Question Aluminum wiring poll

When upon discovering aluminum wiring in the electric panel. How many of you go as far as pulling a few electrical outlets and checking for signs of arcing? Or do you just make the note of your observation and recommend and evaluation by a licensed electrician?

I personally am not an electrician and do not pull outlets in fear of disturbing the connections that may already be loose. How about you?







John Buckley
20/20 Home Inspection of NJ
1-888-798-5190
JOHN@THE2020HOMEINSPECTOR.COM
WWW.THE2020HOMEINSPECTOR.COM
WWW.NJMOLDTEST.COM

Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/8/11, 2:42 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Aluminum wiring poll

I do not pull outlets.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #3  
Old 4/8/11, 2:59 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Aluminum wiring poll

I a retired Sparky do not open outlets.
I report what I visually see .
I do a visual inspection as per My SOP....



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 4/8/11, 3:20 PM
Ken Ruppert Ken Ruppert is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Merritt Island, FL
Posts: 79
Default Re: Aluminum wiring poll

Like the rest of the guy's that answered, I do not pull the cover's off and just report what I see.




Ken Ruppert
NACHI # 08081129
Florida Lic # HI162

www.happyhomeinspection.com
Reply With Quote
  #5  
Old 4/9/11, 5:43 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Aluminum wiring poll

It doesn't really matter if you see aluminum, copper, or whatever type of wire in the panel, you should not be opening any receptacles, switches, or any fixtures for that matter. The is getting to technically exhaustive and could open a can of worms you don't want to be opened.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #6  
Old 4/9/11, 8:07 PM
JOHN BUCKLEY's Avatar
JOHN BUCKLEY JOHN BUCKLEY is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Manasquan, NJ
Posts: 30
Default Re: Aluminum wiring poll

The reason I started this poll was because I was scalded by a sellers agent over reporting aluminum wiring without checking if that outlets were properly pigtailed. she mentioned that her inspectors remove outlets during all of her inspections. I know she was trying to get my dander up over rocking her boat, but hey I did my job. I wanted to get a feel if anyone else was pulling outlets. Thanks for your input.



John Buckley
20/20 Home Inspection of NJ
1-888-798-5190
JOHN@THE2020HOMEINSPECTOR.COM
WWW.THE2020HOMEINSPECTOR.COM
WWW.NJMOLDTEST.COM

Reply With Quote
  #7  
Old 4/9/11, 8:12 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum wiring poll

Quote:
Originally Posted by jbuckley View Post
The reason I started this poll was because I was scalded by a sellers agent over reporting aluminum wiring without checking if that outlets were properly pigtailed. she mentioned that her inspectors remove outlets during all of her inspections. I know she was trying to get my dander up over rocking her boat, but hey I did my job. I wanted to get a feel if anyone else was pulling outlets. Thanks for your input.

How did you report the aluminum wiring?

They do have a point about whether or not the devices were pigtailed even if it's outside of the scope of your inspection.
Reply With Quote
  #8  
Old 4/9/11, 8:14 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Aluminum wiring poll

Quote:
Originally Posted by Robert Meier View Post
How did you report the aluminum wiring?

They do have a point about whether or not the devices were pigtailed even if it's outside of the scope of your inspection.
Maybe so, but that's the electricians job to determine... You did your job. If the selling agents inspector pulls plugs, you've got to wonder what he's not doing... Frankly I wouldn't even believe her... She probably heard something on those lines from an electrician who was doing a followup inspection for her sometime.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 4/9/11, 8:20 PM
JOHN BUCKLEY's Avatar
JOHN BUCKLEY JOHN BUCKLEY is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Manasquan, NJ
Posts: 30
Default Re: Aluminum wiring poll

The observation went like this. Solid strand Alumnin wiring present in localized circuits throughout dwelling. Failures associated with Aluminum wiring have been known to be a possible fire hazard and should be evaluated by a licensed electrician. I think that was putting it lightly... how are you guys calling this out?



John Buckley
20/20 Home Inspection of NJ
1-888-798-5190
JOHN@THE2020HOMEINSPECTOR.COM
WWW.THE2020HOMEINSPECTOR.COM
WWW.NJMOLDTEST.COM

Reply With Quote
  #10  
Old 4/9/11, 8:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum wiring poll

Quote:
Originally Posted by jbuckley View Post
The observation went like this. Solid strand Alumnin wiring present in localized circuits throughout dwelling. Failures associated with Aluminum wiring have been known to be a possible fire hazard and should be evaluated by a licensed electrician. I think that was putting it lightly... how are you guys calling this out?
Sounds fine to me but I'm an electrician not an HI. I don't see how the Realtor can complain about what you wrote, you're simply doing your job. IMO solid aluminum conductors should be reported because as we all know they are a potential hazard.
Reply With Quote
  #11  
Old 4/9/11, 8:50 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Aluminum wiring poll

Here's what I put in my reports:

Solid aluminum (AL) conductors were noted at one or more branch circuits in the electrical panel. AL wire has a higher expansion and contraction rate (approx. 30%) than copper and over time may become loose at its connections causing overheating or arcing. As a result, only receptacles and outlets approved for use with AL should be used (CO/ALR). It is strongly recommended that a licensed Electrical Contractor review the AL branch circuit wires in the home for approved connections at the receptacles and switches. Any necessary corrections or repairs should be made in accordance with current electrical standards.


I am interested to hear comments.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #12  
Old 4/9/11, 9:57 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Aluminum wiring poll

Quote:
Originally Posted by bsmith View Post
Here's what I put in my reports:

Solid aluminum (AL) conductors were noted at one or more branch circuits in the electrical panel. AL wire has a higher expansion and contraction rate (approx. 30%) than copper and over time may become loose at its connections causing overheating or arcing. As a result, only receptacles and outlets approved for use with AL should be used (CO/ALR). It is strongly recommended that a licensed Electrical Contractor review the AL branch circuit wires in the home for approved connections at the receptacles and switches. Any necessary corrections or repairs should be made in accordance with current electrical standards.

I am interested to hear comments.
Sounds great except for the "strongly recommend". It should just be Review from a licensed electrician is needed...

Why strongly? Are your other recommendations "softly"? If you take it out, it leaves not gray area. CALL a licensed electrician.

Just my 2 cents, the rest is written very well. Congrats



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #13  
Old 4/9/11, 10:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Aluminum wiring poll

Quote:
Originally Posted by bsmith View Post
Here's what I put in my reports:

Solid aluminum (AL) conductors were noted at one or more branch circuits in the electrical panel. AL wire has a higher expansion and contraction rate (approx. 30%) than copper and over time may become loose at its connections causing overheating or arcing. As a result, only receptacles and outlets approved for use with AL should be used (CO/ALR). It is strongly recommended that a licensed Electrical Contractor review the AL branch circuit wires in the home for approved connections at the receptacles and switches. Any necessary corrections or repairs should be made in accordance with current electrical standards.


I am interested to hear comments.
Sounds good. My one comment would be that saying receptacles and outlets is somewhat redundant since by definition a receptacle is an outlet. I would replace the word outlet with the word switches or remove all of the specific references and use the single word devices to describe receptacles, switches, circuit breakers etc.
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/10/11, 9:33 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Aluminum wiring poll

Robert ..
Thanks for your post's many have been helped by them .
Please keep helping . Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #15  
Old 4/10/11, 11:52 AM
Jeff Zehnder Jeff Zehnder is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Cary, NC
Posts: 11
Default Re: Aluminum wiring poll

North Carolinas recomended wording for reports follows:

Home Inspection Report & Summary Page – Recommended language for Aluminum Wiring.
Single strand aluminum wire is present on 120 volt branch circuits in this house. This single strand, branch circuit aluminum wire was used widely during the 1960s and 1970s. According to reports published by the U.S. Consumer Product Safety Commission (CPSC), problems due to overheating at the connections between the wire and devices such as switches, outlets, and light fixtures may have been responsible for house fires. It is recommended that the circuits using single strand aluminum wiring be evaluated and modified as may be deemed necessary by a licensed electrical contractor who is familiar with the problems inherent in this type of wiring. For more information on aluminum household wiring, refer to the National Electrical Code and the C.P.S.C. booklet "Repairing Aluminum Wiring." The toll-free hotline number for obtaining this booklet is 1-800-638-2772, or you can visit:
http://



J Jeff Zehnder
www.jjeffzehnder.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Branch Wiring update jshishilla Florida Inspectors 6 3/16/11 11:11 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
Aluminum Wiring jhagarty Electrical Inspections 23 10/5/07 2:56 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM


All times are GMT -4. The time now is 5:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts