Hello,

I am not a home inspector but a concerned client from a recent home inspection I had performed last week.

While examining the breaker box my inspector found what he claimed to be aluminum wiring coming out of several circuits. His verbal words to me were “this is aluminum wiring”.

His report was very ambiguous with a large amount of second opinions especially the aluminum wring concern.

My question to all home inspectors reading this post- Through your training and certification, are you required to positively identify aluminum wiring without a second opinion from a licensed electrician?

Thank you for your time.
Reply With Quote
  #2  
Old 6/22/06, 9:43 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Quote:
Originally Posted by homeowner001
Through your training and certification, are you required to positively identify aluminum wiring without a second opinion from a licensed electrician?
The NACHI standards of practice indicate so.
Quote:

2.7. Electrical
I. The inspector shall inspect:
I. And report the presence of solid conductor aluminum branch circuit wiring if readily visible.


Also note that there is also an older copper wire with a tin coating that may appear to be aluminum if you don't look closely or don't know what to look for. However I find far more actual aluminum wire than the tin cladded copper.

You are the seller?
Reply With Quote
  #3  
Old 6/22/06, 2:30 PM
homeowner001 homeowner001 is offline
New User
 
Join Date: Jun 2006
Posts: 4
Please Note: homeowner001 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

I am the buyer. My inspector told me verbally that you have aluminum wiring. In his report, it stated "what appears to be aluminum wiring".

That is why I asked, as a certified home inspector through NACHI are you required to positivly identify alumimum wire?

Thanks.
Reply With Quote
  #4  
Old 6/22/06, 4:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Aluminum Wiring

If readily visible, yes.

It's actually fairly easy to identify it's presence if the service equipment is fully accessible.

In any event, once identified, it's up to the client to follow up with appropriate evaluation and/or repairs.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 6/22/06, 8:01 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

It sounds like you feel there is a discrepencay between the verbal "it is" and the written "it appears to be". Like I said there is a much less common wiring that on the surface may appear to be aluminium. It is an older wire than the aluminum.

If you phone your inspector I'm sure he will clarify his statements for you.
Reply With Quote
  #6  
Old 6/23/06, 5:17 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Aluminum Wiring

Technically, one could not actually identify aluminum wiring as aluminum without removing it and running it through some identifying laboratory tests. However, based on experience, as well as other circumstances, like the build date of the structure, most home inspectors can "identify" aluminum wiring. But here in my state, I'm not going to "positively identify" aluminum wiring, preferring to let the licensed electrician do that since he is licensed and California has no licensing for home inspectors, even though our jobs require that we know electricity.

So, to answer your question,

Quote:
Originally Posted by homeowner001
My question to all home inspectors reading this post- Through your training and certification, are you required to positively identify aluminum wiring without a second opinion from a licensed electrician?
No.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 6/23/06, 7:32 AM
homeowner001 homeowner001 is offline
New User
 
Join Date: Jun 2006
Posts: 4
Please Note: homeowner001 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Thanks for all your responses. You have been more than helpful. I had a licensed electrician come to the house and positively identify the wires. Turns out they are all copper.

Thanks.
Reply With Quote
  #8  
Old 6/23/06, 9:06 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Aluminum Wiring

Quote:
Originally Posted by homeowner001
Thanks for all your responses. You have been more than helpful. I had a licensed electrician come to the house and positively identify the wires. Turns out they are all copper.

Thanks.
Ya...Tin coated copper.

This is aluminum wiring...(with melted insulation)

Last edited by dvalley; 10/7/07 at 4:42 PM..
Reply With Quote
  #9  
Old 6/23/06, 10:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Aluminum Wiring

Quote:
Originally Posted by rray
Technically, one could not actually identify aluminum wiring as aluminum without removing it and running it through some identifying laboratory tests.
I don't need a laboratory to tell me that my soda can is made of aluminum. AL conductors are easy to identify (positively) if they are visible.

In this case, it sounds like the conductors were tinned copper (as David said).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 6/23/06, 11:39 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

A couple clues. When was the house built? Al was used in the late 60s and early 70s. Aluminum will be a PVC jacketed cable, not the silvery paper/cloth type jacket. The only color I have seen is white but it might be other colors. It will be one size larger than you would expect for the breaker size. (12ga on a 15, 10ga on a 20). The insulation will be TW, a thick solid plastic, not cloth reinforced rubber or the smaller 2 layer THHN you see in NM-b.
The slam dunk is if you can see the cable jacket and see "AL" or "aluminum" next to the conductor size ... but you know that.
Reply With Quote
  #11  
Old 6/24/06, 12:44 AM
Joey D'Adamo Joey D'Adamo is offline
New User
 
Join Date: Aug 2004
Posts: 38
Please Note: Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Up here in Canada there does exist some aluminum wire I've seen personally with the paper/cloth style jacket. I've only ever seen it covered green, although the conductors inside are definately plastic insulated. I think its circa 1965-ish. I can't imagine why this stuff wouldn't also exist in the US. It does, however, very clearly say AL on the jacket.

Aside from that most is that ALCAN stuff which is plastic all the way. Not sure about the states, but here the "good" aluminum stuff from 72-76 has "ACM" stamped on the jacket along with "AL."

ODDLY ENOUGH... I've seen ALCAN COPPER wire in a 1978 townhouse. Weird eh? Funny since Alcan is an aluminum company.

Anyways I'm just rambling now...
Reply With Quote
  #12  
Old 6/24/06, 1:29 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Aluminum Wiring

Here are some pics of tinned copper wire, which may "appear to be" aluminum wiring unless you can see all the cut ends (sometimes very difficult to see) or there are other indications to the contrary like markings. Even if you can see the cut ends of some wires, it's possible to have a mix of different wire types where some are tinned copper and some are aluminum unless all the cables look the same.

Sounds like your inspector called it right that he suspected aluminum wiring (can be a real safety/fire hazard), and to have an electrician disconnect some wires for each type of cable and look at the ends to positively identify them (which is beyond a home inspection, as home inspectors should ABSOLUTELY NOT disturb suspected aluminum wiring).

Older aluminum wiring can be a very serious life safety hazard where you are much better off being safe rather than being sorry ... http://www.inspect-ny.com/aluminum/aluminum.htm

JMO & 2-nickels ...
Attached Thumbnails
aluminum-wiring-tinnedcopperwire1.jpg   aluminum-wiring-tinnedcopperwire2.jpg   aluminum-wiring-tinnedcopperwire3.jpg   aluminum-wiring-tinnedcopperwire4.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/24/06 at 1:36 PM..
Reply With Quote
  #13  
Old 6/24/06, 9:16 PM
homeowner001 homeowner001 is offline
New User
 
Join Date: Jun 2006
Posts: 4
Please Note: homeowner001 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Thanks again for all your comments!
Reply With Quote
  #14  
Old 6/24/06, 9:59 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Aluminum Wiring

Quote:
While examining the breaker box my inspector found what he claimed to be aluminum wiring coming out of several circuits. His verbal words to me were “this is aluminum wiring”.

His report was very ambiguous with a large amount of second opinions especially the aluminum wring concern
.



Quote:
A word, phrase, sentence, or other communication is called ambiguous if it can be interpreted in more than one way.

Sorry to hear about your misfortune.

Sounds like you probably had "Recommend further evaluation by licensed contractor" in your report several times........
Reply With Quote
  #15  
Old 6/25/06, 4:10 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Aluminum Wiring

Quote:
Originally Posted by dduffy
.Sounds like you probably had "Recommend further evaluation by licensed contractor" in your report several times........
If that had been true, seems like the licensed contractors should have their licenses revoked.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM
Aluminum Wiring acox Electrical Inspections 4 8/26/07 11:24 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Reporting Aluminum Wiring Richard Seay Electrical Inspections 3 2/28/07 4:27 PM
Aluminum wiring rray Electrical Inspections 11 6/17/06 11:41 AM


All times are GMT -4. The time now is 2:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts