In the attached pics it appears the there is aluminum wire leading to the 220 circuits. I was surprised to see this since the house was built in 1984. What recommendations would you suggest?
Attached Thumbnails
aluminum-wiring-100_4570.jpg   aluminum-wiring-100_4573.jpg   aluminum-wiring-100_4574.jpg  
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/7/11, 5:23 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Aluminum Wiring

Aluminum wire for the 220 circuits are fine....
It is the Panel that is BAD
Federal Pacific Stab-Lok



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 4/7/11, 5:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Aluminum Wiring

Quote:
Originally Posted by jhagarty View Post
Aluminum wire for the 220 circuits are fine....
It is the Panel that is BAD
Federal Pacific Stab-Lok
Yes, "stranded" AL conductors are okey-dokey!
Reply With Quote
  #4  
Old 4/7/11, 9:43 PM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Aluminum Wiring

Thanks for the responces, but why do insurance companies frown on aluminum wiring in the house?

Last edited by gstrump; 4/8/11 at 10:28 AM..
Reply With Quote
  #5  
Old 4/7/11, 9:58 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Aluminum Wiring

Quote:
Originally Posted by gstrump View Post
Thanks for the responces, but wire do insurance companies frown on aluminum wiring in the house?
Only solid aluminum, and then only certain companies, and under certain circumstances.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 4/7/11, 10:20 PM
Brad Brinke Brad Brinke is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Hampton Roads, VA
Posts: 189
Default Re: Aluminum Wiring

Greg, please don't take this the wrong way, but where did you train for this profession?



Inspecting Norfolk and Hampton Roads
www.procraftinspections.com

Energy Audits in Norfolk

www.procraftgreen.com
Reply With Quote
  #7  
Old 4/7/11, 10:20 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Aluminum Wiring

Rule of thumb... (there's always exceptions)...

Solid AL = Bad
Stranded AL = Okay
Reply With Quote
  #8  
Old 4/7/11, 10:44 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Aluminum Wiring

In Illinois we are required to:

"Report on the presence of solid conductor aluminum branch circuit wiring"



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 4/7/11, 11:01 PM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: Aluminum Wiring

FPE stab-lok panel, known to have problems.
Conduit through concentric knock out, no connector, improper install.
Garbage in bottom of panel.
Reply With Quote
  #10  
Old 4/8/11, 4:50 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

I agree with the others, this panel has issues but the stranded Al isn't one of them. Personally I would change out any FPE panel immediately.
Reply With Quote
  #11  
Old 4/8/11, 7:33 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Aluminum Wiring

Quote:
Originally Posted by gstrump View Post
Thanks for the responces, but wire do insurance companies frown on aluminum wiring in the house?
Fire potential, they mitigate liability by not insuring until upgrades or rewire are completed, once issues are identified. Odds in their favor of fewer loss payouts and more profit in their pocket.

This article may provide a better understanding...

Regardless of where or how much training/experience one has, we all can and should continue to learn and assist whenever possible.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #12  
Old 4/8/11, 8:02 AM
Jeff Zehnder Jeff Zehnder is offline
New User
 
Join Date: Sep 2008
Location: Cary, NC
Posts: 7
Please Note: Jeff Zehnder is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

The following is what the insurance industry states to place in all commercial clients insurance inspection results that have aluminum wire of suspect panels...


Federal Pacific brand panel- You have a Federal Pacific electrical panel or panels installed in your building. It has been found that some of these panels have failed to provide proper protection, as they may have a tendency to overheat and cause a fire. To reduce this exposure it is recommended that a qualified electrical contractor replace Federal Pacific brand panels with another brand that has a current UL listing and which provides improved protection and reliability.

(or)

Zinsco Electrical brand panel- You have Zinsco electrical panels in your building. Many Zinsco panels contain a design flaw which can cause arcing and subsequent overheating. Long term exposure to this heat can cause the breaker to fuse to the bus bar, making it impossible to remove. Even worse, it can cause the breaker's contacts to fuse together, thus preventing the breaker from tripping even in an over current situation, thereby causing a potential fire hazard. To reduce this exposure a qualified electrical contractor should replace Zinsco brand panels with another brand that has a current UL listing and which provides improved protection and reliability.

As far as aluminum branch circuit wiring they ask that it be noted in any insurance reporting and since that panel would have to be more than 30 years old they require replacement.

Jeff Zehnder
Cary, NC
Reply With Quote
  #13  
Old 4/8/11, 10:43 AM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Aluminum Wiring

Does that hold true for residental as well?
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/8/11, 10:47 AM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Aluminum Wiring

Great article thanks Barry!
Reply With Quote
  #15  
Old 4/8/11, 4:01 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum Wiring

Quote:
Originally Posted by Jeff Zehnder View Post
The following is what the insurance industry states to place in all commercial clients insurance inspection results that have aluminum wire of suspect panels...


Federal Pacific brand panel- You have a Federal Pacific electrical panel or panels installed in your building. It has been found that some of these panels have failed to provide proper protection, as they may have a tendency to overheat and cause a fire. To reduce this exposure it is recommended that a qualified electrical contractor replace Federal Pacific brand panels with another brand that has a current UL listing and which provides improved protection and reliability.

(or)

Zinsco Electrical brand panel- You have Zinsco electrical panels in your building. Many Zinsco panels contain a design flaw which can cause arcing and subsequent overheating. Long term exposure to this heat can cause the breaker to fuse to the bus bar, making it impossible to remove. Even worse, it can cause the breaker's contacts to fuse together, thus preventing the breaker from tripping even in an over current situation, thereby causing a potential fire hazard. To reduce this exposure a qualified electrical contractor should replace Zinsco brand panels with another brand that has a current UL listing and which provides improved protection and reliability.

As far as aluminum branch circuit wiring they ask that it be noted in any insurance reporting and since that panel would have to be more than 30 years old they require replacement.

Jeff Zehnder
Cary, NC
Are you saying that by default all aluminum branch circuit wiring is more than 30 years old?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Branch Wiring update jshishilla Florida Inspectors 6 3/16/11 11:11 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM


All times are GMT -4. The time now is 5:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts