A good reference source and explanation for clients regarding the hazard of bundled neutrals and bundled grounding with grounded conductors under the same buss lug...
http://static.schneider-electric.us/...0100DB0705.pdf This issue seems difficult for many inspectors (and some electrical contractors) to grasp, but the PDF is great at explaining the reasons why it is prohibited. Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#18
|
||||
|
||||
|
Thanks Bill.
Quote:
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#19
|
||||
|
||||
|
Okay, Thanks Bill and Thanks Mike. I'm not being a smart *** here, but I'm going to ask the same question I did in post 6 just a little differently, because we are NOT doing code compliancy inspections.
So what, and what's the big deal? What's the harm, and what's the risk? Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#20
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#21
|
||||
|
||||
|
Quote:
Newer panels tell you in the instructions not to install them together as well. |
|
#22
|
||||
|
||||
|
Quote:
So again I ask, what's the big the deal of having them under the same lug? I've yet to hear a compelling reason why (above that it's not allowed) for it being any big deal... Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#23
|
||||
|
||||
|
Quote:
I'm not arguing that it is allowed today. It clearly isn't under code. My question is, why not? Why on a 30 year panel that was installed this way correctly under the codes at that time, would anyone call this out as a defect? There has to be a reason beyond "it's not allowed". If it is a shock risk, there needs to be an explanation as to what circumstances a shock would happen, and why it would be important to call out. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#24
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
It was not installed correctly in the 30 year old panel either. The requirement was listed in the UL standard which is not as easy to access as the NEC. It was a violation of 110.3 before. Now it is specifically spelled out in the NEC to avoid the chance of someone not knowing. I don't have access to a 30 year old panel label, but it might have been stated there and no one bothered to read it.
|
|
#25
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here's a pretty good explanation that was part of the required substantiation to put this directly into the 2002 NEC. This code change came from a representative of Square D. The CMP decided to make this a new code section and called it 408.21 in the 2002 NEC.
Quote:
|
|
#26
|
||||
|
||||
|
Thanks Bob for taking the time to post this...
Quote:
Quote:
Soooo... it's not allowed by NEC because the equipment manufacturers say they should be under the same lug. That's not really a good explanation. So let me ask again in a different way... Why does the manufacturer of the panel wish that the ground be connected if the neutral is disconnected? After all, if you are disconnecting the neutral, the power would be off anyway. I know why you can't have neutrals sharing luggs that's obvious because they are different circuits. The question is why not a ground and neutral that are in the same circuit. As far as I can tell it wouldn't make any difference one way or the other... PS... I'm not trying to be a jerk, or be argumentative. I am just trying to understand what the reason behind the rule, not just the rule itself. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#27
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#28
|
||||
|
||||
|
I think in this instance it simply boils back down to a "double tap" scenario and the associated hazard "potential" (similar to the hazard of a double tapped breaker)... as well as the intent of simply maintaining equipment ground at all times.
Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#29
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is quite possible that if the device failed someone could pull it out to troubleshoot the problem. The power is not off so there is a very good chance of a shock hazard with no path back to the panel to clear the fault.
There is also the diferent coefficient of expansion from a current carrying conductor vs a non-current carrying conductor. |
|
#30
|
|||
|
|||
|
Thanks Michael . I got it . I always thought that arching was an increase in current . Now I now better .
galaxyhomeinspections.com An amateur built the Ark ! Professionals built the Titanic ! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Missing section of foundation-interesting | hmiller | Structural Inspections | 7 | 2/14/11 2:18 PM |
| Missing Foundation Footing | jevans | Structural Inspections | 8 | 4/13/10 4:56 AM |
| Jim Bushart (look what your missing) | belliott | General Inspection Discussion | 71 | 1/8/09 7:34 PM |
| What's missing here? | jtedesco1 | Electrical Inspections | 10 | 12/19/07 8:11 PM |