Default AM I missing somthing here?

Look at the gfci breaker
I know its not right, but what did they do????
Shouldn't the hot wire be installed under a different screw or is this normal.
Attached Thumbnails
am-missing-somthing-here-1200-kirby-glen-dr-knoxville-028.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/8/10, 8:28 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: AM I missing somthing here?




InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 12/8/10, 8:42 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: AM I missing somthing here?

Thanks.
I am used to seeing them without the neutral being stuffed in with the pigtail. Older panel and breaker.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 12/8/10, 9:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AM I missing somthing here?

Quote:
Originally Posted by lkage View Post
Why would they show a splice on the load neutral? Typically they connect directly to the CB making this graphic somewhat confusing.
Reply With Quote
  #5  
Old 12/8/10, 9:09 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: AM I missing somthing here?

Sean, just a tip.... Change the name of the picture, so that no one could find the location from the filename.
Reply With Quote
  #6  
Old 12/8/10, 9:51 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: AM I missing somthing here?

Quote:
Originally Posted by Robert Meier View Post
Why would they show a splice on the load neutral? Typically they connect directly to the CB making this graphic somewhat confusing.
This is the exact reason for my confusion! Like I said it was an older breaker 16 years exactly. I personaly have never seen an installation this way.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #7  
Old 12/8/10, 9:52 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: AM I missing somthing here?

Quote:
Originally Posted by mroberson View Post
Sean, just a tip.... Change the name of the picture, so that no one could find the location from the filename.
Yeah, I wanted an answer and did not want to waste time while doing the report.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 12/8/10, 10:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AM I missing somthing here?

While the image is not what normally happens...it is also technically correct regardless. Nothing in the NEC would prohibit a contractor from splicing a "MISTAKE" they might have made in cutting off the neutral [grounded conductor] too short and adding that pigtail. While not the norm...still compliant never the less.

In regards to the graphic larry posted......I never actually looked at the original posters picture...lol...sorry



Paul W. Abernathy
Reply With Quote
  #9  
Old 12/8/10, 10:50 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AM I missing somthing here?

ok.....now I look at this image and something strikes me as odd. The neutral [grounded conductor] should not be jamed in with the GFCI grounded jumper. I believe their should be another lug on that breaker that is not being used. If this is the case the GFCI will not function as intended when the intent is needed......say that 5 times in a row why don't ya !

But alas.....my eyes may be screwing with me



Paul W. Abernathy
Reply With Quote
  #10  
Old 12/8/10, 11:06 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: AM I missing somthing here?

Quote:
Originally Posted by pabernathy View Post
ok.....now I look at this image and something strikes me as odd. The neutral [grounded conductor] should not be jamed in with the GFCI grounded jumper. I believe their should be another lug on that breaker that is not being used. If this is the case the GFCI will not function as intended when the intent is needed......say that 5 times in a row why don't ya !

But alas.....my eyes may be screwing with me
Hi Paul , the insulated conductors loo a little over striped. IMO



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #11  
Old 12/8/10, 11:12 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AM I missing somthing here?

lol...yeah I was holding my breath on that one as I doubt it meets the technical concept of "encircle"...lol...but hey they atleast tried.



Paul W. Abernathy
Reply With Quote
  #12  
Old 12/8/10, 11:14 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AM I missing somthing here?

lol....I just read your statement again...lol.....I thought you meant the stripes of BLACK marker on the grounded conductors in order to ATTEMPT to re-identify them...lol.....man I gotta read the posts better as I am multi-tasking tonight.



Paul W. Abernathy
Reply With Quote
  #13  
Old 12/8/10, 11:24 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: AM I missing somthing here?

Quote:
Originally Posted by pabernathy View Post
I am multi-tasking tonight.
Paul...... put down the burger and slowly back away.. or are you getting in shape to fit in your Santa outfit?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/9/10, 4:42 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AM I missing somthing here?

Quote:
Originally Posted by sfogarty View Post
This is the exact reason for my confusion! Like I said it was an older breaker 16 years exactly. I personaly have never seen an installation this way.
Ahhh, so the CB is so old that it came with two factory installed pigtails.
Reply With Quote
  #15  
Old 12/9/10, 7:17 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: AM I missing somthing here?

Quote:
Originally Posted by Robert Meier View Post
Ahhh, so the CB is so old that it came with two factory installed pigtails.
Is this the correct answer???
Did they actually do it this way, because I thought it was stuffed in the hole, which is why it looked strange.

Before my time I guess.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Missing Gutter extensions tturner Exterior Inspections 1 9/19/10 4:18 PM
Can you spot whats missing? belliott Inspecting HVAC Systems 13 2/21/09 11:20 AM
What's missing here? jtedesco1 Electrical Inspections 10 12/19/07 8:11 PM
Water Heater label missing rnewman1 Plumbing Inspections 3 9/19/06 6:15 PM


All times are GMT -4. The time now is 5:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts