Default Aluminum Wiring: Please proof this new inspection article.

http://www.nachi.org/aluminum-wiring.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 12/4/09, 7:01 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Aluminum Wiring: Please proof this new inspection article.

Under your "Options for Corrections" you had better make a reference to the appropriate electrical code for the area where the correction is being made for not all of your solutions are universally acceptable.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 12/5/09, 7:12 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Aluminum Wiring: Please proof this new inspection article.

Hi Nick, here's my thoughts (in red)

Quote:
Aluminum Wiring

By Nick Gromicko, Rob London and Kenton Shepard


Between approximately 1965 and 1973, Single strand aluminum wiring was sometimes substituted for copper branch-circuit wiring in residential 15 and 20 amp electrical systems due to the sudden escalating price of copper. After a decade of use by homeowners and electricians, inherent weaknesses were discovered in the metal that lead to its disuse as a branch wiring material. Although properly maintained aluminum wiring is acceptable????, aluminum will generally become defective faster than copper due to certain qualities inherent in the metal. Neglected connections in outlets, switches and light fixtures containing aluminum wiring become increasingly dangerous over time. Poor connections cause wiring to overheat, creating a potential fire hazard. In addition, the presence of aluminum single strand wiring may void a home’s insurance policies. Inspectors may instruct their clients to talk with their insurance agents about whether the presence of aluminum wiring in their home is a problem that requires changes to their policy language.

Aluminum as a Metal


Aluminum possesses certain qualities that, compared with copper, make it an undesirable material as an electrical conductor. These qualities all lead to loose connections, where fire hazards become likely. These qualities are as follows:
  • higher electrical resistance. Aluminum has a higher resistance to electrical current flow, which means that, given the same amperage, aluminum conductors must be of a larger diameter than would be required by copper conductors.
  • less ductile. Aluminum will fatigue and break down more readily when subjected to bending and other forms of abuse than copper, which is more ductile. Fatigue will cause the wire to break down internally and will increasingly resist electrical current, leading to a buildup of excessive heat.
  • galvanic corrosion. In the presence of moisture, aluminum will undergo galvanic corrosion when it comes into contact with certain dissimilar metals.
  • oxidation. Exposure to oxygen in the air causes deterioration to the outer surface of wire. This process is called oxidation. Aluminum wire is more easily oxidized than copper wire, and the compound formed by this process – aluminum oxide – is less conductive than copper oxide. As time passes, oxidation can deteriorate connections and present a fire hazard.
  • greater malleability. Aluminum is soft and malleable, meaning it is highly sensitive to compression. After a screw has been over-tightened on aluminum wiring, for instance, the wire will continue to deform or “flow” even after the tightening has ceased. This deformation will create a loose connection and increase electrical resistance in that location.
  • greater thermal expansion and contraction. Even more than copper, aluminum expands and contracts with changes in temperature. Over time, this process will cause connections between the wire and the device to degrade. For this reason, aluminum wires should never be inserted into the “stab,” “bayonet” or “push-in” type terminations found on the back of many light switches and outlets.
  • excessive vibration. Electrical current vibrates as it passes through wiring. This vibration is more extreme in aluminum than it is in copper, and, as time passes, it can cause connections to loosen.
Identifying Aluminum Wiring
  • Aluminum wires are the color of aluminum and are easily discernable from copper and other metals.
  • Since the early 1970s, wiring-device binding terminals for use with aluminum wire have been marked CO/ALR, which stands for “copper/aluminum revised."
  • Look for the word "aluminum" (or the letters AL) on the plastic wire jacket. Where wiring is visible, such as in the attic or electrical panel, inspectors can look for printed or embossed letters on the plastic wire jacket. Aluminum wire may have the word "aluminum," or a specific brand name, such as "Kaiser Aluminum," marked on the wire jacket. Where labels are hard to read, a light can be shined along the length of the wire.
  • When was the house built? Homes built or expanded between 1965 and 1973 are more likely to have aluminum wiring than houses built before or after those years.
Options for Correction

Aluminum wiring should be evaluated by a qualified electrician who is experienced in evaluating and correcting aluminum wiring problems. Not all licensed electricians are properly trained to deal with defective aluminum wiring. The following corrective actions may be taken:
  • Rewire the home with copper wire. While this is the most effective method, rewiring is expensive and impractical, in most cases.
  • Splice the aluminum wire to copper wire at the connections using approved wire nuts (called "pigtailing") (I believe this is wrong the only listed method I know of is "Copalum" crimps). This method is only effective if the connections between the aluminum wires and the copper pigtails are extremely reliable. Pigtailing with some types of connectors, even though they might be presently listed by Underwriters Laboratories for the application, can lead to increasing the hazard. Also, beware that pigtailing will increase the number of connections, all of which must be maintained.
  • Replace certain failure-prone types of devices and connections with others that are more compatible with aluminum wire.
  • Remove the ignitable materials from the vicinity of the connections (Not practial).
  • All connections should be checked and an anti-oxidant paste applied (not correct).
  • Copalum crimps can be installed. Although effective, they are expensive (typically around $50 per outlet, switch or light fixture).
In summary, aluminum wiring can be a fire hazard due to inherent qualities of the metal. Inspectors should be capable of identifying this type of wiring.
Nick you need to stress this only affects single strand aluminum conductors not multi-stranded

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 12/5/09, 7:27 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Aluminum Wiring: Please proof this new inspection article.

Quote:
Between approximately 1965 and 1973, Single strand aluminum wiring was sometimes substituted for copper branch-circuit wiring in residential 15 and 20 amp
I would not add any AMP numbers to the article myself. I often see single strand AL wiring in larger sizes serving AC units/water heaters/ etc.

I also believe there are more repair connectors available today.


http://www.alcopstore.com/index.asp?...ATS&Category=2
Reply With Quote
  #5  
Old 12/5/09, 8:14 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Aluminum Wiring: Please proof this new inspection article.

Have AFCI's become an accepted method of adding protection?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 12/6/09, 6:50 PM
Allen L. Catterton's Avatar
Allen L. Catterton Allen L. Catterton is offline
InterNACHI Member
 
Join Date: May 2004
Location: Cantonment, FL
Posts: 198
Default Re: Aluminum Wiring: Please proof this new inspection article.

More and more I am seeing that the major insurers, especially here in Florida, will refuse to write a homeowner’s policy on a home with aluminum branch circuit cabling. The polices can usually be written on the secondary market but owner/ buyer should be informed that anything other than total replacement of the cabling is generally considered a “quick fix” and will still lead to high and sometimes exorbitant insurance rates. Would you want to include a paragraph in your article regarding insurability?
Reply With Quote
  #7  
Old 12/7/09, 7:28 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: Aluminum Wiring: Please proof this new inspection article.

I don't know of any insurance companies in Florida that will keep a policy in force once they found out the home has aluminum branch circuits. Most of the electricians I know won't use the crimps. They also will deny a claim if it is a fire and the home has aluminum branch circuits. They say that makes the problem worse then it originally was.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida

Last edited by gbell; 12/7/09 at 5:20 PM..
Reply With Quote
  #8  
Old 12/7/09, 1:08 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Aluminum Wiring: Please proof this new inspection article.

Quote:
I don't know of any insurance companies that will keep a policy in force once they found out the home has aluminum branch circuits.
Greg,

There are tens of thousands of insurance policies in effect. Yes, this is with single-strand aluminum wiring.

Maybe things are different in Florida...
Reply With Quote
  #9  
Old 12/7/09, 2:42 PM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 237
Default Re: Aluminum Wiring: Please proof this new inspection article.

Thank you Gerry, I made most of those corrections. The article has been updated with some information I got from a company that specializes in aluminum wire repair, as well as the CPSC. I'll try to find the answers to the other issues. I sent the article off to a specialist to look at, we'll see what he has to say.



Researcher and Technical Writer, InterNACHI

Last edited by rlondon; 12/7/09 at 4:23 PM..
Reply With Quote
  #10  
Old 12/7/09, 2:58 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Aluminum Wiring: Please proof this new inspection article.

Thank you Nick, I add live links to articles in my HI reports, which benefit my Client with greater knowledge than I can give them in a short time, and make me look good. Keep up the good work. A request, Looking for a good GFCI article.
Reply With Quote
  #11  
Old 12/7/09, 4:25 PM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 237
Default Re: Aluminum Wiring: Please proof this new inspection article.

Quote:
Originally Posted by mroberson View Post
Thank you Nick, I add live links to articles in my HI reports, which benefit my Client with greater knowledge than I can give them in a short time, and make me look good. Keep up the good work. A request
Glad you like them

Quote:
Originally Posted by mroberson View Post
Looking for a good GFCI article.
Putting it on the list



Researcher and Technical Writer, InterNACHI
Reply With Quote
  #12  
Old 12/7/09, 4:32 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Aluminum Wiring: Please proof this new inspection article.

Thanks NACHI. Looking for a good Ghosting article too!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Knob and Tube Wiring: Please proof this new inspection article. gromicko Electrical Inspections 5 7/21/09 8:19 AM
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 5:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts