they say or they used some antique wire when they built it.
That has always been a question, does old technology lose it's listing when newer technology comes along? Could you wire a new building with cloth covered wire and black painted conduit and boxes?

BTW were the devices CO/ALr? It should be stamped on the yoke where you can see it with the cover off.
Reply With Quote
  #12  
Old 4/9/08, 12:16 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

Quote:
Originally Posted by jjones2
Because that is what I was taught. Isnt it supposed to prevent contact with air which promotes oxidation, hence the ANTI oxidant paste. Do you have a reason to not recommend it? I am always open to learn , that is why I asked for opinions.

John
110.14 Electrical Connections.
Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.

The reason I posted the code section was to show what the code said about the use of antioxidants.
If it is used then it must be suitable for the use and the only people that can say what is and is not shall be suitable for the use are the manufacturers of the terminal and conductor.
Therefore if the terminal or the conductor manufacturer does not include something requiring the use of an antioxidant there is no need for its use.

The only time I use the junk is when it is required be the manufacturer of the terminal and these are far and few between.

When an antioxidant is used there are several steps that must be followed in order for it to function properly. It is not as simple as squirting a little in the hole and then installing the conductor as most do when using the junk.

First the conductor must be cleaned with a wire brush. If it is a stranded conductor then the strands needs to be separated and each strand brushed and then reformed into its original shape. This bending and brushing of the strands often damages the strands and the end effect is worse than if no antioxidant was used.

On a side note; if I was worried about the conductor oxidizing and causing some sort of damage to anything then I would install a copper conductor.
Reply With Quote
  #13  
Old 4/9/08, 12:33 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

Quote:
Originally Posted by jjones2
Observed aluminum wiring in a sub panel of a 16 year old house today. This is the first time I have seen solid strand in a newer house like this and I recommended review of connections and application of anti oxidant paste to terminals by a qualified electrician familiar with aluminum wiring. Looking for advice before I send report out.

John
John:

Did you, or can you take a real close up picture of the information that is pasted on the cabinet, or on the inside cover? That information contains the instructions, and if the "Conductor Termination Compounds" is required, that will be the reason for recommending that it be used.



UL INFORMATION FOR CONDUCTOR TERMINATION COMPOUNDS (DVYW)

Conductor termination compounds are for use on splice and termination connections of aluminum, copper-clad aluminum and copper conductors where used to retard oxidation at the conductor/connector interface. These compounds do not have a deleterious effect on the conductor metal, insulation or equipment when used in accordance with the manufacturer’s installation instructions. I also see the use of a white wire on the lower breaker, and that the wires you describe show signs of being "knicked"


Reply With Quote
  #14  
Old 4/9/08, 2:53 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: aluminum wiring

I really hate getting in the "goo" fights because I really don't have an opinion and I do use it (just to keep other inspectors happy) but I agree with Mike. It is not required and you are never really sure you have cleaned the wire enough to actually acccomplish anything.

When you read the lug manufacturer's instructions they "recomend" using the goo, wire brushing the wire etc but it is not a requirement. Alcan (wire manufacturer) says it is not necessary and in their tests it had no effect if the lug is properly torqued (gas tight). The oxide layer is destroyed in the torquing process.
They are also the ones who point out an aluminum conductor in an aluminum lug (which most are) is a better chemical match than copper (but they don't sell copper ).
As an inspector I would never fail a job because of a lack of goo.
Reply With Quote
  #15  
Old 4/9/08, 7:18 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: aluminum wiring

Quote:
Originally Posted by Greg Fretwell
I really hate getting in the "goo" fights because I really don't have an opinion and I do use it (just to keep other inspectors happy) but I agree with Mike. It is not required and you are never really sure you have cleaned the wire enough to actually acccomplish anything.

When you read the lug manufacturer's instructions they "recomend" using the goo, wire brushing the wire etc but it is not a requirement. Alcan (wire manufacturer) says it is not necessary and in their tests it had no effect if the lug is properly torqued (gas tight). The oxide layer is destroyed in the torquing process.
They are also the ones who point out an aluminum conductor in an aluminum lug (which most are) is a better chemical match than copper (but they don't sell copper ).
As an inspector I would never fail a job because of a lack of goo.
Hmmmmm, very interesting Gentlemen.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring jhagarty Electrical 23 10/5/07 3:56 AM
Aluminum Wiring acox Electrical 4 8/27/07 12:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Aluminum Wiring homeowner001 Electrical 36 7/7/06 2:08 AM


All times are GMT -4. The time now is 3:23 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts