Default Aluminum wiring to copper

hello everyone
My question is can a Aluminum main service wire coming into the main service panel be spliced to copper so it can reach the lugs. I inspected a house this week that had this in the main service box.
Thanks Mark



House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #2  
Old 10/24/09, 12:54 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Aluminum wiring to copper

Do a search on the forum, there is very good information to start. You can also post a photo(s) and some members will take the time to comment.

Tom
Reply With Quote
  #3  
Old 10/24/09, 2:29 PM
James E. Braun, CMI James E. Braun, CMI is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 2,786
Default Re: Aluminum wiring to copper

You need a special lug that is for that application. Some of these lugs even require a special paste to prevent corrosion.
Reply With Quote
  #4  
Old 10/24/09, 8:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Aluminum wiring to copper

http://www.nachi.org/forum/f19/pigtailing-sec-44394/



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 10/24/09, 11:24 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 215
Default Re: Aluminum wiring to copper

Quote:
Originally Posted by jpope View Post
thanks jeff that was perfect. The application was not correct but i was not sure if you can pigtail on the main service lines at all from alum to copper.



House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring jhagarty Electrical 23 10/5/07 3:56 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM


All times are GMT -4. The time now is 2:52 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts