Default what am I seeing

Main service tieback has standard three wire, service drop is in conduit to meter of four unit apartment. Service run inside home is to long, close to 20 feet to 200 amp square D box in basement. When dead panel is removed it reveals two neutrals, or am I missing something? Exterior disconnect box was not opened because I could not break the screws free. Updated in 1998. What do you guys see?
Attached Thumbnails
am-seeing-100_6567.jpg   am-seeing-p3270122.jpg   am-seeing-p3270125.jpg   am-seeing-p3270128.jpg  
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/27/10, 1:52 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: what am I seeing

Look at it this way. Your two outside wires are the common two you see in a regular residential panel, and your middle wire appears to be just a ground coming from the transformer etc..
Reply With Quote
  #3  
Old 3/27/10, 2:08 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: what am I seeing

It is a 4 wire feed to the inside remote distribution panel from the service disconnect outside, no?

But, it looks like the grounded conductors are not isolated with that jumper wire touching the grounding conductor and possibly the can...needs repair.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 3/27/10 at 2:13 PM..
Reply With Quote
  #4  
Old 3/27/10, 2:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: what am I seeing

That's 4 wire SER type of SE cable which would be required since this is considered a sub-panel. That is due to the disconnect being on the outside. That means that the SE Cable can run an unlimited length within the structure. The neutral conductors and the EGC's should be separate within the panel which they appear to be. The bare copper conductors should be removed since they serve no purpose and may inadvertently ground the neutral to the panel enclosure. The two neutral bus bars should be mechanically connected through a piece of buss that is connected to the grayish looking neutral conductor in the center.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 5:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts