Default Am I Missing Something

Need some help electrical is probably my weakest link. On today's inspection i opened up the service panel (main) and noticed that the neutrals and grounds were sharing the same buse bar no problem except they were all double lugged when there are plenty of open terminals to allow for single lugs.
Then as i began testing individual devices discovered that probably 8 out 10 outlets had open grounds. So i randomly started to open the boxes and discovered that the ground wire were run into the boxes and not connected to the devices. What am i missing?
Attached Thumbnails
am-missing-something-mckinley-100.jpg  



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/14/11, 2:47 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Am I Missing Something

The double lugging and the open grounds have nothing to do with each other... The open grounds are a defect, but easily corrected (attach the ground wire to the receptacle screw).

The double lugging (neutral & ground) sharing a common lug isn't great, but not that big of a deal.

Grounds can share lugs with other grounds, but neutrals cannot share lugs with other neutrals. When that happens it is a safety and fire issue. What you have is a relatively benign practice that technically isn't allowed but like I said isn't that big of a deal.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 2/14/11, 3:37 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 732
Default Re: Am I Missing Something

See that all the time here.



Greensboro Home Inspection
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspection.html

Raleigh Home Inspection
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

BassRumors.com
Providing a blog, news, and forum dedicated to bass fishing.
Reply With Quote
  #4  
Old 2/14/11, 3:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Am I Missing Something

The neutrals should not be sharing the same lug as the ground.

Although common practice in the past, it is a safety concern.
Reply With Quote
  #5  
Old 2/14/11, 5:02 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Am I Missing Something

Quote:
Originally Posted by bkelly2 View Post
The neutrals should not be sharing the same lug as the ground.

Although common practice in the past, it is a safety concern.
I agree and this was specifically addressed in the 2002 NEC under section 408.21. Although the requirement had been part of the UL Panelboard Standard for quite a while prior to the 2002 they included the wording in the actual code language to emphasize the requirement. It was later moved to section 408.41.

Quote:
408.41 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.
Reply With Quote
  #6  
Old 2/14/11, 6:40 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Am I Missing Something

Okay, granted having a ground and neutral under the same lug is not acceptable according to the NEC.

Beyond it not being "code compliant" shat is the potential harm in this? I've seen pictures of the harm of double lugging neutrals, but not a neutral and ground.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 2/14/11, 6:56 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Am I Missing Something

Quote:
Originally Posted by mnahrgang View Post
Okay, granted having a ground and neutral under the same lug is not acceptable according to the NEC.

Beyond it not being "code compliant" shat is the potential harm in this? I've seen pictures of the harm of double lugging neutrals, but not a neutral and ground.

Double-lugging/tapping can create hot spots on breakers and neutral terminal bars because they are not tightened to the correct torque—especially if two different sized conductors are used. Because the hot (black) and neutral (white) wires are both current carrying conductors the chance is even greater for potential hot spots. If the double-tap/lug becomes loose, it may begin to arc. This will build up carbon increasing resistance, which will make it more difficult for the conductor to make contact—thus increasing the current (electrical draw). The end result may be the current exceeding the rating of the breaker; it becomes hot and trips. There may be signs of over-heating such as discolored wires and terminal screws, melted wires, etc., or worse yet—the possibility of fire exists.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #8  
Old 2/14/11, 7:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Am I Missing Something

Quote:
This will build up carbon increasing resistance, which will make it more difficult for the conductor to make contact—thus increasing the current (electrical draw
Something wrong here but I have to run for a bit.

Increased resistance would lead to less current but voltage would be distributed across 2 loads resulting in insufficient voltage at the appliance.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 2/14/11, 8:20 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Am I Missing Something

Quote:
Originally Posted by mlarson View Post
Something wrong here but I have to run for a bit.

Increased resistance would lead to less current but voltage would be distributed across 2 loads resulting in insufficient voltage at the appliance.
When you return...

The electrical draw (amperage) is increased--more "push" is required to supply the demand. The "draw" may not appear at the appliance, but it is happening at point of the carbon build-up. That's why the breaker disconnects--increased heat generated by the increase in demand.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #10  
Old 2/14/11, 10:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Am I Missing Something

Quote:
Originally Posted by jwilliams4 View Post
When you return...

The electrical draw (amperage) is increased--more "push" is required to supply the demand. The "draw" may not appear at the appliance, but it is happening at point of the carbon build-up. That's why the breaker disconnects--increased heat generated by the increase in demand.
Depends Jae.

The push(voltage) is not variable in this case.

The poor connection causing arcing because instead of a near zero resistance you now have a few ohms and the current flowing through that resistance is creating heat. The current actually goes down in the circuit controlled by the breaker. I'm speaking of resistive loads here.

If there are inductive loads, like a motor, the current would go up as low voltage across the motor will produced increased currents.

So it depends if the load is resistive like lighting or a toaster or if it's inductive like a refrigerator.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 2/15/11, 7:57 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Am I Missing Something

Quote:
Originally Posted by mnahrgang View Post
Okay, granted having a ground and neutral under the same lug is not acceptable according to the NEC.

Beyond it not being "code compliant" shat is the potential harm in this? I've seen pictures of the harm of double lugging neutrals, but not a neutral and ground.
For one thing, if the conductors are not secured under the screw properly, you not only lose the neutral return path you also lose the safety ground should a fault occur. There could be no path back to the panel to clear the fault.
Reply With Quote
  #12  
Old 2/15/11, 8:51 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Am I Missing Something

Quote:
Originally Posted by Jim Port View Post
For one thing, if the conductors are not secured under the screw properly, you not only lose the neutral return path you also lose the safety ground should a fault occur. There could be no path back to the panel to clear the fault.
You have that same potential if they are under a screw all by themselves if the screw is loose. I would think that if the lug was rated for more than one connection, then it wouldn't matter.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #13  
Old 2/15/11, 1:14 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Am I Missing Something

The reason many inspectors assume the current went up with a loose breaker wire that caused the breaker to trip is this:

The bad connection creates heat that causes the breaker to react even when the current is much less than the rating on the breaker. This is due to the sensor mechanism in the breaker being a thermal device. Some newer breakers may be designed differently.

I had a neighbor that had a 200 amp breaker tripping due to a loose wire on it. The current flowing when it tripped was around 30-40 amps.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/15/11, 2:42 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Am I Missing Something

In the case of arching wouldn't there be an increase in current or load , causing a tripped breaker ?



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #15  
Old 2/15/11, 3:39 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Am I Missing Something

Quote:
Originally Posted by agallatin View Post
In the case of arching wouldn't there be an increase in current or load , causing a tripped breaker ?
Most likey--see post #7.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Missing section of foundation-interesting hmiller Structural Inspections 7 2/14/11 2:18 PM
Missing Foundation Footing jevans Structural Inspections 8 4/13/10 4:56 AM
Jim Bushart (look what your missing) belliott General Inspection Discussion 71 1/8/09 7:34 PM
What's missing here? jtedesco1 Electrical Inspections 10 12/19/07 8:11 PM


All times are GMT -4. The time now is 5:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts