hello everyone
My question is can a Aluminum main service wire coming into the main service panel be spliced to copper so it can reach the lugs. I inspected a house this week that had this in the main service box. Thanks Mark House 2 Home LLC 503-602-1420 HomePros@House2HomeLLC.ORG Protecting Peace of Mind One House at a Time |
| Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Do a search on the forum, there is very good information to start. You can also post a photo(s) and some members will take the time to comment.
Tom |
|
#3
|
|||
|
|||
|
You need a special lug that is for that application. Some of these lugs even require a special paste to prevent corrosion.
|
|