Default Aluminum Wiring?

Had this today. All branch wiring copper except for AC condenser and Oven. Both appeared to have AL strand (picture shows 40A breaker for oven). First time I've seen this. Any concerns? Thx.
Attached Thumbnails
aluminum-wiring-wire.jpg  



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 4/8/09, 4:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Aluminum Wiring?

Multi-strand AL wiring does not have the same problems associated with solid AL conductors. No issues to be concerned about. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 4/8/09, 4:41 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Aluminum Wiring?

Quote:
Originally Posted by jpope View Post
Multi-strand AL wiring does not have the same problems associated with solid AL conductors. No issues to be concerned about. . .
I kneel to the Pope

Thanks Jeff!



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 4/8/09, 10:17 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Aluminum Wiring?

The AL conductor appears to be 8 gauge protected by a 40 Amps breakers, shouldn't it be 6 gauge?



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 4/8/09, 10:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Aluminum Wiring?

Quote:
Originally Posted by mgratton View Post
The AL conductor appears to be 8 gauge protected by a 40 Amps breakers, shouldn't it be 6 gauge?
Condenser circuits are generally wired that way. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 4/8/09, 11:09 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Aluminum Wiring?

I assume you also observed/wrote up the doubled neutral connections.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 4/9/09, 6:30 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Aluminum Wiring?


Last edited by bkelly2; 6/12/09 at 6:48 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM
Aluminum Wiring acox Electrical Inspections 4 8/26/07 11:24 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Aluminum Wiring homeowner001 Electrical Inspections 36 7/7/06 1:08 AM


All times are GMT -4. The time now is 5:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts